On Dec 24, 2007 9:31 AM, Edjé <edosseh at ub.tg> wrote:
> > Also, what does "upsc siUps1" return? (Some UPSes have an adjustable
> > "low battery" threshold.)
> That is why it returns:
> battery.alarm.threshold: L
> battery.charge: 100.0
> battery.charge.restart: 15
This probably means that after a power failure, the UPS will wait
until the battery is at least 15% charged before turning on the
outlets again. This means you do not need the hack mentioned in
shutdown.txt under "One more tip".
> battery.date: 03/31/07
[...]
> ups.test.result: NO
Even though the battery seems to be less than a year old, I would
assume that the test result means you need a new battery.
--
- Charles Lepple