[Nut-upsuser] Getting 'Data stale' error with bcmxcp_usb for a PowerWare 5115 on OSX

Charlie Garrison garrison at zeta.org.au
Fri Mar 5 08:55:00 UTC 2010


Good evening,

I tried getting this to work a couple years back but didn't have 
enough time to do all the debugging that was needed (apologies 
to the devs who tried to help at that time). It's working much 
better now, but I'm still not able to get an answer from upsc. 
Can anyone help me work out why I'm getting the error when 
querying with upsc:

Error: Data stale

My environment:

OSX 10.5.8
NUT 2.4.3 (also tried with latest svn)
PowerWare 5115, USB version

I'm able to compile/install without problems using (newly 
created user/group):

$ ./configure --with-user=ups --with-group=nut --with-usb --with-drivers=bcmxcp_usb

I added following to ups.conf:

[powerware5115]
     driver = bcmxcp_usb
     port = auto
     desc = "Workstation"

And I added LISTEN lines for both localhost and internal IP to upsd.conf.

LISTEN 192.168.1.10
LISTEN 127.0.0.1

And the following to upsd.users:

[nobody]
         password  = <hidden>
         upsmon master

And upsmon.conf:

MONITOR powerware5115 at localhost 1 nobody <hidden> master

The driver/daemons seem to run fine (except for error with upsmon):

$ sudo /usr/local/ups/bin/upsdrvctl start
Network UPS Tools - UPS driver controller 2.4.3-2392
Network UPS Tools - BCMXCP UPS driver 0.23 (2.4.3-2392)
USB communication subdriver 0.18

$ sudo /usr/local/ups/sbin/upsd
Network UPS Tools upsd 2.4.3-2392
listening on 127.0.0.1 port 3493
listening on 192.168.1.10 port 3493
Connected to UPS [powerware5115]: bcmxcp_usb-powerware5115

$ sudo /usr/local/ups/sbin/upsmon
Network UPS Tools upsmon 2.4.3-2392
Using power down flag file /etc/killpower
UPS: powerware5115 at localhost (master) (power value 1)

Broadcast Message from charlie at workstation.garrison.com.au
         (no tty) at 19:49 EST...

Communications with UPS powerware5115 at localhost lost

Broadcast Message from charlie at workstation.garrison.com.au
         (no tty) at 19:49 EST...

UPS powerware5115 at localhost is unavailable


But I can't query the UPS:

$ /usr/local/ups/bin/upsc powerware5115
Error: Data stale

I can't see any errors from the driver in debug mode:

$ sudo /usr/local/ups/bin/bcmxcp_usb -DD -a powerware5115

[debug output below]

What can I do to troubleshoot this problem (assuming it should 
work to begin with)?

Thanks,
Charlie



Network UPS Tools - BCMXCP UPS driver 0.23 (2.4.3-2392)
USB communication subdriver 0.18
    0.000000 debug level is '2'
    0.329754 device 002-06da-0002-00-00 opened successfully
    0.332582 entering get_answer(31)
    1.083837 get_answer: (166 bytes) => ab 01 74 01 02 00 01 05 
10 00 14 00 01 00 13 35
    1.083919  31 31 35 31 30 30 30 41 20 20 20 20 20 20 20 20 20 
20 51 00 00 00 00 00 00
    1.084676  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 f0 00 
f0 00 00 00 52 52 00 00
    1.084704  00 00 52 f0 e2 00 00 00 00 00 00 00 00 00 00 00 00 
00 00 00 00 00 00 00 00
    1.084729  f0 00 00 f0 00 00 f0 00 00 41 00 00 41 00 00 f0 00 
00 00 00 00 00 f0 00 00
    1.084755  1b c0 01 00 8a ab 01 28 82 82 04 00 80 0b 00 00 00 
00 00 00 00 40 00 00 00
    1.084780  00 00 05 00 80 06 08 00 50 00 00 00 00 00 00 03 00 
1b 18 00 00 00 11 00 2f
    1.084794 get_answer: block_number = 1
    1.084807 get_answer: sequence number (1) is ok
    1.084821 get_answer: checksum is ok
    1.084846 get_answer: block_number = 1
    1.084861 get_answer: sequence number (2) is ok
    1.084874 get_answer: checksum is ok
    1.084888 get_answer: all data received
    1.085396 Length of meter map: 81

    1.085490 Index   Offset  Format  NUT

    1.085545 0021    0000    f0  None
    1.085560 0023    0004    f0  ups.power
    1.085601 0027    0008    52  output.frequency
    1.085618 0028    0012    52  input.frequency
    1.085632 0033    0016    52  battery.voltage
    1.085673 0034    0020    f0  battery.charge
    1.085688 0035    0024    e2  battery.runtime
    1.085729 0056    0028    f0  input.voltage
    1.085745 0059    0032    f0  None
    1.085760 0062    0036    f0  ambient.temperature
    1.085800 0065    0040    41  output.current
    1.085815 0068    0044    41  output.current.nominal
    1.085856 0071    0048    f0  None
    1.085871 0078    0052    f0  output.voltage
    1.085885

    1.085925 Length of alarm map: 27

    1.085939 Index   Alarm   Supported

    1.085982 -001    INVERTER_AC_OVER_VOLTAGE    No
    1.085997 -001    INVERTER_AC_UNDER_VOLTAGE   No
    1.086011 -001    INVERTER_OVER_OR_UNDER_FREQ No
    1.086053 -001    BYPASS_AC_OVER_VOLTAGE  No
    1.092701 -001    BYPASS_AC_UNDER_VOLTAGE No
    1.092940 -001    BYPASS_OVER_OR_UNDER_FREQ   No
    1.092965 0000    INPUT_AC_OVER_VOLTAGE   Yes
    1.092980 0001    INPUT_AC_UNDER_VOLTAGE  Yes
    1.092994 0002    INPUT_UNDER_OR_OVER_FREQ    Yes
    1.099344 -001    OUTPUT_OVER_VOLTAGE No
    1.099366 -001    OUTPUT_UNDER_VOLTAGE    No
    1.099380 -001    OUTPUT_UNDER_OR_OVER_FREQ   No
    1.099395 -001    REMOTE_EMERGENCY_PWR_OFF    No
    1.099409 -001    REMOTE_GO_TO_BYPASS No
    1.099423 -001    BUILDING_ALARM_6    No
    1.099437 -001    BUILDING_ALARM_5    No
    1.099451 -001    BUILDING_ALARM_4    No
    1.099465 -001    BUILDING_ALARM_3    No
    1.099479 -001    BUILDING_ALARM_2    No
    1.099493 -001    BUILDING_ALARM_1    No
    1.099507 -001    STATIC_SWITCH_OVER_TEMP No
    1.099522 -001    CHARGER_OVER_TEMP   No
    1.099536 -001    CHARGER_LOGIC_PWR_FAIL  No
    1.099550 -001    CHARGER_OVER_VOLTAGE_OR_CURRENT No
    1.099564 -001    INVERTER_OVER_TEMP  No
    1.099884 0003    OUTPUT_OVERLOAD Yes
    1.099900 -001    RECTIFIER_INPUT_OVER_CURRENT    No
    1.099914 -001    INVERTER_OUTPUT_OVER_CURRENT    No
    1.099928 -001    DC_LINK_OVER_VOLTAGE    No
    1.099943 -001    DC_LINK_UNDER_VOLTAGE   No
    1.099957 -001    RECTIFIER_FAILED    No
    1.099971 0004    INVERTER_FAULT  Yes
    1.099985 -001    BATTERY_CONNECTOR_FAIL  No
    1.099999 -001    BYPASS_BREAKER_FAIL No
    1.100013 0005    CHARGER_FAIL    Yes
    1.100028 -001    RAMP_UP_FAILED  No
    1.100042 -001    STATIC_SWITCH_FAILED    No
    1.100056 -001    ANALOG_AD_REF_FAIL  No
    1.100070 -001    BYPASS_UNCALIBRATED No
    1.100084 -001    RECTIFIER_UNCALIBRATED  No
    1.100098 -001    OUTPUT_UNCALIBRATED No
    1.100112 -001    INVERTER_UNCALIBRATED   No
    1.100127 -001    DC_VOLT_UNCALIBRATED    No
    1.100141 -001    OUTPUT_CURRENT_UNCALIBRATED No
    1.100155 -001    RECTIFIER_CURRENT_UNCALIBRATED  No
    1.100169 -001    BATTERY_CURRENT_UNCALIBRATED    No
    1.100183 -001    INVERTER_ON_OFF_STAT_FAIL   No
    1.100198 -001    BATTERY_CURRENT_LIMIT   No
    1.100212 -001    INVERTER_STARTUP_FAIL   No
    1.100725 -001    ANALOG_BOARD_AD_STAT_FAIL   No
    1.100744 -001    OUTPUT_CURRENT_OVER_100 No
    1.100759 -001    BATTERY_GROUND_FAULT    No
    1.100773 -001    WAITING_FOR_CHARGER_SYNC    No
    1.100787 -001    NV_RAM_FAIL No
    1.100802 -001    ANALOG_BOARD_AD_TIMEOUT No
    1.100816 0006    SHUTDOWN_IMMINENT   Yes
    1.100830 0007    BATTERY_LOW Yes
    1.100845 0008    UTILITY_FAIL    Yes
    1.100859 -001    OUTPUT_SHORT_CIRCUIT    No
    1.100874 0009    UTILITY_NOT_PRESENT Yes
    1.100888 -001    FULL_TIME_CHARGING  No
    1.100902 -001    FAST_BYPASS_COMMAND No
    1.100916 -001    AD_ERROR    No
    1.100930 -001    INTERNAL_COM_FAIL   No
    1.100944 -001    RECTIFIER_SELFTEST_FAIL No
    1.100959 -001    RECTIFIER_EEPROM_FAIL   No
    1.100973 -001    RECTIFIER_EPROM_FAIL    No
    1.100987 -001    INPUT_LINE_VOLTAGE_LOSS No
    1.101001 -001    BATTERY_DC_OVER_VOLTAGE No
    1.101015 -001    POWER_SUPPLY_OVER_TEMP  No
    1.101029 -001    POWER_SUPPLY_FAIL   No
    1.101043 -001    POWER_SUPPLY_5V_FAIL    No
    1.101058 -001    POWER_SUPPLY_12V_FAIL   No
    1.101072 -001    HEATSINK_OVER_TEMP  No
    1.102622 -001    HEATSINK_TEMP_SENSOR_FAIL   No
    1.102651 -001    RECTIFIER_CURRENT_OVER_125  No
    1.102665 -001    RECTIFIER_FAULT_INTERRUPT_FAIL  No
    1.102680 -001    RECTIFIER_POWER_CAPASITOR_FAIL  No
    1.102694 -001    INVERTER_PROGRAM_STACK_ERROR    No
    1.102708 -001    INVERTER_BOARD_SELFTEST_FAIL    No
    1.102722 -001    INVERTER_AD_SELFTEST_FAIL   No
    1.102737 -001    INVERTER_RAM_SELFTEST_FAIL  No
    1.102751 -001    NV_MEMORY_CHECKSUM_FAIL No
    1.102765 -001    PROGRAM_CHECKSUM_FAIL   No
    1.102779 -001    INVERTER_CPU_SELFTEST_FAIL  No
    1.102793 -001    NETWORK_NOT_RESPONDING  No
    1.102807 -001    FRONT_PANEL_SELFTEST_FAIL   No
    1.102821 -001    NODE_EEPROM_VERIFICATION_ERROR  No
    1.102835 -001    OUTPUT_AC_OVER_VOLT_TEST_FAIL   No
    1.102849 -001    OUTPUT_DC_OVER_VOLTAGE  No
    1.102863 -001    INPUT_PHASE_ROTATION_ERROR  No
    1.102877 -001    INVERTER_RAMP_UP_TEST_FAILED    No
    1.102891 -001    INVERTER_OFF_COMMAND    No
    1.102905 -001    INVERTER_ON_COMMAND No
    1.102919 -001    TO_BYPASS_COMMAND   No
    1.102933 -001    FROM_BYPASS_COMMAND No
    1.103699 -001    AUTO_MODE_COMMAND   No
    1.103735 -001    EMERGENCY_SHUTDOWN_COMMAND  No
    1.103750 -001    SETUP_SWITCH_OPEN   No
    1.103960 -001    INVERTER_OVER_VOLT_INT  No
    1.103992 -001    INVERTER_UNDER_VOLT_INT No
    1.104007 -001    ABSOLUTE_DCOV_ACOV  No
    1.104020 -001    PHASE_A_CURRENT_LIMIT   No
    1.104034 -001    PHASE_B_CURRENT_LIMIT   No
    1.104048 -001    PHASE_C_CURRENT_LIMIT   No
    1.104062 -001    BYPASS_NOT_AVAILABLE    No
    1.104076 -001    RECTIFIER_BREAKER_OPEN  No
    1.104090 -001    BATTERY_CONTACTOR_OPEN  No
    1.104104 -001    INVERTER_CONTACTOR_OPEN No
    1.104119 -001    BYPASS_BREAKER_OPEN No
    1.104133 -001    INV_BOARD_ACOV_INT_TEST_FAIL    No
    1.104147 -001    INVERTER_OVER_TEMP_TRIP No
    1.104161 -001    INV_BOARD_ACUV_INT_TEST_FAIL    No
    1.104175 -001    INVERTER_VOLTAGE_FEEDBACK_ERROR No
    1.104189 -001    DC_UNDER_VOLTAGE_TIMEOUT    No
    1.104203 -001    AC_UNDER_VOLTAGE_TIMEOUT    No
    1.104217 -001    DC_UNDER_VOLTAGE_WHILE_CHARGE   No
    1.104231 -001    INVERTER_VOLTAGE_BIAS_ERROR No
    1.104245 -001    RECTIFIER_PHASE_ROTATION    No
    1.104259 -001    BYPASS_PHASER_ROTATION  No
    1.104273 -001    SYSTEM_INTERFACE_BOARD_FAIL No
    1.104287 -001    PARALLEL_BOARD_FAIL No
    1.105313 -001    LOST_LOAD_SHARING_PHASE_A   No
    1.105344 -001    LOST_LOAD_SHARING_PHASE_B   No
    1.105393 -001    LOST_LOAD_SHARING_PHASE_C   No
    1.105408 -001    DC_OVER_VOLTAGE_TIMEOUT No
    1.105423 0010    BATTERY_TOTALLY_DISCHARGED  Yes
    1.105463 -001    INVERTER_PHASE_BIAS_ERROR   No
    1.105477 -001    INVERTER_VOLTAGE_BIAS_ERROR_2   No
    1.105518 -001    DC_LINK_BLEED_COMPLETE  No
    1.105533 -001    LARGE_CHARGER_INPUT_CURRENT No
    1.105547 -001    INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
    1.105589 -001    LOSS_OF_REDUNDANCY  No
    1.105603 -001    LOSS_OF_SYNC_BUS    No
    1.105646 -001    RECTIFIER_BREAKER_SHUNT_TRIP    No
    1.105661 -001    LOSS_OF_CHARGER_SYNC    No
    1.105675 -001    INVERTER_LOW_LEVEL_TEST_TIMEOUT No
    1.105717 -001    OUTPUT_BREAKER_OPEN No
    1.105731 -001    CONTROL_POWER_ON    No
    1.105772 -001    INVERTER_ON No
    1.105787 -001    CHARGER_ON  No
    1.105801 -001    BYPASS_ON   No
    1.105843 -001    BYPASS_POWER_LOSS   No
    1.105857 -001    ON_MANUAL_BYPASS    No
    1.105899 -001    BYPASS_MANUAL_TURN_OFF  No
    1.105914 -001    INVERTER_BLEEDING_DC_LINK_VOLT  No
    1.105928 -001    CPU_ISR_ERROR   No
    1.105970 -001    SYSTEM_ISR_RESTART  No
    1.105984 -001    PARALLEL_DC No
    1.106025 -001    BATTERY_NEEDS_SERVICE   No
    1.106040 -001    BATTERY_CHARGING    No
    1.106054 -001    BATTERY_NOT_CHARGED No
    1.106096 -001    DISABLED_BATTERY_TIME   No
    1.106110 -001    SERIES_7000_ENABLE  No
    1.106152 -001    OTHER_UPS_ON    No
    1.106166 -001    PARALLEL_INVERTER   No
    1.106180 -001    UPS_IN_PARALLEL No
    1.106222 -001    OUTPUT_BREAKER_REALY_FAIL   No
    1.106237 -001    CONTROL_POWER_OFF   No
    1.106277 -001    LEVEL_2_OVERLOAD_PHASE_A    No
    1.106292 -001    LEVEL_2_OVERLOAD_PHASE_B    No
    1.106306 -001    LEVEL_2_OVERLOAD_PHASE_C    No
    1.106443 -001    LEVEL_3_OVERLOAD_PHASE_A    No
    1.106457 -001    LEVEL_3_OVERLOAD_PHASE_B    No
    1.106472 -001    LEVEL_3_OVERLOAD_PHASE_C    No
    1.106486 -001    LEVEL_4_OVERLOAD_PHASE_A    No
    1.106500 -001    LEVEL_4_OVERLOAD_PHASE_B    No
    1.106514 -001    LEVEL_4_OVERLOAD_PHASE_C    No
    1.106561 0011    UPS_ON_BATTERY  Yes
    1.106575 -001    UPS_ON_BYPASS   No
    1.106590 0012    LOAD_DUMPED Yes
    1.106629 -001    LOAD_ON_INVERTER    No
    1.106644 -001    UPS_ON_COMMAND  No
    1.106685 -001    UPS_OFF_COMMAND No
    1.106699 -001    LOW_BATTERY_SHUTDOWN    No
    1.106713 -001    AUTO_ON_ENABLED No
    1.106756 -001    SOFTWARE_INCOMPABILITY_DETECTED No
    1.106770 -001    INVERTER_TEMP_SENSOR_FAILED No
    1.106811 -001    DC_START_OCCURED    No
    1.106825 -001    IN_PARALLEL_OPERATION   No
    1.106840 -001    SYNCING_TO_BYPASS   No
    1.106881 -001    RAMPING_UPS_UP  No
    1.106896 -001    INVERTER_ON_DELAY   No
    1.106910 -001    CHARGER_ON_DELAY    No
    1.106924 -001    WAITING_FOR_UTIL_INPUT  No
    1.107084 -001    CLOSE_BYPASS_BREAKER    No
    1.107190 -001    TEMPORARY_BYPASS_OPERATION  No
    1.107210 -001    SYNCING_TO_OUTPUT   No
    1.107224 -001    BYPASS_FAILURE  No
    1.107239 -001    AUTO_OFF_COMMAND_EXECUTED   No
    1.107253 -001    AUTO_ON_COMMAND_EXECUTED    No
    1.107266 0013    BATTERY_TEST_FAILED Yes
    1.107281 -001    FUSE_FAIL   No
    1.107295 0014    FAN_FAIL    Yes
    1.107309 0015    SITE_WIRING_FAULT   Yes
    1.107323 -001    BACKFEED_CONTACTOR_FAIL No
    1.107337 -001    ON_BUCK No
    1.107351 -001    ON_BOOST    No
    1.107365 -001    ON_DOUBLE_BOOST No
    1.107379 -001    BATTERIES_DISCONNECTED  No
    1.107393 -001    UPS_CABINET_OVER_TEMP   No
    1.107407 -001    TRANSFORMER_OVER_TEMP   No
    1.107421 -001    AMBIENT_UNDER_TEMP  No
    1.107435 0016    AMBIENT_OVER_TEMP   Yes
    1.107449 -001    CABINET_DOOR_OPEN   No
    1.107463 -001    CABINET_DOOR_OPEN_VOLT_PRESENT  No
    1.107477 -001    AUTO_SHUTDOWN_PENDING   No
    1.107491 -001    TAP_SWITCHING_REALY_PENDING No
    1.107505 -001    UNABLE_TO_CHARGE_BATTERIES  No
    1.107520 -001    STARTUP_FAILURE_CHECK_EPO   No
    1.107534 -001    AUTOMATIC_STARTUP_PENDING   No
    1.110475 -001    MODEM_FAILED    No
    1.110496 -001    INCOMING_MODEM_CALL_STARTED No
    1.110542 -001    OUTGOING_MODEM_CALL_STARTED No
    1.110557 -001    MODEM_CONNECTION_ESTABLISHED    No
    1.110597 -001    MODEM_CALL_COMPLETED_SUCCESS    No
    1.110611

    1.110625 Length of Config_block: 80

    1.110667 Length of statistics map: 0

    1.110681 Length of command list: 24

    1.110723 Length of outlet_block: 0

    1.110738 Length of alarm_block: 17

    1.112595 entering get_answer(36)
    1.531682 get_answer: (85 bytes) => ab 06 50 81 23 01 ce c7 
00 11 f4 01 f0 00 32 00
    1.532055  00 00 00 33 ba 00 00 00 00 00 c9 0a a0 00 01 00 00 
00 04 08 00 00 00 00 00
    1.532081  01 05 10 00 00 00 00 00 00 00 1f 35 31 31 35 31 30 
30 30 41 20 20 20 20 20
    1.532104  20 20 55 58 32 30 35 41 30 35 37 37 20 20 20 20 20 
20 35
    1.532118 get_answer: block_number = 6
    1.532132 get_answer: sequence number (1) is ok
    1.532146 get_answer: checksum is ok
    1.532160 get_answer: all data received
    1.535766 entering get_answer(3c)
    1.755718 get_answer: (36 bytes) => ab 0c 1f 81 f0 00 32 00 
0d 00 43 30 f4 01 d8 00
    1.755779  fe 00 00 00 02 01 ca 00 16 01 00 00 00 00 4b 01 00 
00 00 0c
    1.755841 get_answer: block_number = c
    1.755859 get_answer: sequence number (1) is ok
    1.755873 get_answer: checksum is ok
    1.755886 get_answer: all data received
    1.755935 entering init_command_map()
    1.757669 entering get_answer(40)
    1.949353 get_answer: (29 bytes) => ab 10 18 81 16 01 31 33 
34 35 36 3b 3c 3f 40 42
    1.949595  43 89 8a 8b 91 93 95 98 a0 b1 b2 cf 56
    1.949618 get_answer: block_number = 10
    1.949632 get_answer: sequence number (1) is ok
    1.949789 get_answer: checksum is ok
    1.949804 get_answer: all data received
    1.949819 Command list block supported.
    1.951681 entering get_answer(34)
    2.283710 get_answer: (61 bytes) => ab 04 38 81 1c 01 00 00 
38 01 00 00 00 00 48 42
    2.283778  00 00 48 42 00 50 dc 41 64 00 00 00 06 04 00 00 fb 
00 00 00 00 00 00 00 23
    2.283874  00 00 00 00 80 95 3f ad 47 91 40 e8 03 00 00 fb 00 
00 00 36
    2.283888 get_answer: block_number = 4
    2.283902 get_answer: sequence number (1) is ok
    2.283916 get_answer: checksum is ok
    2.284514 get_answer: all data received
    2.285653 entering get_answer(35)
    2.443724 get_answer: (22 bytes) => ab 05 11 81 00 00 00 00 
00 00 00 00 00 00 00 00
    2.444391  00 00 00 00 00 be
    2.444640 get_answer: block_number = 5
    2.444655 get_answer: sequence number (1) is ok
    2.444669 get_answer: checksum is ok
    2.444683 get_answer: all data received
    2.447647 entering get_answer(33)
    2.635717 get_answer: (25 bytes) => ab 03 13 81 50 c2 00 00 
05 00 00 00 00 00 00 00
    2.635774  00 00 00 00 00 00 00 a7 00
    2.636578 get_answer: block_number = 3
    2.636596 get_answer: sequence number (1) is ok
    2.636610 get_answer: checksum is ok
    2.636720 get_answer: all data received
    2.639451 dstate_init: sock 
/var/state/ups/bcmxcp_usb-powerware5115 open on fd 4
    2.645158 entering get_answer(34)
    2.971759 get_answer: (61 bytes) => ab 04 38 81 1c 01 00 00 
38 01 00 00 00 00 48 42
    2.971826  00 00 48 42 00 50 dc 41 64 00 00 00 06 04 00 00 fb 
00 00 00 00 00 00 00 23
    2.972644  00 00 00 00 80 ac 3f ad 47 91 40 e8 03 00 00 fb 00 
00 00 1f
    2.972663 get_answer: block_number = 4
    2.972943 get_answer: sequence number (1) is ok
    2.972973 get_answer: checksum is ok
    2.972987 get_answer: all data received
    2.974736 entering get_answer(35)
    3.131691 get_answer: (22 bytes) => ab 05 11 81 00 00 00 00 
00 00 00 00 00 00 00 00
    3.132186  00 00 00 00 00 be
    3.132211 get_answer: block_number = 5
    3.132227 get_answer: sequence number (1) is ok
    3.132241 get_answer: checksum is ok
    3.132255 get_answer: all data received
    3.134670 entering get_answer(33)
    3.324051 get_answer: (25 bytes) => ab 03 13 81 50 c2 00 00 
05 00 00 00 00 00 00 00
    3.324112  00 00 00 00 00 00 00 a7 00
    3.329390 get_answer: block_number = 3
    3.329413 get_answer: sequence number (1) is ok
    3.329428 get_answer: checksum is ok
    3.329442 get_answer: all data received
    4.650156 entering get_answer(34)
    5.006240 get_answer: (61 bytes) => ab 04 38 81 24 01 00 00 
51 01 00 00 00 00 48 42
    5.006315  00 00 48 42 00 50 dc 41 64 00 00 00 06 04 00 00 fb 
00 00 00 00 00 00 00 23
    5.006798  00 00 00 00 80 a3 3f ad 47 91 40 e8 03 00 00 fb 00 
00 00 07
    5.006820 get_answer: block_number = 4
    5.006834 get_answer: sequence number (1) is ok
    5.006848 get_answer: checksum is ok
    5.006862 get_answer: all data received
    5.010101 entering get_answer(35)
    5.180594 get_answer: (22 bytes) => ab 05 11 81 00 00 00 00 
00 00 00 00 00 00 00 00
    5.180994  00 00 00 00 00 be
    5.181010 get_answer: block_number = 5
    5.181024 get_answer: sequence number (1) is ok
    5.181038 get_answer: checksum is ok
    5.181052 get_answer: all data received
    5.183646 entering get_answer(33)
    5.387731 get_answer: (25 bytes) => ab 03 13 81 50 c2 00 00 
05 00 00 00 00 00 00 00
    5.388134  00 00 00 00 00 00 00 a7 00
    5.388149 get_answer: block_number = 3
    5.388163 get_answer: sequence number (1) is ok
    5.389918 get_answer: checksum is ok
    5.390583 get_answer: all data received
^C   5.785337   Signal 2: exiting
    5.794726 CLOSING
-- 
    Ꮚ Charlie Garrison ♊ <garrison at zeta.org.au>
    〠 PO Box 141, Windsor, NSW 2756, Australia

O< ascii ribbon campaign - stop html mail - www.asciiribbon.org
http://www.ietf.org/rfc/rfc1855.txt



More information about the Nut-upsuser mailing list