[Nut-upsuser] NUT with Eaton 9135 6000
Arnaud Quette
arnaud.quette at free.fr
Wed Mar 3 20:19:05 UTC 2010
Hi Dag
2010/3/1 Dag Atle Nettum <dagatle at innit.no>:
> Here are the ressult, send me a mail if I should test something.
Arjen de Korte has made the needed fix (conversion from Kelvin to
Celsius) in the development tree (r2385).
You can either checkout the development tree (subversion trunk) or get
the latest snapshot:
http://buildbot.ghz.cc/~buildbot/docs/latest/website/download.html#_development_tree_2_5
please confirm that your issue is fixed, cc'ing the NUT Users list.
thanks to Arjen,
Arnaud
-------------- next part --------------
nagios:~# upsc ups-u01
battery.capacity: 15.00
battery.charge: 100
battery.charge.low: 20
battery.charge.restart: 0
battery.energysave: no
battery.protection: yes
battery.runtime: 3264
battery.type: PbAc
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.1
driver.version.data: MGE HID 1.12
driver.version.internal: 0.34
input.bypass.current: 0.00
input.bypass.frequency: 50.0
input.bypass.frequency.nominal: 50
input.bypass.voltage: 236.0
input.current: 7.90
input.frequency: 50.0
input.frequency.nominal: 50
input.voltage: 236.0
outlet.1.autoswitch.charge.low: 0
outlet.1.delay.shutdown: 16777215
outlet.1.delay.start: 0
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.status: on
outlet.1.switchable: yes
outlet.2.autoswitch.charge.low: 0
outlet.2.delay.shutdown: 16777215
outlet.2.delay.start: 0
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.status: on
outlet.2.switchable: yes
outlet.desc: Main Outlet
outlet.id: 0
outlet.switchable: no
output.current: 7.90
output.frequency: 50.0
output.frequency.nominal: 50
output.powerfactor: 0.86
output.voltage: 229.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 00F
ups.load: 38
ups.load.high: 105
ups.mfr: EATON POWERWARE
ups.model: 9135 6000
ups.power: 1864
ups.power.nominal: 6000
ups.productid: ffff
ups.realpower: 1609
ups.realpower.nominal: 4200
ups.serial: CB425A5018
ups.start.auto: yes
ups.start.battery: no
ups.start.reboot: yes
ups.status: OL CHRG
ups.temperature: 294.0
ups.test.interval: 604800
ups.test.result: Done and passed
ups.timer.shutdown: -1
ups.timer.start: -1
ups.type: online
ups.vendorid: 0463
More information about the Nut-upsuser
mailing list