[Nut-upsuser] Liebert PSIXR 3000 intellislot web card support with NUT 2.6.0

John Huong jahuong at gmail.com
Thu Aug 11 11:43:22 UTC 2011


Ok now I've specified the MIB file you've asked me to use for snmpwalk.

This is the output for -OS walk:

XPPC-MIB::upsBaseIdentModel.0 = STRING: "Intelligent LiebertPSI"
XPPC-MIB::upsBaseIdentUpsName.0 = ""
XPPC-MIB::upsSmartIdentFirmwareRevision.0 = STRING: "EX000842  "
XPPC-MIB::upsSmartIdentDateOfManufacture.0 = ""
XPPC-MIB::upsSmartIdentUpsSerialNumber.0 = ""
XPPC-MIB::upsSmartIdentAgentFirmwareRevision.0 = STRING: "2.39.CP504.ABE.00"
XPPC-MIB::upsBaseBatteryStatus.0 = INTEGER: batteryNormal(2)
XPPC-MIB::upsBaseBatteryTimeOnBattery.0 = INTEGER: 0
XPPC-MIB::upsBaseBatteryLastReplaceDate.0 = ""
XPPC-MIB::upsSmartBatteryCapacity.0 = INTEGER: 100
XPPC-MIB::upsSmartBatteryVoltage.0 = INTEGER: 550
XPPC-MIB::upsSmartBatteryTemperature.0 = INTEGER: 300
XPPC-MIB::upsSmartBatteryRunTimeRemaining.0 = INTEGER: 0
XPPC-MIB::upsSmartBatteryFullChargeVoltage.0 = INTEGER: 480
XPPC-MIB::upsSmartBatteryCurrent.0 = INTEGER: 0
XPPC-MIB::upsBaseInputPhase.0 = INTEGER: 1
XPPC-MIB::upsSmartInputLineVoltage.0 = INTEGER: 2405
XPPC-MIB::upsSmartInputMaxLineVoltage.0 = INTEGER: 2571
XPPC-MIB::upsSmartInputMinLineVoltage.0 = INTEGER: 2164
XPPC-MIB::upsSmartInputFrequency.0 = INTEGER: 500
XPPC-MIB::upsSmartInputLineFailCause.0 = INTEGER: noTransfer(1)
XPPC-MIB::upsBaseOutputStatus.0 = INTEGER: standBy(8)
XPPC-MIB::upsBaseOutputPhase.0 = INTEGER: 1
XPPC-MIB::upsSmartOutputVoltage.0 = INTEGER: 2425
XPPC-MIB::upsSmartOutputFrequency.0 = INTEGER: 500
XPPC-MIB::upsSmartOutputLoad.0 = INTEGER: 17
XPPC-MIB::upsBaseConfigNumDevices.0 = INTEGER: 4
XPPC-MIB::indexOfDevice.1 = INTEGER: 1
XPPC-MIB::indexOfDevice.2 = INTEGER: 2
XPPC-MIB::indexOfDevice.3 = INTEGER: 3
XPPC-MIB::indexOfDevice.4 = INTEGER: 4
XPPC-MIB::nameOfDevice.1 = ""
XPPC-MIB::nameOfDevice.2 = ""
XPPC-MIB::nameOfDevice.3 = ""
XPPC-MIB::nameOfDevice.4 = ""
XPPC-MIB::vaRatingOfDevice.1 = INTEGER: 0
XPPC-MIB::vaRatingOfDevice.2 = INTEGER: 0
XPPC-MIB::vaRatingOfDevice.3 = INTEGER: 0
XPPC-MIB::vaRatingOfDevice.4 = INTEGER: 0
XPPC-MIB::deviceAccept.1 = INTEGER: no(2)
XPPC-MIB::deviceAccept.2 = INTEGER: no(2)
XPPC-MIB::deviceAccept.3 = INTEGER: no(2)
XPPC-MIB::deviceAccept.4 = INTEGER: no(2)
XPPC-MIB::upsSmartConfigRatedOutputVoltage.0 = INTEGER: 2300
XPPC-MIB::upsSmartConfigHighTransferVolt.0 = INTEGER: 0
XPPC-MIB::upsSmartConfigLowTransferVolt.0 = INTEGER: 0
XPPC-MIB::upsSmartConfigAlarmTimer.0 = INTEGER: 2147483647
XPPC-MIB::upsSmartConfigLowBatteryRunTime.0 = INTEGER: 120
XPPC-MIB::upsSmartConfigReturnDelay.0 = INTEGER: 60
XPPC-MIB::upsSmartConfigShutoffDelay.0 = INTEGER: 120
XPPC-MIB::upsSmartConfigUpsSleepTime.0 = INTEGER: 2
XPPC-MIB::upsBaseControlConserveBattery.0 = INTEGER: noTurnOffUps(1)
XPPC-MIB::upsSmartControlUpsOff.0 = INTEGER: noTurnUpsOff(1)
XPPC-MIB::upsSmartControlRebootUps.0 = INTEGER: noRebootUps(1)
XPPC-MIB::upsSmartControlUpsSleep.0 = INTEGER: noPutUpsToSleep(1)
XPPC-MIB::upsSmartControlSimulatePowerFail.0 = INTEGER:
noSimulatePowerFailure(1)
XPPC-MIB::upsSmartControlFlashAndBeep.0 = INTEGER: noFlashAndBeep(1)
XPPC-MIB::upsSmartControlTurnOnUpsLoad.0 = INTEGER:
noUpsSmartControlTurnOnUpsLoad(1)
XPPC-MIB::upsSmartTestDiagnosticSchedule.0 = INTEGER: never(4)
XPPC-MIB::upsSmartTestDiagnostics.0 = INTEGER: noTestDiagnostics(1)
XPPC-MIB::upsSmartTestDiagnosticsResults.0 = INTEGER: ok(1)
XPPC-MIB::upsSmartTestLastDiagnosticsDate.0 = ""
XPPC-MIB::upsThreePhaseBatteryVoltage.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBatteryCapacityPercentage.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBatteryTimeRemain.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBatteryCurrent.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBatteryTemperature.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseInputFrequency.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseInputVoltageR.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseInputVoltageS.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseInputVoltageT.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputFrequency.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputVoltageR.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputVoltageS.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputVoltageT.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputLoadPercentageR.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputLoadPercentageS.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseOutputLoadPercentageT.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBypassSourceFrequency.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBypssSourceVoltageR.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBypssSourceVoltageS.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseBypssSourceVoltageT.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseDCandRectifierStatusRecRotError.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseDCandRectifierStatusLowBatteryShutdown.0 =
INTEGER: no(16)
XPPC-MIB::upsThreePhaseDCandRectifierStatusLowBattery.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseDCandRectifierStatusInAndOut.0 = INTEGER:
threeInThreeOut(3)
XPPC-MIB::upsThreePhaseDCandRectifierStatusBatteryStatus.0 = INTEGER:
acnormal(5)
XPPC-MIB::upsThreePhaseDCandRectifierStatusChargeStatus.0 = INTEGER: float(7)
XPPC-MIB::upsThreePhaseDCandRectifierStatusRecOperating.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseUPSStatusBypassFreqFail.0 = INTEGER: 15
XPPC-MIB::upsThreePhaseUPSStatusManualBypassBreaker.0 = INTEGER: open(9)
XPPC-MIB::upsThreePhaseUPSStatusACStatus.0 = INTEGER: abnormal(11)
XPPC-MIB::upsThreePhaseUPSStaticSwitchMode.0 = INTEGER: bypassmode(13)
XPPC-MIB::upsThreePhaseUPSStatusInverterOperating.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusEmergencyStop.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusHighDCShutdown.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusBypassBreaker.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusOverLoad.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusInverterOutputFail.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusOverTemperature.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseFaultStatusShortCircuit.0 = INTEGER: no(16)
XPPC-MIB::upsThreePhaseRatingRectifierVoltage.0 = ""
XPPC-MIB::upsThreePhaseRatingRectifierFrequency.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseRatingBypassVoltage.0 = ""
XPPC-MIB::upsThreePhaseRatingBypassFrequency.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseRatingOutputVoltage.0 = ""
XPPC-MIB::upsThreePhaseRatingOutputFrequency.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseRatingBatteryVoltage.0 = INTEGER: 0
XPPC-MIB::upsThreePhaseRatingPower.0 = ""
XPPC-MIB::upsEnvTemperature.0 = INTEGER: 0
XPPC-MIB::upsEnvHumidity.0 = INTEGER: 0
XPPC-MIB::upsEnvWater.0 = INTEGER: 0
XPPC-MIB::upsEnvSmoke.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity1.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity2.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity3.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity4.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity5.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity6.0 = INTEGER: 0
XPPC-MIB::upsEnvSecurity7.0 = INTEGER: 0
XPPC-MIB::upsEnvOverTemperature.0 = INTEGER: 30
XPPC-MIB::upsEnvUnderTemperature.0 = INTEGER: 10
XPPC-MIB::upsEnvOverHumidity.0 = INTEGER: 50
XPPC-MIB::upsEnvUnderHumidity.0 = INTEGER: 12
XPPC-MIB::mconfigTrapsReceiversNum.0 = INTEGER: 8
XPPC-MIB::trapsIndex.1 = INTEGER: 1
XPPC-MIB::trapsIndex.2 = INTEGER: 2
XPPC-MIB::trapsIndex.3 = INTEGER: 3
XPPC-MIB::trapsIndex.4 = INTEGER: 4
XPPC-MIB::trapsIndex.5 = INTEGER: 5
XPPC-MIB::trapsIndex.6 = INTEGER: 6
XPPC-MIB::trapsIndex.7 = INTEGER: 7
XPPC-MIB::trapsIndex.8 = INTEGER: 8
XPPC-MIB::trapsReceiverAddr.1 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.2 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.3 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.4 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.5 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.6 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.7 = IpAddress: 0.0.0.0
XPPC-MIB::trapsReceiverAddr.8 = IpAddress: 0.0.0.0
XPPC-MIB::receiverCommunityString.1 = STRING: "public"
XPPC-MIB::receiverCommunityString.2 = STRING: "public"
XPPC-MIB::receiverCommunityString.3 = STRING: "public"
XPPC-MIB::receiverCommunityString.4 = STRING: "public"
XPPC-MIB::receiverCommunityString.5 = STRING: "public"
XPPC-MIB::receiverCommunityString.6 = STRING: "public"
XPPC-MIB::receiverCommunityString.7 = STRING: "public"
XPPC-MIB::receiverCommunityString.8 = STRING: "public"
XPPC-MIB::severityLevel.1 = INTEGER: information(1)
XPPC-MIB::severityLevel.2 = INTEGER: information(1)
XPPC-MIB::severityLevel.3 = INTEGER: information(1)
XPPC-MIB::severityLevel.4 = INTEGER: information(1)
XPPC-MIB::severityLevel.5 = INTEGER: information(1)
XPPC-MIB::severityLevel.6 = INTEGER: information(1)
XPPC-MIB::severityLevel.7 = INTEGER: information(1)
XPPC-MIB::severityLevel.8 = INTEGER: information(1)
XPPC-MIB::receiverAccept.1 = INTEGER: no(2)
XPPC-MIB::receiverAccept.2 = INTEGER: no(2)
XPPC-MIB::receiverAccept.3 = INTEGER: no(2)
XPPC-MIB::receiverAccept.4 = INTEGER: no(2)
XPPC-MIB::receiverAccept.5 = INTEGER: no(2)
XPPC-MIB::receiverAccept.6 = INTEGER: no(2)
XPPC-MIB::receiverAccept.7 = INTEGER: no(2)
XPPC-MIB::receiverAccept.8 = INTEGER: no(2)
End of MIB

And then here is the one for -On walk :

.1.3.6.1.4.1.935.1.1.1.1.1.1.0 = STRING: "Intelligent LiebertPSI"
.1.3.6.1.4.1.935.1.1.1.1.1.2.0 = ""
.1.3.6.1.4.1.935.1.1.1.1.2.1.0 = STRING: "EX000842  "
.1.3.6.1.4.1.935.1.1.1.1.2.2.0 = ""
.1.3.6.1.4.1.935.1.1.1.1.2.3.0 = ""
.1.3.6.1.4.1.935.1.1.1.1.2.4.0 = STRING: "2.39.CP504.ABE.00"
.1.3.6.1.4.1.935.1.1.1.2.1.1.0 = INTEGER: batteryNormal(2)
.1.3.6.1.4.1.935.1.1.1.2.1.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.2.1.3.0 = ""
.1.3.6.1.4.1.935.1.1.1.2.2.1.0 = INTEGER: 100
.1.3.6.1.4.1.935.1.1.1.2.2.2.0 = INTEGER: 550
.1.3.6.1.4.1.935.1.1.1.2.2.3.0 = INTEGER: 300
.1.3.6.1.4.1.935.1.1.1.2.2.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.2.2.6.0 = INTEGER: 480
.1.3.6.1.4.1.935.1.1.1.2.2.7.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.3.1.1.0 = INTEGER: 1
.1.3.6.1.4.1.935.1.1.1.3.2.1.0 = INTEGER: 2405
.1.3.6.1.4.1.935.1.1.1.3.2.2.0 = INTEGER: 2571
.1.3.6.1.4.1.935.1.1.1.3.2.3.0 = INTEGER: 2164
.1.3.6.1.4.1.935.1.1.1.3.2.4.0 = INTEGER: 500
.1.3.6.1.4.1.935.1.1.1.3.2.5.0 = INTEGER: noTransfer(1)
.1.3.6.1.4.1.935.1.1.1.4.1.1.0 = INTEGER: standBy(8)
.1.3.6.1.4.1.935.1.1.1.4.1.2.0 = INTEGER: 1
.1.3.6.1.4.1.935.1.1.1.4.2.1.0 = INTEGER: 2425
.1.3.6.1.4.1.935.1.1.1.4.2.2.0 = INTEGER: 500
.1.3.6.1.4.1.935.1.1.1.4.2.3.0 = INTEGER: 18
.1.3.6.1.4.1.935.1.1.1.5.1.1.0 = INTEGER: 4
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.1.1 = INTEGER: 1
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.1.2 = INTEGER: 2
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.1.3 = INTEGER: 3
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.1.4 = INTEGER: 4
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.2.1 = ""
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.2.2 = ""
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.2.3 = ""
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.2.4 = ""
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.3.1 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.3.2 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.3.3 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.3.4 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.4.1 = INTEGER: no(2)
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.4.2 = INTEGER: no(2)
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.4.3 = INTEGER: no(2)
.1.3.6.1.4.1.935.1.1.1.5.1.2.1.4.4 = INTEGER: no(2)
.1.3.6.1.4.1.935.1.1.1.5.2.1.0 = INTEGER: 2300
.1.3.6.1.4.1.935.1.1.1.5.2.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.5.2.3.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.5.2.5.0 = INTEGER: 2147483647
.1.3.6.1.4.1.935.1.1.1.5.2.8.0 = INTEGER: 120
.1.3.6.1.4.1.935.1.1.1.5.2.9.0 = INTEGER: 60
.1.3.6.1.4.1.935.1.1.1.5.2.10.0 = INTEGER: 120
.1.3.6.1.4.1.935.1.1.1.5.2.11.0 = INTEGER: 2
.1.3.6.1.4.1.935.1.1.1.6.1.1.0 = INTEGER: noTurnOffUps(1)
.1.3.6.1.4.1.935.1.1.1.6.2.1.0 = INTEGER: noTurnUpsOff(1)
.1.3.6.1.4.1.935.1.1.1.6.2.2.0 = INTEGER: noRebootUps(1)
.1.3.6.1.4.1.935.1.1.1.6.2.3.0 = INTEGER: noPutUpsToSleep(1)
.1.3.6.1.4.1.935.1.1.1.6.2.4.0 = INTEGER: noSimulatePowerFailure(1)
.1.3.6.1.4.1.935.1.1.1.6.2.5.0 = INTEGER: noFlashAndBeep(1)
.1.3.6.1.4.1.935.1.1.1.6.2.6.0 = INTEGER: noUpsSmartControlTurnOnUpsLoad(1)
.1.3.6.1.4.1.935.1.1.1.7.2.1.0 = INTEGER: never(4)
.1.3.6.1.4.1.935.1.1.1.7.2.2.0 = INTEGER: noTestDiagnostics(1)
.1.3.6.1.4.1.935.1.1.1.7.2.3.0 = INTEGER: ok(1)
.1.3.6.1.4.1.935.1.1.1.7.2.4.0 = ""
.1.3.6.1.4.1.935.1.1.1.8.1.1.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.1.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.1.3.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.1.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.1.5.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.2.1.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.2.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.2.3.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.2.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.1.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.3.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.5.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.6.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.3.7.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.4.1.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.4.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.4.3.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.4.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.5.1.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.5.2.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.5.3.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.5.4.0 = INTEGER: threeInThreeOut(3)
.1.3.6.1.4.1.935.1.1.1.8.5.5.0 = INTEGER: acnormal(5)
.1.3.6.1.4.1.935.1.1.1.8.5.6.0 = INTEGER: float(7)
.1.3.6.1.4.1.935.1.1.1.8.5.7.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.6.1.0 = INTEGER: 15
.1.3.6.1.4.1.935.1.1.1.8.6.2.0 = INTEGER: open(9)
.1.3.6.1.4.1.935.1.1.1.8.6.3.0 = INTEGER: abnormal(11)
.1.3.6.1.4.1.935.1.1.1.8.6.4.0 = INTEGER: bypassmode(13)
.1.3.6.1.4.1.935.1.1.1.8.6.5.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.1.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.2.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.3.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.4.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.5.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.6.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.7.7.0 = INTEGER: no(16)
.1.3.6.1.4.1.935.1.1.1.8.8.1.0 = ""
.1.3.6.1.4.1.935.1.1.1.8.8.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.8.3.0 = ""
.1.3.6.1.4.1.935.1.1.1.8.8.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.8.5.0 = ""
.1.3.6.1.4.1.935.1.1.1.8.8.6.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.8.7.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.8.8.8.0 = ""
.1.3.6.1.4.1.935.1.1.1.9.1.1.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.2.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.3.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.4.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.5.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.6.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.7.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.8.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.9.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.10.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.1.11.0 = INTEGER: 0
.1.3.6.1.4.1.935.1.1.1.9.2.1.0 = INTEGER: 30
.1.3.6.1.4.1.935.1.1.1.9.2.2.0 = INTEGER: 10
.1.3.6.1.4.1.935.1.1.1.9.2.3.0 = INTEGER: 50
.1.3.6.1.4.1.935.1.1.1.9.2.4.0 = INTEGER: 12
.1.3.6.1.4.1.935.2.1.1.0 = INTEGER: 8
.1.3.6.1.4.1.935.2.1.2.1.1.1 = INTEGER: 1
.1.3.6.1.4.1.935.2.1.2.1.1.2 = INTEGER: 2
.1.3.6.1.4.1.935.2.1.2.1.1.3 = INTEGER: 3
.1.3.6.1.4.1.935.2.1.2.1.1.4 = INTEGER: 4
.1.3.6.1.4.1.935.2.1.2.1.1.5 = INTEGER: 5
.1.3.6.1.4.1.935.2.1.2.1.1.6 = INTEGER: 6
.1.3.6.1.4.1.935.2.1.2.1.1.7 = INTEGER: 7
.1.3.6.1.4.1.935.2.1.2.1.1.8 = INTEGER: 8
.1.3.6.1.4.1.935.2.1.2.1.2.1 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.2 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.3 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.4 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.5 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.6 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.7 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.2.8 = IpAddress: 0.0.0.0
.1.3.6.1.4.1.935.2.1.2.1.3.1 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.2 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.3 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.4 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.5 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.6 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.7 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.3.8 = STRING: "public"
.1.3.6.1.4.1.935.2.1.2.1.4.1 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.2 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.3 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.4 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.5 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.6 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.7 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.4.8 = INTEGER: information(1)
.1.3.6.1.4.1.935.2.1.2.1.5.1 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.2 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.3 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.4 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.5 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.6 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.7 = INTEGER: no(2)
.1.3.6.1.4.1.935.2.1.2.1.5.8 = INTEGER: no(2)
End of MIB


On Mon, Aug 8, 2011 at 2:53 AM, Arnaud Quette <aquette.dev at gmail.com> wrote:
>
> 2011/8/4 John Huong <jahuong at gmail.com>
>>
>> Ok. Here we go:
>>
>> SNMPv2-SMI::enterprises.935.1.1.1.1.1.1.0 = STRING: "Intelligent
>> LiebertPSI"
>> SNMPv2-SMI::enterprises.935.1.1.1.1.1.2.0 = ""
>> (...)
>
> this first walk is not useful if you don't have the MIB file installed.
> interestingly, your MIB (.935) is not the same as Philip's one (.476), and
> seems to be from Phoenixtec.
> you should already have it underhand, otherwise you can download it here for
> example:
> http://www.icamview.com/pub/pub/netagent%20utility/Upsmate.rar
>
> install it in /usr/share/mibs/netsnmp/ or equivalent on your system.
> then do the '-OS' walk again.
> and check this thread for a procedure to create a new mib to nut mapping:
> http://lists.alioth.debian.org/pipermail/nut-upsdev/2011-February/005272.html
>
> at least, identify the more possible matches, and I'll help you creating and
> integrating the files when I have some spare time...
>
> cheers,
> Arnaud
>
>
>



More information about the Nut-upsuser mailing list