[Nut-upsuser] Getting "Error: No such host" and [ERR ACCESS-DENIED]
Roger Price
roger at rogerprice.org
Thu Sep 30 20:28:20 UTC 2010
Charles Lepple wrote:
> ... It looks like the same "ERR ACCESS-DENIED" code is returned
> for a problem with upsd.users/upsmon.conf versus a TCP wrappers
> match failure.
> What if you run 'tcpdchk' against your hosts.allow file? I am not
> terribly familiar with TCP wrappers, and your configuration looked
> reasonable, but it's possible that there is a problem with the
> syntax.
Opensuse no longer runs inetd nor has the /etc/inetd.conf file
needed by tcpdchk. I havn't yet found an alternative way of
checking the TCP wrappers configuration.
On Thu, 30 Sep 2010, Arjen de Korte wrote:
> It could have to to with the fact that you're probably connecting
> to the server through the '::1' interface. This doesn't seem to
> work if '::1' is not explicitly listed in '/etc/hosts.allow'.
I added [::1] to the upsd line in /etc/hosts.allow
upsd : 10.0.0/24, localhost, LOCAL, 127.0.0.1, [::1] : ALLOW
and then ran command "rcupsd restart" to restart NUT. Problem
solved! /var/log/messages now includes the line
upsd[26097]: User upsmaster@::1 logged into UPS [Eaton-66781]
The man page for upsmon.conf currently says for the MONITOR
directive:
> MONITOR system powervalue username password type
> Each UPS that you need to be monitor should have a MONITOR line.
> Not all of these need supply power to the system that is running
> upsmon. You may monitor other systems if you want to be able to
> send notifications about status changes on them.
> You must have at least one MONITOR directive in this file.
> system is a UPS identifier. It is in this form:
> <upsname>[@<hostname>[:<port>]] The default hostname is
> "localhost".
Perhaps it would be worthwhile adding the following note to this
description
> Note. The hostname "localhost" you specify here cannot be relied
> on as the only possible hostname in access control file
> hosts.allow. You may also need to specify other possible
> identities for local system, for example "upsd : localhost, LOCAL,
> 127.0.0.1, [::1] : ALLOW". See also hosts_access(5) and
> hosts_options(5).
The SEE ALSO for upsmon.conf refers to upsmon(8), upsd(8),
nutupsdrv(8). I suggest adding hosts_access(5), hosts_options(5) and
maybe tcpd(8).
By the way, of the last 572 accesses to my "NUT" web page, 81
visitors have used the three search terms ERR, ACCESS and DENIED,
roughly 14%.
Roger
More information about the Nut-upsuser