Good morning,
I just had the chance this morning to get my linux box tied into our
network and talking to the UPS. I can now confirm that in NUT v2.4.3
snmp-ups (ietf) works with the Liebert Intellislot Web Card for the
GXT2 family of UPS'.
upsc output:
tux ~ # upsc workups at localhost
battery.charge: 100.00
battery.runtime: 2760.00
battery.runtime.low: 5
battery.voltage: 54.60
device.mfr: Liebert Corporation
device.model: GXT2-1500RT120
device.serial: The DAWSON Group
device.type: ups
driver.name: snmp-ups
driver.parameter.mibs: auto
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: 192.168.1.10
driver.version: 2.4.3
driver.version.internal: 0.47 (mib: ietf 1.3)
input.frequency: 60.00
input.phases: 1.00
input.quality: 0.00
input.voltage: 117.00
output.current: 6.60
output.frequency: 60.00
output.phases: 1.00
output.voltage: 120.00
ups.firmware: GXT2-00797V01
ups.firmware.aux: 5.000.0
ups.mfr: Liebert Corporation
ups.model: GXT2-1500RT120
ups.serial: The DAWSON Group
ups.status: OL
All parameters are correct and match exactly against what is shown by
the intellislot's web status page.
--
Drew
"Nothing in life is to be feared. It is only to be understood."
--Marie Curie