Got it working Arjen... I had to compile 2.2.2 and install from source. It
must have been with the current version of NUT packaged with Ubuntu Server
8.04. 
The only remaining weirdness is upsc reports the battery (either 0 or 100,
nothing in between) and remaining minutes starting in the 1000's.
I suspect both of the above (or at least the battery %) are due to not
having a ground when I did an "unplug" test.
-Ken L.
-----Original Message-----
From: Arjen de Korte [mailto:nut+users at de-korte.org] 
Sent: Tuesday, September 09, 2008 1:22 PM
To: ken at litkoaero.com
Cc: Nut-upsuser at lists.alioth.debian.org
Subject: Re: [Nut-upsuser] OMNIPLUS1000LCD is "unavailable"
Citeren Kenneth R Litko <ken at litkoaero.com>:
> OK... Thank you Arjen.
>
> I've killed the extra processes... But have some new problems. And I 
> still cannot connect to the device.
>
> If I run upsdrvctl start (with or without '-u root'):
>
> ------
> klitko at bigdog:/etc/nut$ sudo upsdrvctl start Network UPS Tools - UPS 
> driver controller 2.2.1- Network UPS Tools: 0.29 USB communication 
> driver - core 0.32 (2.2.1-)
>
> Using subdriver: TrippLite HID 0.2 (experimental) Startup timer 
> elapsed, continuing...
This could be due to a problem with handling interrupt reports. If memory
serves, Tripplite UPSes are broken in this aspect (and generate this
continuously), so you may be hit by this.
There was a fix for this in nut-2.2.2 (it limits reading them to 32), so it
would be worthwhile to check if upgrading helps.
Best regards, Arjen
--