> Here's something more I've found using the new soft. Please take a look.
If you have such a table available, you can figure out quite easily
which upstype is applicable here:
cable power = DTR
online = CTS off
low battery = CD on
This looks like a 'genericups upstype=3' or 'genericups upstype=20'
device. The only thing left to check is which shutdown command works
(most likely, the UPS has to be on battery for that to work).
Best regards, Arjen
--