[Nut-upsuser] Liebert PSIXR 3000 intellislot web card support with NUT 2.6.0
Arnaud Quette
aquette.dev at gmail.com
Thu Aug 4 08:58:25 UTC 2011
2011/8/3 John Huong <jahuong at gmail.com>
> Hi,
>
> Looks like I had forgotten about this one.
>
> Here's the long overdue snmpwalk output.
>
>
sadly for you, I'll need another one, on the actual UPS data entry point.
can you please do another walk on ".1.3.6.1.4.1.935"?
as advised, having a double walk (1 string version using "-OS" and 1 numeric
version using "-ON" will help investigations)
cheers,
Arnaud
.1.3.6.1.2.1.1.1.0 = STRING: NET Agent II
> .1.3.6.1.2.1.1.2.0 = OID: .1.3.6.1.4.1.935
> .1.3.6.1.2.1.1.3.0 = Timeticks: (729233200) 84 days, 9:38:52.00
> .1.3.6.1.2.1.1.4.0 = STRING: Administrator
> .1.3.6.1.2.1.1.5.0 = STRING: UPS Agent
> .1.3.6.1.2.1.1.6.0 = STRING: My Office
> .1.3.6.1.2.1.1.7.0 = INTEGER: 79
> .1.3.6.1.2.1.2.1.0 = INTEGER: 3
> .1.3.6.1.2.1.2.2.1.1.1 = INTEGER: 1
> .1.3.6.1.2.1.2.2.1.1.2 = INTEGER: 2
> .1.3.6.1.2.1.2.2.1.1.6 = INTEGER: 6
> .1.3.6.1.2.1.2.2.1.2.1 = STRING: :? 鍩馤鍩馤
> .1.3.6.1.2.1.2.2.1.2.2 = STRING: :? 鍩馤鍩馤
> .1.3.6.1.2.1.2.2.1.2.6 = STRING: loopback
> .1.3.6.1.2.1.2.2.1.3.1 = INTEGER: 0
> .1.3.6.1.2.1.2.2.1.3.2 = INTEGER: ppp(23)
> .1.3.6.1.2.1.2.2.1.3.6 = INTEGER: softwareLoopback(24)
> .1.3.6.1.2.1.2.2.1.4.1 = INTEGER: 1500
> .1.3.6.1.2.1.2.2.1.4.2 = INTEGER: 0
> .1.3.6.1.2.1.2.2.1.4.6 = INTEGER: 1536
> .1.3.6.1.2.1.2.2.1.5.1 = Gauge32: 0
> .1.3.6.1.2.1.2.2.1.5.2 = Gauge32: 0
> .1.3.6.1.2.1.2.2.1.5.6 = Gauge32: 10000
> .1.3.6.1.2.1.2.2.1.6.1 = STRING: 0:0:0:0:0:0
> .1.3.6.1.2.1.2.2.1.6.2 = STRING: 0:0:0:0:0:0
> .1.3.6.1.2.1.2.2.1.6.6 = STRING: 0:0:0:0:0:0
> .1.3.6.1.2.1.2.2.1.7.1 = INTEGER: up(1)
> .1.3.6.1.2.1.2.2.1.7.2 = INTEGER: 0
> .1.3.6.1.2.1.2.2.1.7.6 = INTEGER: up(1)
> .1.3.6.1.2.1.2.2.1.8.1 = INTEGER: 0
> .1.3.6.1.2.1.2.2.1.8.2 = INTEGER: 0
> .1.3.6.1.2.1.2.2.1.8.6 = INTEGER: up(1)
> .1.3.6.1.2.1.2.2.1.9.1 = Timeticks: (0) 0:00:00.00
> .1.3.6.1.2.1.2.2.1.9.2 = Timeticks: (0) 0:00:00.00
> .1.3.6.1.2.1.2.2.1.9.6 = Timeticks: (0) 0:00:00.00
> .1.3.6.1.2.1.2.2.1.10.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.10.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.10.6 = Counter32: 679913524
> .1.3.6.1.2.1.2.2.1.11.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.11.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.11.6 = Counter32: 3812303
> .1.3.6.1.2.1.2.2.1.12.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.12.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.12.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.13.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.13.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.13.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.14.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.14.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.14.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.15.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.15.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.15.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.16.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.16.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.16.6 = Counter32: 679913524
> .1.3.6.1.2.1.2.2.1.17.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.17.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.17.6 = Counter32: 3812303
> .1.3.6.1.2.1.2.2.1.18.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.18.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.18.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.19.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.19.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.19.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.20.1 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.20.2 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.20.6 = Counter32: 0
> .1.3.6.1.2.1.2.2.1.21.1 = Gauge32: 0
> .1.3.6.1.2.1.2.2.1.21.2 = Gauge32: 0
> .1.3.6.1.2.1.2.2.1.21.6 = Gauge32: 0
> .1.3.6.1.2.1.2.2.1.22.1 = OID: .0.0
> .1.3.6.1.2.1.2.2.1.22.2 = OID: .0.0
> .1.3.6.1.2.1.2.2.1.22.6 = OID: .0.0
> .1.3.6.1.2.1.3.1.1.1.1.1.192.168.0.2 = INTEGER: 1
> .1.3.6.1.2.1.3.1.1.1.1.1.192.168.0.5 = INTEGER: 1
> .1.3.6.1.2.1.3.1.1.1.1.1.192.168.0.6 = INTEGER: 1
> .1.3.6.1.2.1.3.1.1.1.1.1.192.168.0.8 = INTEGER: 1
> .1.3.6.1.2.1.3.1.1.2.1.1.192.168.0.2 = Hex-STRING: 00 17 A4 F7 BF 00
> .1.3.6.1.2.1.3.1.1.2.1.1.192.168.0.5 = Hex-STRING: 00 90 FB 26 85 D0
> .1.3.6.1.2.1.3.1.1.2.1.1.192.168.0.6 = Hex-STRING: 00 21 5A 5D 6C EA
> .1.3.6.1.2.1.3.1.1.2.1.1.192.168.0.8 = Hex-STRING: 00 1E C9 BB E3 06
> .1.3.6.1.2.1.3.1.1.3.1.1.192.168.0.2 = Network Address: C0:A8:00:02
> .1.3.6.1.2.1.3.1.1.3.1.1.192.168.0.5 = Network Address: C0:A8:00:05
> .1.3.6.1.2.1.3.1.1.3.1.1.192.168.0.6 = Network Address: C0:A8:00:06
> .1.3.6.1.2.1.3.1.1.3.1.1.192.168.0.8 = Network Address: C0:A8:00:08
> .1.3.6.1.2.1.4.1.0 = INTEGER: forwarding(1)
> .1.3.6.1.2.1.4.2.0 = INTEGER: 64
> .1.3.6.1.2.1.4.3.0 = Counter32: 54303337
> .1.3.6.1.2.1.4.4.0 = Counter32: 0
> .1.3.6.1.2.1.4.5.0 = Counter32: 0
> .1.3.6.1.2.1.4.6.0 = Counter32: 0
> .1.3.6.1.2.1.4.7.0 = Counter32: 4572
> .1.3.6.1.2.1.4.8.0 = Counter32: 0
> .1.3.6.1.2.1.4.9.0 = Counter32: 54303343
> .1.3.6.1.2.1.4.10.0 = Counter32: 54416501
> .1.3.6.1.2.1.4.11.0 = Counter32: 0
> .1.3.6.1.2.1.4.12.0 = Counter32: 0
> .1.3.6.1.2.1.4.13.0 = INTEGER: 30 seconds
> .1.3.6.1.2.1.4.14.0 = Counter32: 0
> .1.3.6.1.2.1.4.15.0 = Counter32: 0
> .1.3.6.1.2.1.4.16.0 = Counter32: 0
> .1.3.6.1.2.1.4.17.0 = Counter32: 0
> .1.3.6.1.2.1.4.18.0 = Counter32: 0
> .1.3.6.1.2.1.4.19.0 = Counter32: 0
> .1.3.6.1.2.1.4.20.1.1.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.4.20.1.1.127.0.0.1 = IpAddress: 127.0.0.1
> .1.3.6.1.2.1.4.20.1.1.192.168.0.11 = IpAddress: 192.168.0.11
> .1.3.6.1.2.1.4.20.1.2.0.0.0.0 = INTEGER: 2
> .1.3.6.1.2.1.4.20.1.2.127.0.0.1 = INTEGER: 6
> .1.3.6.1.2.1.4.20.1.2.192.168.0.11 = INTEGER: 1
> .1.3.6.1.2.1.4.20.1.3.0.0.0.0 = IpAddress: 255.0.0.0
> .1.3.6.1.2.1.4.20.1.3.127.0.0.1 = IpAddress: 255.0.0.0
> .1.3.6.1.2.1.4.20.1.3.192.168.0.11 = IpAddress: 255.255.255.0
> .1.3.6.1.2.1.4.20.1.4.0.0.0.0 = INTEGER: 0
> .1.3.6.1.2.1.4.20.1.4.127.0.0.1 = INTEGER: 0
> .1.3.6.1.2.1.4.20.1.4.192.168.0.11 = INTEGER: 1
> .1.3.6.1.2.1.4.20.1.5.0.0.0.0 = INTEGER: 65535
> .1.3.6.1.2.1.4.20.1.5.127.0.0.1 = INTEGER: 65535
> .1.3.6.1.2.1.4.20.1.5.192.168.0.11 = INTEGER: 65535
> .1.3.6.1.2.1.4.21.1.1.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.4.21.1.1.127.0.0.1 = IpAddress: 127.0.0.1
> .1.3.6.1.2.1.4.21.1.1.192.168.0.0 = IpAddress: 192.168.0.0
> .1.3.6.1.2.1.4.21.1.2.0.0.0.0 = INTEGER: 1
> .1.3.6.1.2.1.4.21.1.2.127.0.0.1 = INTEGER: 6
> .1.3.6.1.2.1.4.21.1.2.192.168.0.0 = INTEGER: 1
> .1.3.6.1.2.1.4.21.1.3.0.0.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.3.127.0.0.1 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.3.192.168.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.4.0.0.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.4.127.0.0.1 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.4.192.168.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.5.0.0.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.5.127.0.0.1 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.5.192.168.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.6.0.0.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.6.127.0.0.1 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.6.192.168.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.7.0.0.0.0 = IpAddress: 192.168.0.5
> .1.3.6.1.2.1.4.21.1.7.127.0.0.1 = IpAddress: 127.0.0.1
> .1.3.6.1.2.1.4.21.1.7.192.168.0.0 = IpAddress: 192.168.0.11
> .1.3.6.1.2.1.4.21.1.8.0.0.0.0 = INTEGER: indirect(4)
> .1.3.6.1.2.1.4.21.1.8.127.0.0.1 = INTEGER: direct(3)
> .1.3.6.1.2.1.4.21.1.8.192.168.0.0 = INTEGER: direct(3)
> .1.3.6.1.2.1.4.21.1.9.0.0.0.0 = INTEGER: local(2)
> .1.3.6.1.2.1.4.21.1.9.127.0.0.1 = INTEGER: local(2)
> .1.3.6.1.2.1.4.21.1.9.192.168.0.0 = INTEGER: local(2)
> .1.3.6.1.2.1.4.21.1.10.0.0.0.0 = INTEGER: 0
> .1.3.6.1.2.1.4.21.1.10.127.0.0.1 = INTEGER: 0
> .1.3.6.1.2.1.4.21.1.10.192.168.0.0 = INTEGER: 0
> .1.3.6.1.2.1.4.21.1.11.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.4.21.1.11.127.0.0.1 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.4.21.1.11.192.168.0.0 = IpAddress: 255.255.255.0
> .1.3.6.1.2.1.4.21.1.12.0.0.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.12.127.0.0.1 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.12.192.168.0.0 = INTEGER: -1
> .1.3.6.1.2.1.4.21.1.13.0.0.0.0 = OID: .0.0
> .1.3.6.1.2.1.4.21.1.13.127.0.0.1 = OID: .0.0
> .1.3.6.1.2.1.4.21.1.13.192.168.0.0 = OID: .0.0
> .1.3.6.1.2.1.4.22.1.1.1.192.168.0.2 = INTEGER: 1
> .1.3.6.1.2.1.4.22.1.1.1.192.168.0.5 = INTEGER: 1
> .1.3.6.1.2.1.4.22.1.1.1.192.168.0.6 = INTEGER: 1
> .1.3.6.1.2.1.4.22.1.1.1.192.168.0.8 = INTEGER: 1
> .1.3.6.1.2.1.4.22.1.2.1.192.168.0.2 = STRING: 0:17:a4:f7:bf:0
> .1.3.6.1.2.1.4.22.1.2.1.192.168.0.5 = STRING: 0:90:fb:26:85:d0
> .1.3.6.1.2.1.4.22.1.2.1.192.168.0.6 = STRING: 0:21:5a:5d:6c:ea
> .1.3.6.1.2.1.4.22.1.2.1.192.168.0.8 = STRING: 0:1e:c9:bb:e3:6
> .1.3.6.1.2.1.4.22.1.3.1.192.168.0.2 = IpAddress: 192.168.0.2
> .1.3.6.1.2.1.4.22.1.3.1.192.168.0.5 = IpAddress: 192.168.0.5
> .1.3.6.1.2.1.4.22.1.3.1.192.168.0.6 = IpAddress: 192.168.0.6
> .1.3.6.1.2.1.4.22.1.3.1.192.168.0.8 = IpAddress: 192.168.0.8
> .1.3.6.1.2.1.4.22.1.4.1.192.168.0.2 = INTEGER: dynamic(3)
> .1.3.6.1.2.1.4.22.1.4.1.192.168.0.5 = INTEGER: dynamic(3)
> .1.3.6.1.2.1.4.22.1.4.1.192.168.0.6 = INTEGER: dynamic(3)
> .1.3.6.1.2.1.4.22.1.4.1.192.168.0.8 = INTEGER: dynamic(3)
> .1.3.6.1.2.1.4.23.0 = Counter32: 0
> .1.3.6.1.2.1.5.1.0 = Counter32: 585328
> .1.3.6.1.2.1.5.2.0 = Counter32: 0
> .1.3.6.1.2.1.5.3.0 = Counter32: 4769
> .1.3.6.1.2.1.5.4.0 = Counter32: 0
> .1.3.6.1.2.1.5.5.0 = Counter32: 0
> .1.3.6.1.2.1.5.6.0 = Counter32: 0
> .1.3.6.1.2.1.5.7.0 = Counter32: 0
> .1.3.6.1.2.1.5.8.0 = Counter32: 290531
> .1.3.6.1.2.1.5.9.0 = Counter32: 290028
> .1.3.6.1.2.1.5.10.0 = Counter32: 0
> .1.3.6.1.2.1.5.11.0 = Counter32: 0
> .1.3.6.1.2.1.5.12.0 = Counter32: 0
> .1.3.6.1.2.1.5.13.0 = Counter32: 0
> .1.3.6.1.2.1.5.14.0 = Counter32: 585086
> .1.3.6.1.2.1.5.15.0 = Counter32: 0
> .1.3.6.1.2.1.5.16.0 = Counter32: 4527
> .1.3.6.1.2.1.5.17.0 = Counter32: 0
> .1.3.6.1.2.1.5.18.0 = Counter32: 0
> .1.3.6.1.2.1.5.19.0 = Counter32: 0
> .1.3.6.1.2.1.5.20.0 = Counter32: 0
> .1.3.6.1.2.1.5.21.0 = Counter32: 290028
> .1.3.6.1.2.1.5.22.0 = Counter32: 290531
> .1.3.6.1.2.1.5.23.0 = Counter32: 0
> .1.3.6.1.2.1.5.24.0 = Counter32: 0
> .1.3.6.1.2.1.5.25.0 = Counter32: 0
> .1.3.6.1.2.1.5.26.0 = Counter32: 0
> .1.3.6.1.2.1.6.1.0 = INTEGER: vanj(4)
> .1.3.6.1.2.1.6.2.0 = INTEGER: 1000 milliseconds
> .1.3.6.1.2.1.6.3.0 = INTEGER: 64000 milliseconds
> .1.3.6.1.2.1.6.4.0 = INTEGER: -1
> .1.3.6.1.2.1.6.5.0 = Counter32: 290043
> .1.3.6.1.2.1.6.6.0 = Counter32: 290054
> .1.3.6.1.2.1.6.7.0 = Counter32: 3
> .1.3.6.1.2.1.6.8.0 = Counter32: 14
> .1.3.6.1.2.1.6.9.0 = Gauge32: 0
> .1.3.6.1.2.1.6.10.0 = Counter32: 2646368
> .1.3.6.1.2.1.6.11.0 = Counter32: 2646323
> .1.3.6.1.2.1.6.12.0 = Counter32: 0
> .1.3.6.1.2.1.6.13.1.1.0.0.0.0.21.0.0.0.0.0 = INTEGER: listen(2)
> .1.3.6.1.2.1.6.13.1.1.0.0.0.0.23.0.0.0.0.0 = INTEGER: listen(2)
> .1.3.6.1.2.1.6.13.1.1.0.0.0.0.80.0.0.0.0.0 = INTEGER: listen(2)
> .1.3.6.1.2.1.6.13.1.2.0.0.0.0.21.0.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.6.13.1.2.0.0.0.0.23.0.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.6.13.1.2.0.0.0.0.80.0.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.6.13.1.3.0.0.0.0.21.0.0.0.0.0 = INTEGER: 21
> .1.3.6.1.2.1.6.13.1.3.0.0.0.0.23.0.0.0.0.0 = INTEGER: 23
> .1.3.6.1.2.1.6.13.1.3.0.0.0.0.80.0.0.0.0.0 = INTEGER: 80
> .1.3.6.1.2.1.6.13.1.4.0.0.0.0.21.0.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.6.13.1.4.0.0.0.0.23.0.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.6.13.1.4.0.0.0.0.80.0.0.0.0.0 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.6.13.1.5.0.0.0.0.21.0.0.0.0.0 = INTEGER: 0
> .1.3.6.1.2.1.6.13.1.5.0.0.0.0.23.0.0.0.0.0 = INTEGER: 0
> .1.3.6.1.2.1.6.13.1.5.0.0.0.0.80.0.0.0.0.0 = INTEGER: 0
> .1.3.6.1.2.1.6.14.0 = Counter32: 0
> .1.3.6.1.2.1.6.15.0 = Counter32: 1
> .1.3.6.1.2.1.7.1.0 = Counter32: 51067263
> .1.3.6.1.2.1.7.2.0 = Counter32: 4527
> .1.3.6.1.2.1.7.3.0 = Counter32: 0
> .1.3.6.1.2.1.7.4.0 = Counter32: 51185237
> .1.3.6.1.2.1.7.5.1.1.0.0.0.0.161 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.7.5.1.1.0.0.0.0.199 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.7.5.1.1.0.0.0.0.5500 = IpAddress: 0.0.0.0
> .1.3.6.1.2.1.7.5.1.2.0.0.0.0.161 = INTEGER: 161
> .1.3.6.1.2.1.7.5.1.2.0.0.0.0.199 = INTEGER: 199
> .1.3.6.1.2.1.7.5.1.2.0.0.0.0.5500 = INTEGER: 5500
> .1.3.6.1.2.1.11.1.0 = Counter32: 50603351
> .1.3.6.1.2.1.11.2.0 = Counter32: 50603347
> .1.3.6.1.2.1.11.3.0 = Counter32: 0
> .1.3.6.1.2.1.11.4.0 = Counter32: 0
> .1.3.6.1.2.1.11.5.0 = Counter32: 0
> .1.3.6.1.2.1.11.6.0 = Counter32: 4
> .1.3.6.1.2.1.11.8.0 = Counter32: 0
> .1.3.6.1.2.1.11.9.0 = Counter32: 0
> .1.3.6.1.2.1.11.10.0 = Counter32: 0
> .1.3.6.1.2.1.11.11.0 = Counter32: 0
> .1.3.6.1.2.1.11.12.0 = Counter32: 0
> .1.3.6.1.2.1.11.13.0 = Counter32: 50313294
> .1.3.6.1.2.1.11.14.0 = Counter32: 0
> .1.3.6.1.2.1.11.15.0 = Counter32: 50311778
> .1.3.6.1.2.1.11.16.0 = Counter32: 291583
> .1.3.6.1.2.1.11.17.0 = Counter32: 0
> .1.3.6.1.2.1.11.18.0 = Counter32: 0
> .1.3.6.1.2.1.11.19.0 = Counter32: 0
> .1.3.6.1.2.1.11.20.0 = Counter32: 0
> .1.3.6.1.2.1.11.21.0 = Counter32: 290063
> .1.3.6.1.2.1.11.22.0 = Counter32: 0
> .1.3.6.1.2.1.11.24.0 = Counter32: 0
> .1.3.6.1.2.1.11.25.0 = Counter32: 0
> .1.3.6.1.2.1.11.26.0 = Counter32: 0
> .1.3.6.1.2.1.11.27.0 = Counter32: 0
> .1.3.6.1.2.1.11.28.0 = Counter32: 50603371
> .1.3.6.1.2.1.11.29.0 = Counter32: 0
> .1.3.6.1.2.1.11.30.0 = INTEGER: enabled(1)
> .1.3.6.1.2.1.33.1.1.1.0 = STRING: "Emerson Network Power"
> .1.3.6.1.2.1.33.1.1.2.0 = STRING: "LiebertPSI"
> .1.3.6.1.2.1.33.1.1.3.0 = STRING: "EX000842 "
> .1.3.6.1.2.1.33.1.1.4.0 = STRING: "2.39.CP504.ABE.00"
> .1.3.6.1.2.1.33.1.1.5.0 = ""
> .1.3.6.1.2.1.33.1.2.1.0 = INTEGER: 2
> .1.3.6.1.2.1.33.1.2.2.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.2.3.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.2.4.0 = INTEGER: 100
> .1.3.6.1.2.1.33.1.2.5.0 = INTEGER: 550
> .1.3.6.1.2.1.33.1.2.6.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.2.7.0 = INTEGER: 30
> .1.3.6.1.2.1.33.1.3.1.0 = Counter32: 0
> .1.3.6.1.2.1.33.1.3.2.0 = INTEGER: 1
> .1.3.6.1.2.1.33.1.3.3.1.2.1 = INTEGER: 500
> .1.3.6.1.2.1.33.1.3.3.1.3.1 = INTEGER: 244
> .1.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.3.3.1.5.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.4.1.0 = INTEGER: 3
> .1.3.6.1.2.1.33.1.4.2.0 = INTEGER: 500
> .1.3.6.1.2.1.33.1.4.3.0 = INTEGER: 1
> .1.3.6.1.2.1.33.1.4.4.1.2.1 = INTEGER: 245
> .1.3.6.1.2.1.33.1.4.4.1.3.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.4.4.1.4.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.4.4.1.5.1 = INTEGER: 17
> .1.3.6.1.2.1.33.1.5.1.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.5.2.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.5.3.1.2.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.5.3.1.3.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.5.3.1.4.1 = INTEGER: 0
> .1.3.6.1.2.1.33.1.6.1.0 = Gauge32: 0
> .1.3.6.1.2.1.33.1.7.1.0 = OID: .1.3.6.1.2.1.33.1.7.7.1
> .1.3.6.1.2.1.33.1.7.2.0 = INTEGER: 1
> .1.3.6.1.2.1.33.1.7.3.0 = INTEGER: 1
> .1.3.6.1.2.1.33.1.7.4.0 = ""
> .1.3.6.1.2.1.33.1.7.5.0 = Timeticks: (0) 0:00:00.00
> .1.3.6.1.2.1.33.1.7.6.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.8.1.0 = INTEGER: 1
> .1.3.6.1.2.1.33.1.8.2.0 = INTEGER: -1
> .1.3.6.1.2.1.33.1.8.3.0 = INTEGER: -1
> .1.3.6.1.2.1.33.1.8.4.0 = INTEGER: -1
> .1.3.6.1.2.1.33.1.8.5.0 = INTEGER: 2
> .1.3.6.1.2.1.33.1.9.1.0 = INTEGER: 2300
> .1.3.6.1.2.1.33.1.9.2.0 = INTEGER: 500
> .1.3.6.1.2.1.33.1.9.3.0 = INTEGER: 2300
> .1.3.6.1.2.1.33.1.9.4.0 = INTEGER: 500
> .1.3.6.1.2.1.33.1.9.5.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.9.6.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.9.7.0 = INTEGER: 2
> .1.3.6.1.2.1.33.1.9.8.0 = INTEGER: 2
> .1.3.6.1.2.1.33.1.9.9.0 = INTEGER: 0
> .1.3.6.1.2.1.33.1.9.10.0 = INTEGER: 0
>
>
> On Wed, Mar 23, 2011 at 9:56 PM, Arnaud Quette <aquette.dev at gmail.com>
> wrote:
> > Hi John,
> >
> > 2011/3/23 John Huong <jahuong at gmail.com>
> >>
> >> Hi Arnaud,
> >>
> >> Sure I am willing to take this up. Will need guidance on how to get
> >> started as I am new to doing stuff like SNMP walks.
> >> Just lead the way :) .
> >
> > just start by reading the pointed mails, and more specifically this one
> > where I give some starting directions:
> >
> http://lists.alioth.debian.org/pipermail/nut-upsdev/2011-February/005272.html
> >
> > just remember that the nut lookup table ("snmp_info_t") use the numeric
> > OIDs...
> >
> > cheers,
> > Arnaud
> > --
> > Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
> > Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
> > Debian Developer - http://www.debian.org
> > Free Software Developer - http://arnaud.quette.free.fr/
> >
> >> On Mar 23, 2011 5:29 PM, "Arnaud Quette" <aquette.dev at gmail.com> wrote:
> >> > Hi John,
> >> >
> >> > 2011/3/16 John Huong <jahuong at gmail.com>
> >> >
> >> >> Hi,
> >> >>
> >> >> Just started using NUT with a Liebert PSI-XR 3000 with an Intellislot
> >> >> web
> >> >> card.
> >> >>
> >> >> It seems I can't get it to run properly.
> >> >>
> >> >> I am using NUT 2.6.0 built from source on Ubuntu 8.0.4 .
> >> >>
> >> >> My build parameters are :
> >> >>
> >> >> ./configure --enable-strip
> >> >> --with-linux-hiddev=/usr/include/linux/hiddev.h
> >> >> --with-udev-dir=/lib/udev \
> >> >> --prefix=/usr \
> >> >> --exec-prefix=/ \
> >> >> --sysconfdir=/etc/nut \
> >> >> --mandir=/usr/share/man \
> >> >> --libdir=/lib \
> >> >> --includedir=/usr/include \
> >> >> --without-ssl \
> >> >> --with-dev \
> >> >> --enable-static \
> >> >> --with-statepath=/var/run/nut \
> >> >> --with-altpidpath=/var/run/nut \
> >> >> --with-drvpath=/lib/nut \
> >> >> --with-htmlpath=/usr/share/nut/www \
> >> >> --with-pidpath=/var/run/nut \
> >> >> --datadir=/usr/share/nut \
> >> >> --with-pkgconfig-dir=/usr/lib/pkgconfig \
> >> >> --with-user=nut --with-group=nut
> >> >>
> >> >>
> >> >> I get this when I run upsdrvctl start
> >> >>
> >> >> Detected LiebertPSI on host 192.168.0.11 (mib: ietf 1.3)
> >> >> [liebertpsiweb] unhandled ASN 0x6 recieved from
> 1.3.6.1.2.1.33.1.7.1.0
> >> >>
> >> >> Then when I run /etc/init.d/nut I get
> >> >>
> >> >> * Starting Network UPS Tools [
> >> >> OK ]
> >> >>
> >> >> Broadcast Message from nut at mail.sop.com.my
> >> >> (somewhere) at 1:02 ...
> >> >>
> >> >> Communications with UPS liebertpsiweb at localhost lost
> >> >>
> >> >> Running upsc liebertpsiweb at localhost gets me :
> >> >>
> >> >> battery.charge: 100.00
> >> >> battery.current: 0.00
> >> >> battery.runtime: 0.00
> >> >> battery.runtime.low: 120.00
> >> >> battery.temperature: 30.00
> >> >> battery.voltage: 55.00
> >> >> beeper.status: enabled
> >> >> device.mfr: Emerson Network Power
> >> >> device.model: LiebertPSI
> >> >> device.type: ups
> >> >> driver.name: snmp-ups
> >> >> driver.parameter.mibs: auto
> >> >> driver.parameter.pollinterval: 2
> >> >> driver.parameter.port: 192.168.0.11
> >> >> driver.version: 2.6.0
> >> >> driver.version.internal: 0.50 (mib: ietf 1.3)
> >> >> input.bypass.phases: 0.00
> >> >> input.current: 0.00
> >> >> input.frequency: 50.00
> >> >> input.frequency.nominal: 50.00
> >> >> input.phases: 1.00
> >> >> input.realpower: 0.00
> >> >> input.transfer.high: 0.00
> >> >> input.transfer.low: 0.00
> >> >> input.voltage: 247.00
> >> >> input.voltage.nominal: 2300.00
> >> >> output.current: 0.00
> >> >> output.frequency: 50.00
> >> >> output.frequency.nominal: 50.00
> >> >> output.phases: 1.00
> >> >> output.power.nominal: 0.00
> >> >> output.realpower: 0.00
> >> >> output.realpower.nominal: 0.00
> >> >> output.voltage: 249.00
> >> >> output.voltage.nominal: 2300.00
> >> >> ups.firmware: EX000842
> >> >> ups.firmware.aux: 2.39.CP504.ABE.00
> >> >> ups.load: 17.00
> >> >> ups.mfr: Emerson Network Power
> >> >> ups.model: LiebertPSI
> >> >> ups.start.auto: no
> >> >> ups.status:
> >> >> ups.test.result: done and passed
> >> >> ups.timer.reboot: -1
> >> >> ups.timer.shutdown: -1
> >> >> ups.timer.start: -1
> >> >>
> >> >> What can I do or is this particular model not supported?
> >> >>
> >> >
> >> > the support for this unit, and more generally Liebert SNMP support,
> >> > doesn't
> >> > yet exist.
> >> >
> >> > the best for you is to check the MIB(s) supported, since Liebert may
> >> > provide
> >> > its own, with a basic RFC 1628 (aka IETF MIB) supplement.
> >> >
> >> > if you're willing to work on this, we will help you.
> >> > The idea is to create a lookup table between SNMP data and values to
> the
> >> > NUT
> >> > ones, as done for example here (look for "snmp_info_t"):
> >> > http://svn.debian.org/wsvn/nut/trunk/drivers/eaton-mib.c
> >> >
> >> > So, send us back an SNMP walk of the device, and start checking for
> >> > creating
> >> > this mapping.
> >> > Note that you may want to work with Philip Tait
> >> >
> >> >
> http://lists.alioth.debian.org/pipermail/nut-upsdev/2011-February/005255.html
> >> >
> >> >
> http://lists.alioth.debian.org/pipermail/nut-upsdev/2011-February/005263.html
> >> >
> >> > Have a special look at the 2nd thread!
> >> >
> >> > cheers,
> >> > Arnaud
> >> > --
> >> > Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
> >> > Network UPS Tools (NUT) Project Leader -
> http://www.networkupstools.org/
> >> > Debian Developer - http://www.debian.org
> >> > Free Software Developer - http://arnaud.quette.free.fr/
> >
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20110804/ba9b766e/attachment-0001.html>
More information about the Nut-upsuser
mailing list