[Nut-upsuser] Setting Battery Runtime Low
    Arnaud Quette 
    aquette.dev at gmail.com
       
    Thu Dec 16 11:43:43 UTC 2010
    
    
  
2010/12/15 Arjen de Korte
> Citeren "Poulton, Stuart W.L.":
>
>  rcs-manage-1:/var/log # upsrw  phys-eaton
>> [battery.runtime.low]
>> Remaining battery runtime when UPS switches to LB (seconds)
>> Type: UNKNOWN (unrecognized)
>>
>
> The definition in the MIB to NUT mapping is lacking a type for this
> variable. Clients expect it to be either a string or an enumerated value and
> the driver doesn't report either. This needs to be fixed in the driver,
> there is no workaround.
>
>
>  I suspect from this that it may not be configurable.
>>
>
> Maybe, but until this is fixed in the driver it's a driver bug. Note that
> the snmp-ups driver is currently in dire need of an active developer taking
> over the maintenance.
indeed, and a full rewrite is also needed, to support the subdrivers
approach as in usbhid-ups.
this would fix various issues and limitations, and would also unblock a few
patch that are stagging in my TODO stack.
> Since I don't have a SNMP capable UPS, I can't really work on it other than
> the occasional fix for an obvious problem.
>
well, your NMC (in the evolution) is SNMP capable (beside the XML/HTTP
channel).
depending on your exact card reference and FW version, it will expose a
minimum or full set of IETF + MGE MIBS.
Arjen: if needed, I can also check to send you a more suitable card, but I
know that you're already quite busy.
so up to you, you know who to ask ;-)
cheers,
Arnaud
-- 
Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20101216/a5181185/attachment.htm>
    
    
More information about the Nut-upsuser
mailing list