[Nut-upsuser] USB UPS and FreeBSD
Scott Tuc Ellentuch at T-B-O-H
ml at t-b-o-h.net
Tue May 23 04:03:24 UTC 2006
> On Monday 22 May 2006 23:36, Scott Tuc Ellentuch at T-B-O-H wrote:
> > I was wondering as a fellow FreeBSD user, where
> > did you do the "upsdrvctl shutdown" command?
> >
> > For the others, there was mention of "rc.early",
> > but it seems that it is not run during shutdown.
>
> There is /etc/rc.shutdown.
>
In another convo I talked about /etc/rc.shutdown
being too early in the process. I corrupt filesystems that cause the system
not to boot, which of course is a bad thing.
>
> What I have is a script in /usr/local/etc/rc.d called nut.sh. It starts and
> stops the NUT daemons. If it has been asked to stop it, it checks if the
> killpower flag is present and if so, it runs upsdrvctl with the option to
> shutdown the UPS.
>
I'm using the ports... And there is the nut.sh, which I use. The
problem is that you are also supposed to put in the "upsdrvctl shutdown" at
some point where the filesystems are mounted read only so you don't get
file corruption.
>
> Make sure you have a shutdown gracedelay though - FreeBSD doesn't run any
> scripts after the disks are unmounted so you must start the UPS shutdown
> phase before the disks are unmounted, hence the need for a grace delay.
>
Where is this set then, no one else has mentioned it.
Thanks, Tuc