[Nut-upsuser] TrippLite Eco Series UPS
    Arjen de Korte 
    nut+users at de-korte.org
       
    Mon Sep 21 18:09:55 UTC 2009
    
    
  
Citeren Lindsey Chesnutt <mrchesnutt op gmail.com>:
> I've attached the requested output.
Although it didn't make it to the list (because we don't allow  
attachments larger than 40 kB), I received it directly.
>   0.272003	HID descriptor, method 1: (9 bytes) => 09 21 10 01 00 01 22 c9 01
>   0.272075	i=0, extra[i]=09, extra[i+1]=21
>   0.272146	HID descriptor, method 2: (9 bytes) => 09 21 10 01 00 01 22 c9 01
>   0.272212	HID descriptor length 457
>   0.766975	Report Descriptor size = 457
That's a fairly short report descriptor for a HID PDC device. It is a  
valid one though, but it just doesn't have a lot of reports in it. I  
think we already support most of it as it is and that it doesn't  
report battery voltage. The only report that comes close is
>   0.968349	Entering libusb_get_report
>   0.984961	Report[get]: (3 bytes) => 31 b9 04
>   0.985031	PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
>   0.985099	Unit = 00000000, UnitExp = 0
>   0.985164	Exponent = 0
>   0.985230	hid_lookup_path: 00840004 -> UPS
>   0.985298	hid_lookup_path: 00840024 -> PowerSummary
>   0.985365	hid_lookup_path: 00840002 -> PresentStatus
>   0.985432	hid_lookup_path: 00840030 -> Voltage
>   0.985520	Path: UPS.PowerSummary.PresentStatus.Voltage, Type:  
> Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 1209.000000
This could be the battery voltage times 100, but in that case the  
value is surprisingly low (a few tenths of a second before, it  
reported a fully charged battery). It could also mean the input or  
output voltage (or something completely unrelated). There is no way to  
tell without digging deeper into this.
The remainder of the reports are either already supported or vendor  
specific ones. If you're willing to work with us, we might attempt to  
figure out what these mean. Please let us know if you're able to do so  
(this will probably require frequent updates of the driver with lot of  
debugging enabled) and we'll continue on the development mailing list.
Best regards, Arjen
-- 