on 06/02/2011 18:19 Arjen de Korte wrote:
> Citeren Kevin <bakdong at gmail.com>:
>
>> Seems to have gone a bit quiet. Are we at a dead end now?
>
> No, I just don't have a lot of spare time on my hand lately.
That's ok. I quite understand. Thank you for all your help so far.
> You could
> try if changing
>
> { "shutdown.reboot", 0, 0,
> "UPS.APCGeneralCollection.APCDelayBeforeReboot", NULL, "10",
> HU_TYPE_CMD, NULL },
>
> to
>
> { "shutdown.return", 0, 0,
> "UPS.APCGeneralCollection.APCDelayBeforeReboot", NULL, "1", HU_TYPE_CMD,
> NULL },
>
Thank you. I will try that and see what happens.
I know it's very old code, but if it helps at all I know that this
modified shutdown function in hidups works:
void upsdrv_shutdown(void)
{
/* XXX: replace with a proper shutdown function
fatalx("shutdown not supported"); */
/* 1) set DelayBeforeStartup */
if (getval ("ondelay"))
ondelay = atoi (getval ("ondelay"));
/* setvalue(UPS_WAKEDELAY, ondelay); */ /* commented out this
line for APC CS 500 */
/* 2) set DelayBeforeShutdown */
if (getval ("offdelay"))
offdelay = atoi (getval ("offdelay"));
/* setvalue(UPS_GRACEDELAY, offdelay); */
setvalue(0xff86007c, 1); /* changed this line for APC CS 500 */
}
> helps. Looking in the apcupsd sources seems to indicate that this isn't
> a timer at all, but instead just a flag that forces a reboot cycle.
>
> Given the brokenness of the APC HID PDC implementation (the apcupsd
> project uses about half a dozen ways to shutdown), I doubt that the
> support status of APC is going to improve a lot. If you have not already
> tried the apcupsd project, I'd suggest to try that too. Since NUT is not
> focussed on one specific make, we probably can never give the same
> support. This is also due to the fact that none of the active developers
> has access to one of these devices.
Thanks again, I will have a look.