[Nut-upsuser] Premature end of script headers: upsimage.cgi
Arjen de Korte
nut+users at de-korte.org
Fri Jul 10 16:06:58 UTC 2009
Citeren benjamin thielsen <bthielsen op safarivideonetworks.com>:
> working voltage graph:
>
> [ups2]
> driver = usbhid-ups
> port = auto
[...]
> battery.voltage: 27.7
> battery.voltage.nominal: 24.0
This looks normal.
> non-working voltage graph:
>
> [ups4]
> driver = snmp-ups
> port = ups4
> community = xxxxxxxxxx
> snmp_version = v1
> pollfreq = 5
[...]
> battery.voltage: 55.00
> battery.voltage.nominal: 0.00
But here we have located the problem. A 'battery.voltage.nominal'
equal to zero will mean that the calculated 'battery.voltage.minimum'
and 'battery.voltage.maximum' will both be zero. This results in a
divide by zero error in the range calculation. You can work around
this by adding
override.battery.voltage.nominal = 48
in 'ups.conf' for these drivers. This will make them ignore the
reported value from the UPS and use the correct nominal value. You can
also set
default.battery.voltage.minimum = 38.4
default.battery.voltage.maximum = 55.2
to preset the minimum and maximum voltage range of the battery, since
neither are reported by the UPS.
What remains is the question if this is a problem in the snmp-ups
driver or the UPS. I honestly don't know.
Best regards, Arjen
--
Please keep list traffic on the list
More information about the Nut-upsuser
mailing list