[Nut-upsuser] Shutdown Problem

Eli Wapniarski eli at orbsky.homelinux.org
Mon Jul 17 18:06:43 UTC 2006


> Maybe your UPS falls into the category mentioned in the fentonups man page:
>
> EXTRA ARGUMENTS
>        This  driver  supports  the  following   optional   settings   in  
> the ups.conf(5):
>
>        lowbattvolt=decimal
>               Sets  a user-defined battery voltage under which the driver
> will consider that the UPS is on "low battery" condition when running on
> battery.  This allows initiating a system shutdown before the UPS signals a
> low battery status by itself, and  may  be  useful for  some UPSes that
> don't have enough runtime left for properly shutting down the system when
> they start signaling a  "low  bat- tery" status.

That did the trick. Thank  you. Normal OL battery voltage hovers around 14.2 
14.3 I set the lowbattvolt parameter to 12.5 and my computer shutdown cleanly 
after unplugging the ups and the Battery Voltage dropped to 12.5. Thank you. 
Thank you. Thank you. :) .

Eli