[Nut-upsuser] HP R1500 G2 UPS
Arjen de Korte
nut+users at de-korte.org
Fri Feb 19 11:30:50 UTC 2010
Citeren Kjell Claesson <kjell.claesson op epost.tidanet.se>:
>> ups.alarm: BATTERIES_DISCONNECTED
>
>> ups.status: ALARM OL
>>
> Can you confirm that you have disconnected the battery.
> So we don't have a problem parsing the alarm block.
The values reported from the UPS look suspect.
Both battery.voltage and battery.charge look really low for a UPS that
is running on mains and the ambient.temperature is a bit high. These
could be correct if the mains voltage has just returned after an
outage or a battery test was just finished. If this is not the case,
I'd say the battery is bad and needs to be replaced.
Best regards, Arjen
--