[Nut-upsuser] Belkin Regulator Pro dropping connection and halting
John Bayly
freebsd.ports at tipstrade.net
Wed Dec 1 12:42:01 UTC 2010
I've a Belkin Regulator Pro (F6C1400-EUR) connected via serial to a
FreeBSD machine using NUT v.2.4.3
Sometimes I get a series of logged messages saying that the data is
switching between stale and valid, this in itself isn't an issue,
however occasionally when the communication is re-established, upsmon
gets a "On battery" message followed quickly by "Battery low" message,
and calls on the system to halt. I know for a fact that the battery
isn't low at any stage, as other UPSs have not reported a loss of power.
This behaviour has only started occurring since using NUT rather than
Belkin Bulldog (not supported on FreeBSD x64).
Dec 1 08:02:46 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:02:47 rack upsmon[957]: Communications with UPS
belkinreg at localhost established
Dec 1 08:02:48 rack upsd[941]: Data for UPS [belkinreg] is stale -
check driver
Dec 1 08:02:52 rack upsmon[957]: Poll UPS [belkinreg at localhost] failed
- Data stale
Dec 1 08:02:52 rack upsmon[957]: Communications with UPS
belkinreg at localhost lost
Dec 1 08:02:57 rack upsmon[957]: Poll UPS [belkinreg at localhost] failed
- Data stale
Dec 1 08:02:59 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:03:00 rack upsd[941]: Data for UPS [belkinreg] is stale -
check driver
Dec 1 08:03:02 rack upsmon[957]: Poll UPS [belkinreg at localhost] failed
- Data stale
Dec 1 08:03:27 rack last message repeated 5 times
Dec 1 08:03:32 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:03:32 rack upsmon[957]: Communications with UPS
belkinreg at localhost established
Dec 1 08:03:34 rack upsd[941]: Data for UPS [belkinreg] is stale -
check driver
Dec 1 08:03:37 rack upsmon[957]: Poll UPS [belkinreg at localhost] failed
- Data stale
Dec 1 08:03:37 rack upsmon[957]: Communications with UPS
belkinreg at localhost lost
Dec 1 08:03:42 rack upsmon[957]: Poll UPS [belkinreg at localhost] failed
- Data stale
...
Dec 1 08:03:52 rack upsmon[957]: Poll UPS [belkinreg at localhost] failed
- Data stale
Dec 1 08:03:52 rack upsmon[957]: Communications with UPS
belkinreg at localhost lost
Dec 1 08:03:57 rack upsd[941]: UPS [belkinreg] data is no longer stale
Dec 1 08:03:57 rack upsmon[957]: Communications with UPS
belkinreg at localhost established
Dec 1 08:03:57 rack upsmon[957]: UPS belkinreg at localhost on battery
Dec 1 08:03:57 rack upsmon[957]: UPS belkinreg at localhost battery is low
Dec 1 08:03:57 rack upsmon[957]: Executing automatic power-fail shutdown
Dec 1 08:03:57 rack upsmon[957]: Auto logout and shutdown proceeding
I can see no reason why the NUT is seeing a battery low message.
Unfortunately there is only a 5 minute resolution for the ups log:
20101201 072111 100 238.7 022 [OL] 012 50.1
20101201 072611 NA NA NA [NA] NA NA
20101201 073111 NA NA NA [NA] NA NA
20101201 073611 000 000.0 2400 [OL] 000 0.0
20101201 074111 NA NA NA [NA] NA NA
20101201 074611 NA NA NA [NA] NA NA
20101201 075111 NA NA NA [NA] NA NA
20101201 075611 NA NA NA [NA] NA NA
20101201 080111 NA NA NA [NA] NA NA
20101201 090322 NA NA NA [WAIT] NA NA
20101201 090822 100 234.5 024 [OL] 017 49.9
20101201 091348 NA NA NA [WAIT] NA NA
20101201 091848 100 236.7 022 [OL] 017 50.0
20101201 092348 100 235.7 022 [OL] 017 49.9
Has anyone got any suggestions?
John