[Nut-upsuser] APC Smart-UPS 1000

Charles Lepple clepple at gmail.com
Sun Feb 6 14:06:57 UTC 2011


On Sun, Feb 6, 2011 at 8:29 AM, Kevin <bakdong at gmail.com> wrote:
> I know it's very old code, but if it helps at all I know that this modified
> shutdown function in hidups works:
>
> void upsdrv_shutdown(void)
> {
>        /* XXX: replace with a proper shutdown function
>        fatalx("shutdown not supported"); */
>
>        /* 1) set DelayBeforeStartup */
>        if (getval ("ondelay"))
>                ondelay = atoi (getval ("ondelay"));
>
>        /* setvalue(UPS_WAKEDELAY, ondelay); */ /* commented out this line
> for APC CS 500 */
>
>        /* 2) set DelayBeforeShutdown */
>        if (getval ("offdelay"))
>                offdelay = atoi (getval ("offdelay"));
>
>        /* setvalue(UPS_GRACEDELAY, offdelay); */
>        setvalue(0xff86007c, 1); /* changed this line for APC CS 500 */
> }

It looks like the only uncommented code which talks to the device is
the last line. (The results from the getval() calls do not seem to be
used.)

APCDelayBeforeReboot maps to 0xff86007c, so Arjen's suggestion to
change the 10 to 1 should be equivalent to the setvalue() line at the
end.

-- 
- Charles Lepple