[Nut-upsuser] communications lost/established

Arjen de Korte nut+users at de-korte.org
Mon Mar 15 08:08:33 UTC 2010


Citeren ricman <ricman op neomedia.it>:

> same issue (both terminal and log)
>
> Mar 14 22:48:13 maialinux blazer_usb[2638]: Communications with UPS  
> lost: status
> read failed!
> Mar 14 22:48:16 maialinux blazer_usb[2638]: Communications with UPS
> re-established
> Mar 14 22:48:17 maialinux blazer_usb[2638]: Communications with UPS  
> lost: status
> read failed!
> Mar 14 22:48:23 maialinux blazer_usb[2638]: last message repeated 2 times
> Mar 14 22:48:23 maialinux upsd[2640]: Data for UPS [myups] is stale - check
> driver
> Mar 14 22:48:25 maialinux upsmon[2647]: Poll UPS [myups op localhost]  
> failed - Data
> stale
> Mar 14 22:48:25 maialinux upsmon[2647]: Communications with UPS  
> myups op localhost
> lost
> Mar 14 22:48:26 maialinux blazer_usb[2638]: Communications with UPS
> re-established
> Mar 14 22:48:26 maialinux upsd[2640]: UPS [myups] data is no longer stale
> Mar 14 22:48:27 maialinux blazer_usb[2638]: Communications with UPS  
> lost: status
> read failed!

If the USB ID of this device is 06da:0003, upgrading to nut-2.4.2 is  
definitely worth a try (and if it is different, it still might be). We  
have reworked a lot of USB stuff in this release, so the problem may  
have been resolved in the mean time.

Best regards, Arjen
-- 
Please keep list traffic on the list




More information about the Nut-upsuser mailing list