[Nut-upsuser] New NUT user with HP R3000XR problem
Brother Railgun of Reason
alaric at caerllewys.net
Wed May 27 18:08:57 UTC 2009
[oops, forgot to copy list]
On Wed, May 27, 2009 at 06:04:40PM +0200, Kjell Claesson wrote:
> > On Tue, May 26, 2009 at 09:51:31PM -0400, Brother Railgun of Reason wrote:
> Hi,
> > > ups.conf looks like this:
> > >
> > > [tokamak]
> > > driver = bcmxcp
> > > port = /dev/tty00
> > > baud_rate = 19200
> > > desc = HP R3000XR (main rack)
> >
> > (Oops. That's *after* changing to the 19200 rate the driver claims to
> > autodetect.)
> That sound strange. It should hit 19200 direct if it is in the config.
> And the HP R3000XR is communicating at 19200 default. That type
> is the reason the baud changing got into the driver.
Sorry, I confused the issue a little there. I originally had 9600
specified. It failed to connect at 9600, autodetected, and claimed sync
at 19200. When I went back and pasted in the config section, I didn't
realize until too late that I'd pasted the config from *after* editing
to 19200 in before the stage of the process where I'd actually done so.
With the config indicating 19200, it locks immediately at 19200. I just
don't get any UPS "signature" displayed on connection:
babylon4:root:/opt/nut:24 # bin/upsdrvctl start
Network UPS Tools - UPS driver controller 2.4.1
Network UPS Tools - BCMXCP UPS driver 0.21 (2.4.1)
RS-232 communication subdriver 0.17
Connected to UPS on /dev/tty00 with baudrate 19200
babylon4:root:/opt/nut:25 # sbin/upsd
Network UPS Tools upsd 2.4.1
listening on 127.0.0.1 port 3493
listening on ::1 port 3493
/opt/nut/var is world readable
Connected to UPS [tokamak]: bcmxcp-tokamak
Maximum number of connections limited to 256 [requested 1024]
babylon4:root:/opt/nut:26 # bin/upsc tokamak at localhost
Error: Connection failure: Connection refused
> If it say it connect it is talking to the ups. But to be sure about that, you
> may run it in debug mode, like this.
>
> /path/to/bcmxcp -DD -a tokamak
> (stop it by hitting ctrl-c)
>
> Now it would spit out some info. I'm interested in the output. There may
> be some problems how the HP is counting the load-segments.
> It depends on the version of the firmware in the ups.
That generates a lot of output with many repeats. I've edited out most
of the repeats from the end of the following:
debug level is '2'
Connected to UPS on /dev/tty00 with baudrate 19200
Length of meter map: 82
Index Offset Format NUT
0015 0000 61 None
0018 0004 61 input.current
0021 0008 61 None
0023 0012 61 ups.power
0027 0016 51 output.frequency
0028 0020 51 input.frequency
0031 0024 61 None
0033 0028 51 battery.voltage
0034 0032 51 battery.charge
0035 0036 e2 battery.runtime
0056 0040 61 input.voltage
0062 0044 61 ambient.temperature
0065 0048 61 output.current
0068 0052 61 output.current.nominal
0071 0056 61 None
0078 0060 61 output.voltage
Length of alarm map: 27
Index Alarm Supported
0000 INVERTER_AC_OVER_VOLTAGE Yes
0001 INVERTER_AC_UNDER_VOLTAGE Yes
-001 INVERTER_OVER_OR_UNDER_FREQ No
-001 BYPASS_AC_OVER_VOLTAGE No
-001 BYPASS_AC_UNDER_VOLTAGE No
-001 BYPASS_OVER_OR_UNDER_FREQ No
0002 INPUT_AC_OVER_VOLTAGE Yes
0003 INPUT_AC_UNDER_VOLTAGE Yes
0004 INPUT_UNDER_OR_OVER_FREQ Yes
-001 OUTPUT_OVER_VOLTAGE No
-001 OUTPUT_UNDER_VOLTAGE No
-001 OUTPUT_UNDER_OR_OVER_FREQ No
0005 REMOTE_EMERGENCY_PWR_OFF Yes
-001 REMOTE_GO_TO_BYPASS No
-001 BUILDING_ALARM_6 No
-001 BUILDING_ALARM_5 No
-001 BUILDING_ALARM_4 No
-001 BUILDING_ALARM_3 No
-001 BUILDING_ALARM_2 No
-001 BUILDING_ALARM_1 No
-001 STATIC_SWITCH_OVER_TEMP No
-001 CHARGER_OVER_TEMP No
-001 CHARGER_LOGIC_PWR_FAIL No
-001 CHARGER_OVER_VOLTAGE_OR_CURRENT No
-001 INVERTER_OVER_TEMP No
0006 OUTPUT_OVERLOAD Yes
0007 RECTIFIER_INPUT_OVER_CURRENT Yes
0008 INVERTER_OUTPUT_OVER_CURRENT Yes
0009 DC_LINK_OVER_VOLTAGE Yes
-001 DC_LINK_UNDER_VOLTAGE No
-001 RECTIFIER_FAILED No
0010 INVERTER_FAULT Yes
-001 BATTERY_CONNECTOR_FAIL No
-001 BYPASS_BREAKER_FAIL No
0011 CHARGER_FAIL Yes
-001 RAMP_UP_FAILED No
-001 STATIC_SWITCH_FAILED No
-001 ANALOG_AD_REF_FAIL No
-001 BYPASS_UNCALIBRATED No
-001 RECTIFIER_UNCALIBRATED No
-001 OUTPUT_UNCALIBRATED No
-001 INVERTER_UNCALIBRATED No
-001 DC_VOLT_UNCALIBRATED No
-001 OUTPUT_CURRENT_UNCALIBRATED No
-001 RECTIFIER_CURRENT_UNCALIBRATED No
-001 BATTERY_CURRENT_UNCALIBRATED No
-001 INVERTER_ON_OFF_STAT_FAIL No
-001 BATTERY_CURRENT_LIMIT No
-001 INVERTER_STARTUP_FAIL No
-001 ANALOG_BOARD_AD_STAT_FAIL No
-001 OUTPUT_CURRENT_OVER_100 No
-001 BATTERY_GROUND_FAULT No
-001 WAITING_FOR_CHARGER_SYNC No
-001 NV_RAM_FAIL No
-001 ANALOG_BOARD_AD_TIMEOUT No
-001 SHUTDOWN_IMMINENT No
0012 BATTERY_LOW Yes
0013 UTILITY_FAIL Yes
-001 OUTPUT_SHORT_CIRCUIT No
0014 UTILITY_NOT_PRESENT Yes
-001 FULL_TIME_CHARGING No
-001 FAST_BYPASS_COMMAND No
-001 AD_ERROR No
-001 INTERNAL_COM_FAIL No
-001 RECTIFIER_SELFTEST_FAIL No
-001 RECTIFIER_EEPROM_FAIL No
-001 RECTIFIER_EPROM_FAIL No
-001 INPUT_LINE_VOLTAGE_LOSS No
0015 BATTERY_DC_OVER_VOLTAGE Yes
-001 POWER_SUPPLY_OVER_TEMP No
-001 POWER_SUPPLY_FAIL No
-001 POWER_SUPPLY_5V_FAIL No
-001 POWER_SUPPLY_12V_FAIL No
0016 HEATSINK_OVER_TEMP Yes
-001 HEATSINK_TEMP_SENSOR_FAIL No
-001 RECTIFIER_CURRENT_OVER_125 No
-001 RECTIFIER_FAULT_INTERRUPT_FAIL No
-001 RECTIFIER_POWER_CAPASITOR_FAIL No
-001 INVERTER_PROGRAM_STACK_ERROR No
0017 INVERTER_BOARD_SELFTEST_FAIL Yes
-001 INVERTER_AD_SELFTEST_FAIL No
-001 INVERTER_RAM_SELFTEST_FAIL No
-001 NV_MEMORY_CHECKSUM_FAIL No
-001 PROGRAM_CHECKSUM_FAIL No
-001 INVERTER_CPU_SELFTEST_FAIL No
-001 NETWORK_NOT_RESPONDING No
-001 FRONT_PANEL_SELFTEST_FAIL No
-001 NODE_EEPROM_VERIFICATION_ERROR No
-001 OUTPUT_AC_OVER_VOLT_TEST_FAIL No
-001 OUTPUT_DC_OVER_VOLTAGE No
-001 INPUT_PHASE_ROTATION_ERROR No
-001 INVERTER_RAMP_UP_TEST_FAILED No
-001 INVERTER_OFF_COMMAND No
-001 INVERTER_ON_COMMAND No
-001 TO_BYPASS_COMMAND No
-001 FROM_BYPASS_COMMAND No
-001 AUTO_MODE_COMMAND No
-001 EMERGENCY_SHUTDOWN_COMMAND No
-001 SETUP_SWITCH_OPEN No
-001 INVERTER_OVER_VOLT_INT No
-001 INVERTER_UNDER_VOLT_INT No
-001 ABSOLUTE_DCOV_ACOV No
-001 PHASE_A_CURRENT_LIMIT No
-001 PHASE_B_CURRENT_LIMIT No
-001 PHASE_C_CURRENT_LIMIT No
0018 BYPASS_NOT_AVAILABLE Yes
-001 RECTIFIER_BREAKER_OPEN No
-001 BATTERY_CONTACTOR_OPEN No
-001 INVERTER_CONTACTOR_OPEN No
-001 BYPASS_BREAKER_OPEN No
-001 INV_BOARD_ACOV_INT_TEST_FAIL No
-001 INVERTER_OVER_TEMP_TRIP No
-001 INV_BOARD_ACUV_INT_TEST_FAIL No
-001 INVERTER_VOLTAGE_FEEDBACK_ERROR No
-001 DC_UNDER_VOLTAGE_TIMEOUT No
-001 AC_UNDER_VOLTAGE_TIMEOUT No
-001 DC_UNDER_VOLTAGE_WHILE_CHARGE No
-001 INVERTER_VOLTAGE_BIAS_ERROR No
-001 RECTIFIER_PHASE_ROTATION No
-001 BYPASS_PHASER_ROTATION No
-001 SYSTEM_INTERFACE_BOARD_FAIL No
-001 PARALLEL_BOARD_FAIL No
-001 LOST_LOAD_SHARING_PHASE_A No
-001 LOST_LOAD_SHARING_PHASE_B No
-001 LOST_LOAD_SHARING_PHASE_C No
-001 DC_OVER_VOLTAGE_TIMEOUT No
0019 BATTERY_TOTALLY_DISCHARGED Yes
-001 INVERTER_PHASE_BIAS_ERROR No
-001 INVERTER_VOLTAGE_BIAS_ERROR_2 No
-001 DC_LINK_BLEED_COMPLETE No
-001 LARGE_CHARGER_INPUT_CURRENT No
-001 INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
-001 LOSS_OF_REDUNDANCY No
-001 LOSS_OF_SYNC_BUS No
-001 RECTIFIER_BREAKER_SHUNT_TRIP No
-001 LOSS_OF_CHARGER_SYNC No
-001 INVERTER_LOW_LEVEL_TEST_TIMEOUT No
-001 OUTPUT_BREAKER_OPEN No
-001 CONTROL_POWER_ON No
-001 INVERTER_ON No
-001 CHARGER_ON No
-001 BYPASS_ON No
-001 BYPASS_POWER_LOSS No
-001 ON_MANUAL_BYPASS No
-001 BYPASS_MANUAL_TURN_OFF No
-001 INVERTER_BLEEDING_DC_LINK_VOLT No
-001 CPU_ISR_ERROR No
-001 SYSTEM_ISR_RESTART No
-001 PARALLEL_DC No
-001 BATTERY_NEEDS_SERVICE No
-001 BATTERY_CHARGING No
-001 BATTERY_NOT_CHARGED No
-001 DISABLED_BATTERY_TIME No
-001 SERIES_7000_ENABLE No
-001 OTHER_UPS_ON No
-001 PARALLEL_INVERTER No
-001 UPS_IN_PARALLEL No
-001 OUTPUT_BREAKER_REALY_FAIL No
-001 CONTROL_POWER_OFF No
-001 LEVEL_2_OVERLOAD_PHASE_A No
-001 LEVEL_2_OVERLOAD_PHASE_B No
-001 LEVEL_2_OVERLOAD_PHASE_C No
-001 LEVEL_3_OVERLOAD_PHASE_A No
-001 LEVEL_3_OVERLOAD_PHASE_B No
-001 LEVEL_3_OVERLOAD_PHASE_C No
-001 LEVEL_4_OVERLOAD_PHASE_A No
-001 LEVEL_4_OVERLOAD_PHASE_B No
-001 LEVEL_4_OVERLOAD_PHASE_C No
0020 UPS_ON_BATTERY Yes
0021 UPS_ON_BYPASS Yes
0022 LOAD_DUMPED Yes
-001 LOAD_ON_INVERTER No
-001 UPS_ON_COMMAND No
-001 UPS_OFF_COMMAND No
0023 LOW_BATTERY_SHUTDOWN Yes
-001 AUTO_ON_ENABLED No
-001 SOFTWARE_INCOMPABILITY_DETECTED No
-001 INVERTER_TEMP_SENSOR_FAILED No
0024 DC_START_OCCURED Yes
-001 IN_PARALLEL_OPERATION No
-001 SYNCING_TO_BYPASS No
-001 RAMPING_UPS_UP No
-001 INVERTER_ON_DELAY No
-001 CHARGER_ON_DELAY No
-001 WAITING_FOR_UTIL_INPUT No
-001 CLOSE_BYPASS_BREAKER No
-001 TEMPORARY_BYPASS_OPERATION No
-001 SYNCING_TO_OUTPUT No
-001 BYPASS_FAILURE No
-001 AUTO_OFF_COMMAND_EXECUTED No
-001 AUTO_ON_COMMAND_EXECUTED No
0025 BATTERY_TEST_FAILED Yes
-001 FUSE_FAIL No
0026 FAN_FAIL Yes
0027 SITE_WIRING_FAULT Yes
-001 BACKFEED_CONTACTOR_FAIL No
-001 ON_BUCK No
-001 ON_BOOST No
-001 ON_DOUBLE_BOOST No
0028 BATTERIES_DISCONNECTED Yes
-001 UPS_CABINET_OVER_TEMP No
-001 TRANSFORMER_OVER_TEMP No
-001 AMBIENT_UNDER_TEMP No
0029 AMBIENT_OVER_TEMP Yes
-001 CABINET_DOOR_OPEN No
-001 CABINET_DOOR_OPEN_VOLT_PRESENT No
0030 AUTO_SHUTDOWN_PENDING Yes
-001 TAP_SWITCHING_REALY_PENDING No
0031 UNABLE_TO_CHARGE_BATTERIES Yes
-001 STARTUP_FAILURE_CHECK_EPO No
-001 AUTOMATIC_STARTUP_PENDING No
-001 MODEM_FAILED No
-001 INCOMING_MODEM_CALL_STARTED No
-001 OUTGOING_MODEM_CALL_STARTED No
-001 MODEM_CONNECTION_ESTABLISHED No
-001 MODEM_CALL_COMPLETED_SUCCESS No
Lengt of Config_block: 80
Length of statistics map: 0
Lengt of command list: 25
Lengt of outlet_block: 20
Lengt of alarm_block: 31
Number of outlets: 3
Number of bytes: 6
Outlet number: 1
Outlet state: 1
Auto delay off: -1
Auto delay on: 1
Outlet number: 2
Outlet state: 1
Auto delay off: -1
Auto delay on: 2
Outlet number: 3
Outlet state: 1
Auto delay off: -1
Auto delay on: 3
Number of outlets: 3
Number of bytes: 6
Outlet number: 1
Outlet state: 1
Auto delay off: -1
Auto delay on: 1
Outlet number: 2
Outlet state: 1
Auto delay off: -1
Auto delay on: 2
Outlet number: 3
Outlet state: 1
Auto delay off: -1
Auto delay on: 3
dstate_init: sock /opt/nut/var/bcmxcp-tokamak open on fd 6
Number of outlets: 3
Number of bytes: 6
Outlet number: 1
Outlet state: 1
Auto delay off: -1
Auto delay on: 1
Outlet number: 2
Outlet state: 1
Auto delay off: -1
Auto delay on: 2
Outlet number: 3
Outlet state: 1
Auto delay off: -1
Auto delay on: 3
Signal 2: exiting
Network UPS Tools - BCMXCP UPS driver 0.21 (2.4.1)
RS-232 communication subdriver 0.17
--
Phil Stracchino, CDK#2 DoD#299792458 ICBM: 43.5607, -71.355
alaric at caerllewys.net alaric at metrocast.net phil at co.ordinate.org
Renaissance Man, Unix ronin, Perl hacker, Free Stater
It's not the years, it's the mileage.
More information about the Nut-upsuser
mailing list