[Nut-upsuser] OMNIPLUS1000LCD is "unavailable"

Arjen de Korte nut+users at de-korte.org
Tue Sep 9 20:41:29 UTC 2008


Citeren Kenneth R Litko <ken at litkoaero.com>:

> Got it working Arjen... I had to compile 2.2.2 and install from source. It
> must have been with the current version of NUT packaged with Ubuntu Server
> 8.04.

Good to hear that!

> The only remaining weirdness is upsc reports the battery (either 0 or 100,
> nothing in between) and remaining minutes starting in the 1000's.

As to the latter, time remaining is reported in seconds (not minutes),  
so if the load is small, this doesn't sound unreasonable. See  
'docs/new-names.txt'. With regard to the battery charge, there is  
probably not much we can do about that. The driver will report what we  
read from the UPS ad verbatim, so it's garbage in, garbage out. We  
would like to see the output from 'upsc' anyway, so that we can add  
this to our collection of reports.

> I suspect both of the above (or at least the battery %) are due to not
> having a ground when I did an "unplug" test.

Unplugging is usually not a good idea, since that will also disconnect  
the ground connection. A switchable power strip is a better choice for  
tests like this.

Best regards, Arjen
-- 
Eindhoven - The Netherlands
Key fingerprint - 66 4E 03 2C 9D B5 CB 9B  7A FE 7E C1 EE 88 BC 57

----------------------------------------------------------------
This message was sent using IMP, the Internet Messaging Program.