On Sat, Sep 24, 2011 at 5:00 PM, Tim Gould <tgould at reverb.com.au> wrote:
> -DDD output attached.
Given that the ConfigVoltage should not change for a given UPS, this
should be useful:
0.413040 Report[get]: (3 bytes) => 1d 11 01
0.413075 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID:
0x1d, Offset: 0, Size: 16, Value: 2.73e-06
0.417039 Report[get]: (3 bytes) => 1f 18 00
0.417063 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
ReportID: 0x1f, Offset: 0, Size: 16, Value: 2.4e-07
0.421044 Report[get]: (2 bytes) => 07 0d
0.421080 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x07, Offset: 0, Size: 1, Value: 1e-07
0.421096 Report[buf]: (2 bytes) => 07 0d
If you multiply those values by 1e7, they should all be right. It
looks like a misplaced exponent in the HID descriptor.
--
- Charles Lepple