[Nut-upsuser] Misreported values with newhidups
Peter Selinger
selinger at mathstat.dal.ca
Tue Feb 28 23:06:11 UTC 2006
This is a duplicate bug report. It was first reported by Gordon Rowell
on Feb 06 on the Nut-upsdev list, and has subsequently been fixed in
CVS. See
http://boxster.ghz.cc/projects/nut/changeset/352
Arnaud, should we backport these bugfixes to 2.0.3? I have a feeling
we will see this bug reported several times more.
-- Peter
John Gruenenfelder wrote:
>
> Okay, now that I've got NUT up and running with the newhidups driver, I can
> give it a quick shakedown.
>
> Most of the values look good, but are few are off. Here's what I get:
>
> elrond at foxstar:~$ upsc foxstarups at localhost
> battery.charge: 100
> battery.charge.low: 10
> battery.charge.warning: 50
> battery.date: 3150/08/01
> battery.mfr.date: 2005/03/22
> battery.runtime: 1935
> battery.runtime.low: 120
> battery.temperature: 302.0
> battery.voltage: 27.0
> battery.voltage.nominal: 24.0
> driver.name: newhidups
> driver.parameter.offdelay: 600
> driver.parameter.port: auto
> driver.version: 2.0.3
> driver.version.data: APC HID 0.8
> driver.version.internal: 0.28
> input.voltage: -6437.0
> input.voltage.nominal: 120
> output.voltage: 120.0
> output.voltage.target.line: 120.0
> ups.beeper.status: enabled
> ups.delay.shutdown: -1
> ups.firmware: 9.o2 .D
> ups.firmware.aux: o2
> ups.load: 25.0
> ups.mfr: American Power Conversion
> ups.mfr.date: 2005/03/22
> ups.model: Back-UPS BR 800
> ups.serial: QB0513140434
> ups.status: OL
> ups.temperature: 302.0
> ups.test.result: No test initiated
>
> In particular, the bad ones are:
> battery.date, battery.temperature, input.voltage, ups.temperature, and maybe
> battery.voltage.
>
> battery.date has a very wrong year.
>
> battery.temperature is very high. The NUT cgi scripts treat this value as a
> reading in Celcius, which would seem appropriate. However, it looks as though
> the UPS is actually giving a reading in Kelvin. 302 degrees Kelvin is about
> 46 degrees Celius. That's a far more reasonable reading. The same conversion
> would be appropriate for ups.temperature.
>
> input.voltage is just plain wrong.
>
> battery.voltage... I'm not really sure if this is wrong or not. It's higher
> than the nominal voltage of 24V. Once charged, shouldn't the voltage be near
> the "nominal" value?
>
> All of the other values look at least in the ballpark. The runtime looks
> good. And by turning devices on and off I think the load value is correct to.
>
>
> --
> --John Gruenenfelder Research Assistant, UMass Amherst student
> Systems Manager, MKS Imaging Technology, LLC.
> Try Weasel Reader for PalmOS -- http://gutenpalm.sf.net
> "This is the most fun I've had without being drenched in the blood
> of my enemies!"
> --Sam of Sam & Max
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
>
More information about the Nut-upsuser