Citeren ahouse-support <support op ahouse.mine.nu>:

> # ./nut start
> Network UPS Tools - UPS driver controller 2.4.1
> Network UPS Tools - Megatec/Q1 protocol serial driver 1.51 (2.4.1)
> Supported UPS detected with megatec protocol
> Vendor information read in 1 tries
> Battery runtime will not be calculated (runtimecal not set)  
> <================= !!!

RTFM - 'man 8 blazer'.

> backup# upsc Powercom op localhost
> battery.voltage: 28.80 <========= !!! it is a normal? what u thing  
> about this value??  iam have 4x7AH battery in Ups

This boils down to about 2.4 V / cell, which is fairly high for a PbAc  
battery. But please understand that a UPS is not a measuring  
instrument. More often than not, the reported resolution is much more  
than the accuracy of the measurement justifies. So unless your  
batteries wear out quickly, you can safely ignore this.

Best regards, Arjen
-- 