[Nut-upsuser] HP R1500 G2 UPS
Schupfer Stephan
Stephan.Schupfer at ksengineers.at
Fri Feb 19 12:57:37 UTC 2010
Sorry the UPS was in kind of strange state hat to switch it off and restart
Battery disconnected was also reported by the original HP software on another system
Temp can be that high because a server rack is direct on the UPS rack - no airflow inbetween - just for testing reasons
Now the new upsc (everything in normal operational state now)
ambient.temperature: 46
ambient.temperature.high: 75
battery.charge: 95
battery.runtime: 1476
battery.voltage: 39.20
driver.name: bcmxcp
driver.parameter.baud_rate: 9600
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS1
driver.version: 2.4.1
driver.version.internal: 0.21
input.frequency: 50.00
input.frequency.high: 55
input.frequency.low: 45
input.frequency.nominal: 50
input.transfer.boost.high: 207
input.transfer.high: 266
input.transfer.low: 194
input.transfer.trim.low: 243
input.voltage: 231
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 0
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 1
outlet.2.id: 2
outlet.2.status: On
output.current: 1.9
output.current.nominal: 6.4
output.frequency: 50.00
output.phases: 1
output.voltage: 231
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.firmware: Cont:02.00 Inve:02.00
ups.load: 29.3
ups.model: HP R1500 G2 1500VA
ups.power: 439
ups.power.nominal: 1500
ups.serial: 3C88431991
ups.status: OL
-----Ursprüngliche Nachricht-----
Von: Kjell Claesson [mailto:kjell.claesson at epost.tidanet.se]
Gesendet: Freitag, 19. Februar 2010 11:55
An: nut-upsuser at lists.alioth.debian.org
Cc: Schupfer Stephan
Betreff: Re: [Nut-upsuser] HP R1500 G2 UPS
Hi Stephan,
> ups.alarm: BATTERIES_DISCONNECTED
> ups.status: ALARM OL
>
Can you confirm that you have disconnected the battery.
So we don't have a problem parsing the alarm block.
/Kjell