[Nut-upsuser] KIN-1500AP RM + Windows 2008 64-bit Standard R2 SP1 (nut 2.6.1)
Frédéric Bohé
fredericbohe at eaton.com
Fri Aug 5 11:23:37 UTC 2011
For the record, it ends up to be a misconfiguration:
The powercom driver need the "type" variable to be correctly set.
In this case it is "type = KIN"
Fred
On Tue, 2011-08-02 at 16:23 +0200, Frédéric Bohé wrote:
> On Tue, 2011-07-26 at 15:30 +0300, Павел Гуменюк wrote:
> > After adding COM1 I've got this:
> >
> > c:\Program Files (x86)\NUT\bin>powercom.exe -DDD -a KIN1500
> > Network UPS Tools - PowerCom protocol UPS driver 0.13
> > (2.6.1-3057:3116M)
> > 0.000000 debug level is '3'
> > 0.000000 w32_serial_open (notUsed)
> > 0.000000 could not open notUsed
> >
> > Unable to open notUsed: Operation not permitted
> >
> > Things to try:
> >
> > - Check 'port=' in ups.conf
> >
> > - Check owner/permissions of all parts of path
> >
> > 0.015600 Fatal error: unusable configuration
> >
> > c:\Program Files (x86)\NUT\bin>powercom.exe -DDD -a KIN1500
> > Network UPS Tools - PowerCom protocol UPS driver 0.13
> > (2.6.1-3057:3116M)
> > 0.000000 debug level is '3'
> > 0.000000 w32_serial_open (COM1)
> > 0.015600 setting initial state on COM1
> > 0.015600 00000054 = w32_serial_open (COM1)
> > 0.015600 Warning: no locking method is available: No error
> > [+яхЁрЎш єёях
> > °эю чртхЁ°хэр. ]
> > 0.031200 vmin_ 0, vtime_ 0
> > 0.140400 action 0
> > 0.140400 vtime 0, vmin 1
> >
> > 0.140400 ReadTotalTimeoutConstant -2, ReadIntervalTimeout -1,
> > ReadTotalTi
> > meoutMultiplier -1
> > 0.140400 DTR => 0, RTS => 1
> > 0.140400 Values of arguments:
> > 0.140400 manufacturer : 'PowerCom'
> > 0.140400 model name : 'Unknown'
> > 0.156000 serial number : 'Unknown'
> > 0.156000 line voltage : '230'
> > 0.156000 type : 'Trust'
> > 0.156000 number of bytes from UPS: '11'
> > 0.156000 method of flow control : 'dtr0rts1'
> > 0.156000 validation sequence: '{{5,0},{7,0},{8,0}}'
> > 0.171600 shutdown arguments: '{{0,10},n}'
> > 0.171600 frequency calculation coefficients:
> > '{0.000210,0.000209}'
> > 0.171600 load percentage calculation coefficients:
> > '{6.134300,-0.380800,
> > 4.311000,0.181100}'
> > 0.171600 battery percentage calculation coefficients:
> > '{5.000000,0.32680
> > 0,-825.000000,4.563900,-835.
> > 820007}'
> > 0.187200 voltage calculation coefficients:
> > '{0.954500,0.000000}'
> > 0.343200 data receiving error (validation check)
> > 0.343200 dstate_init: sock \\.\pipe\powercom-KIN1500 open on fd
> > 100
> > 3.432006 data receiving error (0 instead of 11 bytes)
> > 6.442811 data receiving error (0 instead of 11 bytes)
> > 9.453616 data receiving error (0 instead of 11 bytes)
> > 12.464422 data receiving error (0 instead of 11 bytes)
> > 21.668438 data receiving error (0 instead of 11 bytes)
> > 24.679243 data receiving error (0 instead of 11 bytes)
>
> Hello Pavel,
>
> Maybe it's a bug in serial drivers. It's hard to be sure since I don't
> have a Powercom UPS for testing. Anyway, I will privately send you an
> experimental binary. If it doesn't fix your issue, please send its
> output on this list using -DDDDD ( five D) for maximum output.
>
> Fred
>
> >
> > c:\Program Files (x86)\NUT\bin>
> >
> >
> > 2011/7/19 Павел Гуменюк <pavel.gumenyuk at gmail.com>
> > I have only RS-232 on the box (meanwhile, it was manufactured
> > on march of 2011)
> > Here is my configs:
> >
> > nut.conf:
> >
> >
> > MODE = netserver
> >
> >
> > ups.conf:
> >
> >
> > [KIN1500]
> > driver = powercom
> > port = notUsed
> > desc = "Powercom KING PRO KIN-1500AP RM"
> >
> >
> >
> > upsd.conf:
> >
> >
> > LISTEN 192.168.1.2 3493
> >
> >
> >
> > upsd.users:
> >
> >
> > [monuser]
> > password = xxxxxxxx
> > upsmon master
> >
> >
> >
> > upsmon.conf:
> >
> >
> > MONITOR KIN1500 at 192.168.1.2 1 monuser xxxxxxxx master
> > MINSUPPLIES 1
> > SHUTDOWNCMD "C:\\WINDOWS\\system32\\shutdown.exe -s -t 0"
> > NOTIFYCMD /sbin/upssched
> > POLLFREQ 5
> > POLLFREQALERT 5
> > HOSTSYNC 15
> > DEADTIME 15
> > POWERDOWNFLAG "C:\\killpower"
> > NOTIFYFLAG ONLINE SYSLOG+WALL+EXEC
> > NOTIFYFLAG ONBATT SYSLOG+WALL+EXEC
> > NOTIFYFLAG LOWBATT SYSLOG+WALL+EXEC
> > RBWARNTIME 43200
> > NOCOMMWARNTIME 300
> > FINALDELAY 5
> >
> >
> >
> > upssched.conf:
> >
> >
> > CMDSCRIPT /bin/upssched-cmd
> > AT ONBATT * START-TIMER onbattwarn 10
> > AT ONLINE * CANCEL-TIMER onbattwarn
> > AT LOWBATT * EXECUTE lowbattwarn
> > AT ONBATT * START-TIMER timeshutdown 100
> > AT ONLINE * CANCEL-TIMER timeshutdown
> >
> >
> > After start I can see couple neutral events:
> > upsd.exe - listening on 192.168.1.2 port 3493.
> > upsd.exe - User monuser at 192.168.1.2 logged into UPS [KIN1500].
> >
> > Also, there are a lot of errors, such as "upsmon - Poll UPS
> > [KIN1500 at 192.168.1.2] failed - Data stale."
> > Anybody, please advise how to get it works.
> > Thanks
> >
> > _______________________________________________
> > Nut-upsuser mailing list
> > Nut-upsuser at lists.alioth.debian.org
> > http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
>
> --
> Team Open Source Eaton - http://powerquality.eaton.com
>
> --------------------------------------------------------------------------
>