> I had a very strange occurance in my basement datacenter this early AM.
>
> the following was logged by upslog:
>
> 20080219 023452 100.0 123.0 049.0 [OL CHRG] NA 60.00
> 20080219 023522 100.0 122.8 049.0 [OL CHRG] NA 60.00
> 20080219 023552 098.0 123.0 049.0 [OL DISCHRG] NA 60.00
> 20080219 023622 097.0 123.0 049.0 [OL DISCHRG] NA 60.00
>
> ...
>
> 20080219 063429 019.0 122.6 049.0 [OL DISCHRG] NA 60.00
> 20080219 063459 019.0 122.8 049.0 [OL DISCHRG] NA 60.00
> 20080219 183013 100.0 121.1 050.0 [OL CHRG] NA 60.00
> 20080219 183043 100.0 120.9 049.0 [OL CHRG] NA 60.00
>
> the good news is the UPS held up for four hours.
>
> the bad news is that nut completely ignored that the UPS was
> discharging, and none of my connected machines shut down properly. I
> know that the UPS driver was running, because if was not, upsd would
> have complained loudly and frequently. I know upsd was running (on the
> connected server as well as all the clients), because if it was not,
> upsmon would have complained loudly and frequently.
>
> there were no indications in my logs that nut was paying any attention
> to the situation.
>
> why did my UPS decide to discharge its battery when there appears to be
> no power outage? (just looking for suggestions and guesses here from
> other MGE users...)
>
> why did nut not see that my UPS was discharging and the battery
> percentage running down and take appropriate action? "OL DISCHRG"
> status in the logs seems nonsensical. I have only seen this condition a
> few times before in my logs:
>
> 20061002 002628 094.0 079.6 045.0 [OB DISCHRG] NA 60.00
> 20061002 002658 093.0 096.8 045.0 [OL DISCHRG BOOST] NA 60.00
> 20061002 002728 093.0 088.3 045.0 [OL DISCHRG] NA 60.00
> 20061002 002758 093.0 000.0 045.0 [OB DISCHRG] NA 00.00
>
> Oct 2 00:22:59 aragorn upsmon[234]: UPS mge3000 at localhost on battery
> Oct 2 00:26:45 aragorn upsmon[234]: UPS mge3000 at localhost on line power
> Oct 2 00:27:35 aragorn upsmon[234]: UPS mge3000 at localhost on battery
>
> nut saw this one, and shut everything down, as expected.
>
> 20061214 224604 100.0 122.4 054.0 [OL CHRG] NA 60.00
> 20061214 224634 099.0 123.7 056.0 [OL DISCHRG] NA 60.00
> 20061214 224704 097.0 000.0 054.0 [OB DISCHRG] NA 00.00
>
> Dec 14 22:46:45 aragorn upsmon[234]: UPS mge3000 at localhost on battery
> Dec 14 22:58:41 aragorn upsmon[234]: UPS mge3000 at localhost battery is low
> Dec 14 22:58:41 aragorn upsd[226]: Client master at 127.0.0.1 set FSD on UPS [mge3000]
> Dec 14 22:58:57 aragorn upsmon[234]: Host sync timer expired, forcing shutdown
> Dec 14 22:58:57 aragorn upsmon[234]: Executing automatic power-fail shutdown
> Dec 14 22:58:57 aragorn upsmon[234]: Auto logout and shutdown proceeding
> Dec 14 22:59:02 aragorn upsd[226]: Host 127.0.0.1 disconnected (read failure)
> Dec 14 22:59:08 aragorn upsd[226]: Signal 15: exiting
>
> nut did not see this one, but it was transient:
>
> 20070227 083935 100.0 122.2 048.0 [OL CHRG] NA 60.00
> 20070227 084005 100.0 122.2 048.0 [OL DISCHRG] NA 60.00
> 20070227 084035 100.0 122.2 048.0 [OL CHRG] NA 60.00
>
> here is the device (online now)
>
> $ upsc mge3000 at localhost
> battery.charge: 100.0
> battery.charge.low: 30
> battery.runtime: 00876
> battery.voltage: 081.6
> battery.voltage.nominal: 072.0
> driver.name: mge-utalk
> driver.parameter.port: /dev/tty00
> driver.version: 2.0.1
> driver.version.internal: 0.81.0
> input.frequency: 60.00
> input.transfer.boost.low: 102.0
> input.transfer.high: 132.0
> input.transfer.low: 102.0
> input.transfer.trim.high: 132.0
> input.voltage: 122.8
> output.current: 010.3
> output.voltage: 122.2
> ups.delay.shutdown: 020
> ups.delay.start: 001
> ups.firmware: unknown
> ups.id: Evolutio 3000 17
> ups.load: 049.0
> ups.mfr: MGE UPS SYSTEMS
> ups.model: Evolution 3000
> ups.status: OL CHRG
> ups.test.interval: 10080
>
> thanks in advance for any advice.
as always, Arjen already replied.
I would just add that you should prefer the mge-shut driver.
It's more complete and maintained that the mge-utalk (which is for the
legacy ASCII protocol).
Best regards,
Arnaud
--
Linux / Unix Expert R&D - MGE Office Protection Systems - http://www.mgeops.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://people.debian.org/~aquette/
Free Software Developer - http://arnaud.quette.free.fr/
More information about the Nut-upsuser
mailing list