[Nut-upsuser] false alerts/shutdown
Arjen de Korte
nut+users at de-korte.org
Mon Jun 18 16:14:12 UTC 2007
> My colleague asked me to mail this info.
> It seems the problem only occures when using the usb interface.
Indeed. So for the moment I would suggest the obvious (use the serial
interface), while we let the author of the USB driver figure out what is
going on here. Since I don't have any USB connected UPSes here, I'm
drawing a complete blank here.
What we can conclude from this is, that the alert messages are probably
indeed bogus and that they are most likely generated by the driver (not by
the server, nor client). Maybe it is polling the UPS too fast, or there is
a problem with the USB interface, I really don't know.
> With the usb interface:
> ***********************
> [root at testserver /var/log]# /usr/local/ups/bin/upsc
> usb-mge-evolution at localhost
> battery.charge: 100
> battery.charge.low: 20
> battery.charge.restart: 0
> battery.runtime: 1200
> battery.type: PbAc
> battery.voltage: 13.0
That's *really* low for a fully charged battery. I don't either trust this
value, the value for the battery charge or both.
> driver.name: newhidups
> driver.parameter.port: auto
> driver.parameter.productid: ffff
> driver.parameter.vendorid: 0463
> driver.version: 2.0.5
> driver.version.data: MGE HID 1.0
> driver.version.internal: 0.30
> input.frequency: 50.0
> input.transfer.boost.low: 184.0
> input.transfer.high: 294.0
> input.transfer.low: 160.0
> input.transfer.trim.high: 265.0
> input.voltage: 226.0
> outlet.0.desc: Main Outlet
> outlet.0.id: 0
> outlet.0.switchable: no
> outlet.1.autoswitch.charge.low: 0
> outlet.1.delay.shutdown: 65535
> outlet.1.delay.start: 3
> outlet.1.desc: PowerShare Outlet 1
> outlet.1.id: 1
> outlet.1.status: on
> outlet.1.switchable: yes
> outlet.2.autoswitch.charge.low: 0
> outlet.2.delay.shutdown: 65535
> outlet.2.delay.start: 6
> outlet.2.desc: PowerShare Outlet 2
> outlet.2.id: 2
> outlet.2.status: on
> outlet.2.switchable: yes
> output.current: 0.40
> output.frequency: 50.0
> output.voltage: 226.0
> output.voltage.nominal: 24.0
Errrr, that's either off by a factor of 10 or meaning something completely
differen.
> ups.beeper.status: enabled
> ups.delay.shutdown: -1
> ups.delay.start: -1
> ups.load: 21
> ups.mfr: MGE UPS SYSTEMS
> ups.model: Evolution 650
> ups.power.nominal: 650
> ups.serial: AV0G4602F
> ups.status: OL CHRG
> ups.test.interval: 604800
> ups.test.result: Done and passed
>
> In the log file:
> ****************
>
> Broadcast message from nutups (Mon Jun 18 12:25:33 2007):
>
> UPS usb-mge-evolution at localhost on battery
> Jun 18 12:25:33 testserver upsmon[2872]: UPS usb-mge-evolution at localhost
> on battery
> Jun 18 12:25:33 testserver wall[361]: wall: user nutups broadcasted 1
> lines (44 chars)
>
> Broadcast message from nutups (Mon Jun 18 12:25:43 2007):
>
> UPS usb-mge-evolution at localhost on line power
> Jun 18 12:25:43 testserver upsmon[2872]: UPS usb-mge-evolution at localhost
> on line power
> Jun 18 12:25:43 testserver wall[366]: wall: user nutups broadcasted 1
> lines (47 chars)
>
> Broadcast message from nutups (Mon Jun 18 12:26:23 2007):
>
> UPS usb-mge-evolution at localhost on battery
> Jun 18 12:26:23 testserver upsmon[2872]: UPS usb-mge-evolution at localhost
> on battery
> Jun 18 12:26:23 testserver wall[370]: wall: user nutups broadcasted 1
> lines (44 chars)
>
> Broadcast message from nutups (Mon Jun 18 12:26:33 2007):
>
> UPS usb-mge-evolution at localhost on line power
> Jun 18 12:26:33 testserver upsmon[2872]: UPS usb-mge-evolution at localhost
> on line power
> Broadcast message from nutups (Mon Jun 18 12:42:18 2007):
>
> UPS usb-mge-evolution at localhost on battery
> Jun 18 12:42:18 testserver upsmon[2872]: UPS usb-mge-evolution at localhost
> on battery
> Jun 18 12:42:18 testserver wall[385]: wall: user nutups broadcasted 1
> lines (44 chars)
>
> Broadcast message from nutups (Mon Jun 18 12:42:28 2007):
>
> UPS usb-mge-evolution at localhost on line power
> Jun 18 12:42:28 testserver upsmon[2872]: UPS usb-mge-evolution at localhost
> on line power
> Jun 18 12:42:28 testserver wall[389]: wall: user nutups broadcasted 1
> lines (47 chars)
> Broadcast message from nutups (Mon Jun 18 12:42:48 2007):
>
> UPS usb-mge-evolution at localhost battery is low
>
> Broadcast message from nutups (Mon Jun 18 12:42:48 2007):
>
> Executing automatic power-fail shutdown
>
>
> Broadcast message from nutups (Mon Jun 18 12:42:48 2007):
>
> UPS usb-mge-evolution at localhost on battery
>
> Broadcast message from nutups (Mon Jun 18 12:42:48 2007):
>
> Auto logout and shutdown proceeding
Provided your systems came back online normally, you passed the test for
the halt sequence.
> With the serial interface:
> **************************
> [root at testserver ~]# /usr/local/ups/bin/upsc
> serial-mge-evolution at localhost
> battery.charge: 100
> battery.charge.low: 20
> battery.runtime: 1200
> driver.name: mge-shut
> driver.parameter.port: /dev/ttyS0
> driver.version: 2.0.5
> driver.version.internal: 0.66
> input.frequency: 50
> input.voltage: 226
> outlet.0.desc: Main Outlet
> outlet.0.id: 0
> outlet.0.switchable: 0
> outlet.1.autoswitch.charge.low: 0
> outlet.1.delay.shutdown: -1
> outlet.1.delay.start: -1
That's odd. The USB driver reports different values here, it looks like
they are not used here.
> outlet.1.desc: PowerShare Outlet 1
> outlet.1.id: 1
> outlet.1.switch: 1
> outlet.1.switchable: 1
> outlet.2.autoswitch.charge.low: 0
> outlet.2.delay.shutdown: -1
> outlet.2.delay.start: -1
Same here.
> outlet.2.desc: PowerShare Outlet 2
> outlet.2.id: 2
> outlet.2.switch: 1
> outlet.2.switchable: 1
> output.frequency: 50
> output.voltage: 226
> output.voltage.nominal: 24
Again, this doesn't look right.
> ups.delay.shutdown: -1
> ups.delay.start: -1
> ups.load: 20
> ups.mfr: MGE UPS SYSTEMS
> ups.model: Evolution 650
> ups.power.nominal: 650
> ups.serial: AV0G4602F
> ups.status: OL CHRG
> ups.test.result: Done and passed
>
> in the log file:
> ****************
> no shutdown or "on battery" messages
Best regards, Arjen