[Nut-upsuser] HP R3000 XR, warning or perhaps error
    Gregory Orange 
    gregory.orange at metoceanengineers.com
       
    Wed Apr 18 01:43:56 UTC 2007
    
    
  
Kjell Claesson wrote:
>> Communications with UPS lost: Error executing command
>> Communications with UPS lost: Error executing command
>> Communications with UPS lost: Error executing command
>> Communications with UPS re-established
>> Connected to UPS on /dev/ttyS0 baudrate: 9600
>> Model = HP R3000 XR      3000VA
>>
>> It all seems to work but the initial errors or warnings concern me. I'm 
>> running stable 2.05 built from source.
> 
> This come from the baudhunting function in the driver.
> If you set the baud_rate in the ups.conf to 9600 You don't get this
> errors.
Ah yes, I should have tried that. At one stage I had it set to 19200 
which was clearly wrong, so I got another error of it failing then going 
to the baudhunting function for three more. Thanks for the tip - no more 
warnings or errors.
Greg.
-- 
    - ---- -----
      Gregory Orange             Phone: +61 8 9387 7955
     System Administator            Fax: +61 8 9387 6686
    MetOcean Engineers Pty Ltd           http://www.metoceanengineers.com
   System Administrators Guild of Australia  http://www.sage-au.org.au
- ---- -----
    
    
More information about the Nut-upsuser
mailing list