> Thanks a bunch, that worked like a charm :)
Glad to hear that.
> But now I've got another question... After I run commands (tests) with
> upscmd, where do I see the results?
You don't.
> Ran a battery test check and it did not give any output.
Only if the UPS finds that the battery needs to be replaced it will
report the 'RB' status (replace battery). If it doesn't, all is well.
The Q1 protocol that is used by your UPS doesn't support more verbose
messages (and neither does it report runtime or charge capacity) so
there is nothing more to report.
Best regards, Arjen
--