[Nut-upsuser] Status OB (on battery) when polling a Liebert PSA
    Arjen de Korte 
    nut+users at de-korte.org
       
    Sun Feb  6 11:26:24 UTC 2011
    
    
  
Citeren Pier Paolo Glave <pierpaolo.glave op gmail.com>:
> Everything seems to be fine, except that, when I run "upsc
> liebert op localhostups.status", it retuns "OB", even if the UPS is
> currently online.
Looking at the rejected earlier message, I'd say you have a Belkin OEM  
device that has a very broken report descriptor. You may want to  
checkout the recently released nut-2.6.0 version. But I'm almost  
certain that the fixes in the HID parser are not going to solve this  
problem and that instead the problem is in the UPS itself. We may or  
may not be able to work around this, but in that case we will need  
lots of support from you (and you must be willing/capable to run the  
development version too).
[...]
> I would like to paste also a complete tracing of "/lib/nut/usbhid-ups -DDDDD
> -a liebert", but the message would become too big.
Then use gzip to compress it before attaching. We really need the full  
listing as an attachment, not inline in a message.
Best regards, Arjen
-- 
Please keep list traffic on the list (off-list replies will be rejected)
    
    
More information about the Nut-upsuser
mailing list