[Nut-upsuser] Connectiion to UPS via SNMP
Kjell Claesson
kjell.claesson at telia.com
Thu Aug 3 08:41:21 UTC 2006
tor 2006-08-03 klockan 09:51 +0200 skrev Daniel Haas:
> Hi NUT-Users,
>
Hi Daniel,
> we work with a GE LP 33 UPS and an Advanced SNMP WEB Interface Card. This card supports the RFC1628 Definition.
> So I think this combination work together with NUT and the snmp-driver, correct?
>
> I installed the networkupstools on my Debian Sarge with apt-get (nut & nut-snmp).
>
> After configuration I start the upsd and upsmon. I get following output in /var/log/syslog:
> ...
> Aug 3 08:40:44 localhost upsd[1321]: Connected to UPS [snmp]: snmp-ups-136.8.4.14
> Aug 3 08:40:44 localhost snmp-ups[1320]: Startup successful
> Aug 3 08:40:44 localhost upsd[1321]: Data for UPS [snmp] is stale - check driver
> Aug 3 08:40:44 localhost upsd[1322]: Startup successful
> Aug 3 08:40:44 localhost upsmon[1324]: Startup successful
> Aug 3 08:40:44 localhost upsmon[1325]: UPS [snmp at 136.8.4.14]: connect failed: Connection failure: Connection refused
> Aug 3 08:40:44 localhost upsmon[1325]: Communications with UPS snmp at 136.8.4.14 lost
Looks like you have to check your upsmon.conf. You should be
monitoring GE_LP33 at 136.8.4.14 not smnp. Also check the ACl in
upsd.conf if you run the monitor on another computer then the
upsd.
Best would be to give us all configs.
Regards
Kjell