> Hi,
>
> Edjé wrote:
>> Hello,
>> My APC Ups uses nut to manage all systems connected to it. But if online 
>> power failed until it shutdown, it not restart automatically after the 
>> power returned. It stay down until i restart it.
> Can you clarify this please?  Do you mean that the UPS is shut down as a 
> result of power failure and the UPS does not restart automatically after 
> the power has returned?  Or are you referring to a server?
Yes the UPS is shut down when power failure is surronded long time but after 
power return, it doesn't restart automatically.
> Thanks,
> Jon
>> When i execute the command: # upsc siUps1
>> it output me this:
>> battery.alarm.threshold: L
>> battery.charge: 018.0
>> battery.charge.restart: 15
>> battery.date: 03/31/07
>> battery.runtime: 120
>> battery.runtime.low: 120
>> battery.voltage: 26.77
>> battery.voltage.nominal: 024
>> driver.name: apcsmart
>> driver.parameter.pollinterval: 2
>> driver.parameter.port: /dev/ttyS0
>> driver.parameter.sdtype: 0
>> driver.version: 2.2.0-
>> driver.version.internal: 1.99.8
>> input.frequency: 51.00
>> input.quality: FF
>> input.sensitivity: H
>> input.transfer.high: 253
>> input.transfer.low: 208
>> input.transfer.reason: S
>> input.voltage: 226.0
>> input.voltage.maximum: 226.0
>> input.voltage.minimum: 222.0
>> output.voltage: 224.0
>> output.voltage.nominal: 230
>> ups.delay.shutdown: 300
>> ups.delay.start: 000
>> ups.firmware: 738.2.I
>> ups.id: UPS_IDEN
>> ups.load: 033.1
>> ups.mfr: APC
>> ups.mfr.date: 03/31/07
>> ups.model: Smart-UPS SC1500
>> ups.serial: 5S0713T66466
>> ups.status: OL
>> ups.test.interval: 1209600
>> ups.test.result: NO
>>  What can be my problem? Battery is concerned? Please Help.
>>  ------------------------------------------------------------------------
>>
>> _______________________________________________
>> Nut-upsuser mailing list
>> Nut-upsuser at lists.alioth.debian.org
>> http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
>
> -- 
> ----------------------------
> Jon Clark
> Scientific Officer
> Dept. of Applied Mathematics
> University of Sheffield
> Sheffield, S3 7RH, UK
> ---------------------------- 




More information about the Nut-upsuser mailing list