[Nut-upsuser] [BUG] nut 2.4.3+: UPS EP-1K: Firmware fault: USB-Interface crashes with nut.org monitoring if driver polling time <15 sec
    thomas schorpp 
    thomas.schorpp at googlemail.com
       
    Wed Sep 28 14:54:23 UTC 2011
    
    
  
@fsp
Please forward to development, manufacturing and quality management department:
Model EP1000(PPF6000/100), 431107300095, 4711140480534, Art-Nr. 8296861, 70539, 14Z00000, 35-0200116-01G
@nut-users
http://www.networkupstools.org/ 2.4.3 debian stable, 2.6.2 upstream, linux 2.6.38-debian-bpo
# /usr/local/src/nut-2.6.2/drivers/blazer_usb -u root -DDDDD -a ups
Network UPS Tools - Megatec/Q1 protocol USB driver 0.03 (2.6.2)
    0.000000	send_to_all: SETINFO driver.parameter.port "auto"
    0.000080	send_to_all: SETINFO driver.parameter.chargetime "8"
    0.000104	send_to_all: SETINFO driver.parameter.runtimecal "1200,100,3200,50"
    0.000381	debug level is '5'
    0.081525	Checking device (0D8C/0006) (005/002)
   ...
    0.179808	Trying to match device
    0.179822	Device does not match - skipping
    0.179845	Checking device (0665/5161) (001/007)
    0.183682	- VendorID: 0665
    0.183707	- ProductID: 5161
    0.183780	- Manufacturer: unknown
    0.183791	- Product: USB to Serial
    0.183801	- Serial Number: 20100813
    0.183811	- Bus: 001
    0.183820	Trying to match device
    0.183833	Device matches
    0.184323	send_to_all: SETINFO ups.vendorid "0665"
    0.184342	send_to_all: SETINFO ups.productid "5161"
    0.184371	send_to_all: SETINFO device.type "ups"
    0.184397	send_to_all: SETINFO driver.version "2.6.2"
    0.184413	send_to_all: SETINFO driver.version.internal "0.03"
    0.184428	send_to_all: SETINFO driver.name "blazer_usb"
    0.184442	Trying megatec protocol...
    0.185778	send: Q1
    0.246367	read: Q1
    0.246412	blazer_status: short reply
    0.246425	Status read 1 failed
    0.247045	send: Q1
    0.310340	read: Q1
    0.310376	blazer_status: short reply
    0.310388	Status read 2 failed
    0.310920	send: Q1
    0.374377	read: Q1
    0.374416	blazer_status: short reply
    0.374430	Status read 3 failed
    0.374442	Trying mustek protocol...
    0.375215	send: QS
    0.630323	read: (231.2 231.2 231.2 027 50.1 27.4 --.- 00001001
    0.630419	send_to_all: SETINFO input.voltage "231.2"
    0.630444	send_to_all: SETINFO input.voltage.fault "231.2"
    0.630462	send_to_all: SETINFO output.voltage "231.2"
    0.630502	send_to_all: SETINFO ups.load "27"
    0.630521	send_to_all: SETINFO input.frequency "50.1"
    0.630541	send_to_all: SETINFO battery.voltage "27.40"
    0.630553	blazer_status: non numerical value [--.-]
    0.630568	send_to_all: SETINFO beeper.status "enabled"
    0.630585	send_to_all: SETINFO ups.type "offline / line interactive"
    0.630603	send_to_all: SETINFO ups.status "OL"
    0.630616	Status read in 1 tries
    0.630628	Supported UPS detected with mustek protocol
    0.631285	send: F
    0.758275	read: #220.0 005 24.00 50.0
    0.758390	send_to_all: SETINFO input.voltage.nominal "220"
    0.758410	send_to_all: SETINFO input.current.nominal "5.0"
    0.758431	send_to_all: SETINFO battery.voltage.nominal "24.0"
    0.758450	send_to_all: SETINFO input.frequency.nominal "50"
    0.758463	Ratings read in 1 tries
    0.759118	send: I
    0.822314	read: I
    0.822349	blazer_vendor: short reply
    0.822362	Vendor information read 1 failed
    0.822988	send: I
    0.886255	read: I
    0.886292	blazer_vendor: short reply
    0.886305	Vendor information read 2 failed
    0.886979	send: I
    0.950253	read: I
    0.950346	blazer_vendor: short reply
    0.950359	Vendor information read 3 failed
    0.950371	Vendor information unavailable
    0.950447	battery runtime exponent : 1.415
    0.950477	battery runtime nominal  : 1200.0
    0.950504	send_to_all: SETINFO battery.charge "94"
    0.950520	battery runtime estimate : 1128.0
    0.950533	battery charge time      : 8
    0.950545	No idle load specified, using built in default [10.0 %]
    0.950562	send_to_all: SETINFO ups.delay.start "180"
    0.950576	send_to_all: SETINFO ups.delay.shutdown "30"
    0.950590	send_to_all: ADDCMD beeper.toggle
    0.950602	send_to_all: ADDCMD load.off
    0.950614	send_to_all: ADDCMD load.on
    0.950627	send_to_all: ADDCMD shutdown.return
    0.950641	send_to_all: ADDCMD shutdown.stayoff
    0.950654	send_to_all: ADDCMD shutdown.stop
    0.950668	send_to_all: ADDCMD test.battery.start
    0.950741	send_to_all: ADDCMD test.battery.start.deep
    0.950755	send_to_all: ADDCMD test.battery.start.quick
    0.950769	send_to_all: ADDCMD test.battery.stop
    0.951532	send: QS
    1.207958	read: (231.2 231.2 231.2 027 50.1 27.4 --.- 00001001
    1.208145	blazer_status: non numerical value [--.-]
    1.208176	send_to_all: SETINFO battery.charge "100"
    1.208205	send_to_all: SETINFO battery.runtime "7653"
    1.208220	send_to_all: DATAOK
    1.208789	dstate_init: sock /var/state/ups/blazer_usb-ups open on fd 5
    1.208824	send_to_all: SETINFO driver.parameter.pollinterval "15"
    1.209837	send: QS
    1.462236	read: (231.2 231.2 231.2 028 50.1 27.4 --.- 00001001
    1.462441	send_to_all: SETINFO ups.load "28"
    1.462466	blazer_status: non numerical value [--.-]
    1.462512	send_to_all: SETINFO battery.runtime "7269"
   16.222071	send: QS
   16.468629	read: (231.2 231.2 231.2 026 50.1 27.4 --.- 00001001
   16.468798	send_to_all: SETINFO ups.load "26"
   16.468825	blazer_status: non numerical value [--.-]
   16.468854	send_to_all: SETINFO battery.runtime "8073"
   31.231186	send: QS
   31.475165	read: (231.2 231.2 231.2 026 50.1 27.4 --.- 00001001
   31.475245	blazer_status: non numerical value [--.-]
   46.244356	send: QS
   46.481487	read: (231.2 231.2 231.2 025 50.1 27.4 --.- 00001001
   46.481617	send_to_all: SETINFO ups.load "25"
   46.481643	blazer_status: non numerical value [--.-]
   46.481672	send_to_all: SETINFO battery.runtime "8533"
...
  565.543591	send: QS
  565.783246	read: (231.2 231.2 231.2 027 50.1 27.4 --.- 00001001
  565.783376	send_to_all: SETINFO ups.load "27"
  565.783401	blazer_status: non numerical value [--.-]
  565.783430	send_to_all: SETINFO battery.runtime "7653"
  568.541003	send: error sending control message: Connection timed out
  568.541174	blazer_status: short reply
  568.541188	Communications with UPS lost: status read failed!
^C
tom1:~#
tom1:~# /lib/nut/blazer_usb  -DDDDD -a ups
Network UPS Tools - Megatec/Q1 protocol USB driver 0.03 (2.4.3)
    0.000000	send_to_all: SETINFO driver.parameter.port "auto"
    0.000082	send_to_all: SETINFO driver.parameter.chargetime "8"
    0.000115	send_to_all: SETINFO driver.parameter.runtimecal "1200,100,3200,50"
    0.000360	debug level is '5'
    ...
    0.088412	Checking device (0665/5161) (001/007)
    0.092398	- VendorID: 0665
    0.092425	- ProductID: 5161
    0.092436	- Manufacturer: unknown
    0.092450	- Product: USB to Serial
    0.092461	- Serial Number: 20100813
    0.092472	- Bus: 001
    0.092482	Trying to match device
    0.092497	Device matches
    0.097414	send_to_all: SETINFO ups.vendorid "0665"
    0.097460	send_to_all: SETINFO ups.productid "5161"
    0.097539	send_to_all: SETINFO device.type "ups"
    0.097556	send_to_all: SETINFO driver.version "2.4.3"
    0.097572	send_to_all: SETINFO driver.version.internal "0.03"
    0.097588	send_to_all: SETINFO driver.name "blazer_usb"
    0.097601	Trying megatec protocol...
    0.099736	send: Q1
    1.099839	read: error sending control message: Operation not permitted
    1.099881	blazer_status: short reply
    1.099894	Status read 1 failed
    1.100423	send: Q1
    1.178402	read: Q1
    1.178441	blazer_status: short reply
    1.178455	Status read 2 failed
    1.179155	send: Q1
    1.242341	read: Q1
    1.242378	blazer_status: short reply
    1.242392	Status read 3 failed
    1.242405	Trying mustek protocol...
    1.244070	send: QS
    1.497320	read: (231.6 231.2 231.2 028 50.1 27.4 --.- 00001001
    1.497465	send_to_all: SETINFO input.voltage "231.6"
    1.497490	send_to_all: SETINFO input.voltage.fault "231.2"
    1.497509	send_to_all: SETINFO output.voltage "231.2"
    1.497549	send_to_all: SETINFO ups.load "28"
    1.497568	send_to_all: SETINFO input.frequency "50.1"
    1.497590	send_to_all: SETINFO battery.voltage "27.40"
    1.497602	blazer_status: non numerical value [--.-]
    1.497619	send_to_all: SETINFO beeper.status "enabled"
    1.497649	send_to_all: SETINFO ups.type "offline / line interactive"
    1.497668	send_to_all: SETINFO ups.status "OL"
    1.497680	Status read in 1 tries
    1.497693	Supported UPS detected with mustek protocol
    1.498249	send: F
    1.625271	read: #220.0 005 24.00 50.0
    1.625417	send_to_all: SETINFO input.voltage.nominal "220"
    1.625437	send_to_all: SETINFO input.current.nominal "5.0"
    1.625458	send_to_all: SETINFO battery.voltage.nominal "24.0"
    1.625477	send_to_all: SETINFO input.frequency.nominal "50"
    1.625490	Ratings read in 1 tries
    1.626551	send: I
    1.689331	read: I
    1.689368	blazer_vendor: short reply
    1.689383	Vendor information read 1 failed
    1.690100	send: I
    1.753241	read: I
    1.753295	blazer_vendor: short reply
    1.753311	Vendor information read 2 failed
    1.753720	send: I
    1.817243	read: I
    1.817312	blazer_vendor: short reply
    1.817327	Vendor information read 3 failed
    1.817339	Vendor information unavailable
    1.817407	battery runtime exponent : 1.415
    1.817440	battery runtime nominal  : 1200.0
    1.817472	send_to_all: SETINFO battery.charge "94"
    1.817550	battery runtime estimate : 1128.0
    1.817563	battery charge time      : 8
    1.817604	No idle load specified, using built in default [10.0 %]
    1.817622	send_to_all: SETINFO ups.delay.start "180"
    1.817638	send_to_all: SETINFO ups.delay.shutdown "30"
    1.817653	send_to_all: ADDCMD beeper.toggle
    1.817667	send_to_all: ADDCMD load.off
    1.817680	send_to_all: ADDCMD load.on
    1.817694	send_to_all: ADDCMD shutdown.return
    1.817709	send_to_all: ADDCMD shutdown.stayoff
    1.817724	send_to_all: ADDCMD shutdown.stop
    1.817737	send_to_all: ADDCMD test.battery.start
    1.817751	send_to_all: ADDCMD test.battery.start.deep
    1.817765	send_to_all: ADDCMD test.battery.start.quick
    1.817780	send_to_all: ADDCMD test.battery.stop
    1.820719	send: QS
    2.074009	read: (231.2 231.6 231.6 029 50.1 27.4 --.- 00001001
    2.074067	send_to_all: SETINFO input.voltage "231.2"
    2.074146	send_to_all: SETINFO input.voltage.fault "231.6"
    2.074165	send_to_all: SETINFO output.voltage "231.6"
    2.074203	send_to_all: SETINFO ups.load "29"
    2.074227	blazer_status: non numerical value [--.-]
    2.074257	send_to_all: SETINFO battery.runtime "6502"
    2.074270	send_to_all: DATAOK
    2.074414	dstate_init: sock /var/run/nut/blazer_usb-ups open on fd 5
    2.074436	send_to_all: SETINFO driver.parameter.pollinterval "15"
    2.075189	send: QS
    2.329181	read: (231.6 231.2 231.2 029 50.1 27.4 --.- 00001001
    2.329254	send_to_all: SETINFO input.voltage "231.6"
    2.329300	send_to_all: SETINFO input.voltage.fault "231.2"
    2.329322	send_to_all: SETINFO output.voltage "231.2"
    2.329361	blazer_status: non numerical value [--.-]
    2.329387	send_to_all: SETINFO battery.charge "100"
    2.329405	send_to_all: SETINFO battery.runtime "6917"
   17.089915	send: QS
   17.335594	read: (231.6 231.2 231.2 026 50.1 27.4 --.- 00001001
   17.335656	send_to_all: SETINFO ups.load "26"
   17.335672	blazer_status: non numerical value [--.-]
   17.335696	send_to_all: SETINFO battery.runtime "8073"
   32.101933	send: QS
   32.342038	read: (231.2 231.6 231.2 026 50.1 27.4 --.- 00001001
   32.342097	send_to_all: SETINFO input.voltage "231.2"
   32.342253	send_to_all: SETINFO input.voltage.fault "231.6"
   32.342290	blazer_status: non numerical value [--.-]
   47.114708	send: QS
   47.380472	read: (231.2 231.6 231.2 026 50.1 27.4 --.- 00001001
   47.380553	blazer_status: non numerical value [--.-]
   62.123783	send: QS
   62.387165	read: (231.6 231.6 231.6 026 50.1 27.4 --.- 00001001
   62.387222	send_to_all: SETINFO input.voltage "231.6"
   62.387257	send_to_all: SETINFO output.voltage "231.6"
   62.387290	blazer_status: non numerical value [--.-]
   77.136465	send: QS
   77.393745	read: (231.6 231.6 231.6 025 50.1 27.4 --.- 00001001
   77.393829	send_to_all: SETINFO ups.load "25"
   77.393863	blazer_status: non numerical value [--.-]
   77.393893	send_to_all: SETINFO battery.runtime "8533"
   92.149897	send: QS
   92.399733	read: (231.6 231.6 231.6 026 50.1 27.4 --.- 00001001
   92.399812	send_to_all: SETINFO ups.load "26"
   92.399838	blazer_status: non numerical value [--.-]
   92.399867	send_to_all: SETINFO battery.runtime "8073"
  107.165453	send: QS
  107.406217	read: (231.6 231.6 231.6 027 50.1 27.4 --.- 00001001
  107.406290	send_to_all: SETINFO ups.load "27"
  107.406316	blazer_status: non numerical value [--.-]
  107.406345	send_to_all: SETINFO battery.runtime "7653"
^C 109.161376	Signal 2: exiting
tom1:~#
tom1:~# grep 'usb 1-3.2' /var/log/syslog.0
Sep 27 13:02:15 tom1 kernel: [  738.052154] usb 1-3.2: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret -110
...
Sep 27 21:36:03 tom1 kernel: [31566.152163] usb 1-3.2: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret -110
Sep 27 21:38:44 tom1 kernel: [31726.256161] usb 1-3.2: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret -110
Sep 27 21:38:50 tom1 kernel: [31732.520148] usb 1-3.2: reset low speed USB device using ehci_hcd and address 7
Sep 27 21:39:05 tom1 kernel: [31747.780471] usb 1-3.2: device descriptor read/64, error -110
Sep 27 21:39:20 tom1 kernel: [31763.144217] usb 1-3.2: device descriptor read/64, error -110
Sep 27 21:39:21 tom1 kernel: [31763.510030] usb 1-3.2: reset low speed USB device using ehci_hcd and address 7
Sep 27 21:39:36 tom1 kernel: [31778.768238] usb 1-3.2: device descriptor read/64, error -110
Sep 27 21:39:51 tom1 kernel: [31794.132257] usb 1-3.2: device descriptor read/64, error -110
Sep 27 21:39:52 tom1 kernel: [31794.496217] usb 1-3.2: reset low speed USB device using ehci_hcd and address 7
Sep 27 21:39:57 tom1 kernel: [31799.904036] usb 1-3.2: device not accepting address 7, error -32
Sep 27 21:39:57 tom1 kernel: [31800.164132] usb 1-3.2: reset low speed USB device using ehci_hcd and address 7
Sep 27 21:39:58 tom1 kernel: [31800.572033] usb 1-3.2: device not accepting address 7, error -32
Sep 27 21:39:58 tom1 kernel: [31800.573336] usb 1-3.2: USB disconnect, address 7
Sep 27 21:39:58 tom1 kernel: [31800.660202] usb 1-3.2: new low speed USB device using ehci_hcd and address 16
Sep 27 21:39:58 tom1 kernel: [31800.748168] usb 1-3.2: device descriptor read/64, error -32
Sep 27 21:39:58 tom1 kernel: [31800.940173] usb 1-3.2: device descriptor read/64, error -32
Sep 27 21:39:58 tom1 kernel: [31801.132152] usb 1-3.2: new low speed USB device using ehci_hcd and address 17
Sep 27 21:39:59 tom1 kernel: [31801.220519] usb 1-3.2: device descriptor read/64, error -32
Sep 27 21:39:59 tom1 kernel: [31801.412121] usb 1-3.2: device descriptor read/64, error -32
Sep 27 21:39:59 tom1 kernel: [31801.604395] usb 1-3.2: new low speed USB device using ehci_hcd and address 18
Sep 27 21:39:59 tom1 kernel: [31802.012699] usb 1-3.2: device not accepting address 18, error -32
Sep 27 21:39:59 tom1 kernel: [31802.100177] usb 1-3.2: new low speed USB device using ehci_hcd and address 19
Sep 27 21:40:00 tom1 kernel: [31802.508033] usb 1-3.2: device not accepting address 19, error -32
Sep 27 22:02:25 tom1 kernel: [33147.836232] usb 1-3.2: new low speed USB device using ehci_hcd and address 20
Sep 27 22:02:25 tom1 kernel: [33147.924343] usb 1-3.2: device descriptor read/64, error -32
Sep 27 22:02:25 tom1 kernel: [33148.116203] usb 1-3.2: device descriptor read/64, error -32
Sep 27 22:02:26 tom1 kernel: [33148.308218] usb 1-3.2: new low speed USB device using ehci_hcd and address 21
Sep 27 22:02:26 tom1 kernel: [33148.400220] usb 1-3.2: device descriptor read/64, error -32
Sep 27 22:02:26 tom1 kernel: [33148.592281] usb 1-3.2: device descriptor read/64, error -32
Sep 27 22:02:26 tom1 kernel: [33148.784192] usb 1-3.2: new low speed USB device using ehci_hcd and address 22
Sep 27 22:02:26 tom1 kernel: [33149.192035] usb 1-3.2: device not accepting address 22, error -32
Sep 27 22:02:27 tom1 kernel: [33149.282324] usb 1-3.2: new low speed USB device using ehci_hcd and address 23
Sep 27 22:02:27 tom1 kernel: [33149.688347] usb 1-3.2: device not accepting address 23, error -32
Sep 27 23:21:58 tom1 kernel: [37920.456121] usb 1-3.2: new low speed USB device using ehci_hcd and address 24
Sep 27 23:21:58 tom1 kernel: [37920.544084] usb 1-3.2: device descriptor read/64, error -32
Sep 27 23:21:58 tom1 kernel: [37920.740213] usb 1-3.2: device descriptor read/64, error -32
Sep 27 23:21:58 tom1 kernel: [37920.932199] usb 1-3.2: new low speed USB device using ehci_hcd and address 25
Sep 27 23:21:58 tom1 kernel: [37921.020176] usb 1-3.2: device descriptor read/64, error -32
Sep 27 23:21:59 tom1 kernel: [37921.212167] usb 1-3.2: device descriptor read/64, error -32
Sep 27 23:21:59 tom1 kernel: [37921.404126] usb 1-3.2: new low speed USB device using ehci_hcd and address 26
Sep 27 23:21:59 tom1 kernel: [37921.812063] usb 1-3.2: device not accepting address 26, error -32
Sep 27 23:21:59 tom1 kernel: [37921.900197] usb 1-3.2: new low speed USB device using ehci_hcd and address 27
Sep 27 23:22:00 tom1 kernel: [37922.308071] usb 1-3.2: device not accepting address 27, error -32
Sep 28 00:33:03 tom1 kernel: [    2.956070] usb 1-3.2: new low speed USB device using ehci_hcd and address 7
Sep 28 00:33:03 tom1 kernel: [    3.070562] usb 1-3.2: New USB device found, idVendor=0665, idProduct=5161
Sep 28 00:33:03 tom1 kernel: [    3.070630] usb 1-3.2: New USB device strings: Mfr=1, Product=2, SerialNumber=3
Sep 28 00:33:03 tom1 kernel: [    3.070708] usb 1-3.2: Product: USB to Serial
Sep 28 00:33:03 tom1 kernel: [    3.070772] usb 1-3.2: Manufacturer: INNO TECH
Sep 28 00:33:03 tom1 kernel: [    3.070835] usb 1-3.2: SerialNumber: 20100813
tom1:~# lsusb
Bus 005 Device 002: ID 0d8c:0006 C-Media Electronics, Inc. Storm HP-USB500 5.1 Headset
Bus 005 Device 001: ID 1d6b:0001 Linux Foundation 1.1 root hub
Bus 004 Device 001: ID 1d6b:0001 Linux Foundation 1.1 root hub
Bus 003 Device 002: ID 0c4b:9102 Reiner SCT Kartensysteme GmbH
Bus 003 Device 001: ID 1d6b:0001 Linux Foundation 1.1 root hub
Bus 002 Device 001: ID 1d6b:0001 Linux Foundation 1.1 root hub
Bus 001 Device 013: ID 067b:0001 Prolific Technology, Inc. PL2302 USB-USB Bridge
Bus 001 Device 012: ID 06f2:0011 Emine Technology Co. KVM Switch Keyboard
Bus 001 Device 010: ID 04fc:05d8 Sunplus Technology Co., Ltd Wireless keyboard/mouse
Bus 001 Device 009: ID 145f:013e Trust
Bus 001 Device 008: ID 148f:2573 Ralink Technology, Corp. RT2501/RT2573 Wireless Adapter
Bus 001 Device 007: ID 0665:5161 Cypress Semiconductor USB to Serial
Bus 001 Device 006: ID 1462:8807 Micro Star International DIGIVOX mini III [af9015]
Bus 001 Device 005: ID 05e3:0606 Genesys Logic, Inc. USB 2.0 Hub / D-Link DUB-H4 USB 2.0 Hub
Bus 001 Device 002: ID 058f:6254 Alcor Micro Corp. USB Hub
Bus 001 Device 001: ID 1d6b:0002 Linux Foundation 2.0 root hub
tom1:~# lsusb -t
/:  Bus 05.Port 1: Dev 1, Class=root_hub, Driver=uhci_hcd/2p, 12M
     |__ Port 1: Dev 2, If 0, Class=audio, Driver=snd-usb-audio, 12M
     |__ Port 1: Dev 2, If 1, Class=audio, Driver=snd-usb-audio, 12M
     |__ Port 1: Dev 2, If 2, Class=audio, Driver=snd-usb-audio, 12M
     |__ Port 1: Dev 2, If 3, Class=HID, Driver=usbhid, 12M
/:  Bus 04.Port 1: Dev 1, Class=root_hub, Driver=uhci_hcd/2p, 12M
/:  Bus 03.Port 1: Dev 1, Class=root_hub, Driver=uhci_hcd/2p, 12M
     |__ Port 2: Dev 2, If 0, Class=scard, Driver=usbfs, 12M
/:  Bus 02.Port 1: Dev 1, Class=root_hub, Driver=uhci_hcd/2p, 12M
/:  Bus 01.Port 1: Dev 1, Class=root_hub, Driver=ehci_hcd/8p, 480M
     |__ Port 3: Dev 2, If 0, Class=hub, Driver=hub/4p, 480M
         |__ Port 1: Dev 6, If 0, Class=vend., Driver=dvb_usb_af9015, 480M
         |__ Port 2: Dev 7, If 0, Class=HID, Driver=usbfs, 1.5M
         |__ Port 3: Dev 8, If 0, Class=vend., Driver=rt73usb, 480M
         |__ Port 4: Dev 9, If 0, Class='bInterfaceClass 0x0e not yet handled', Driver=uvcvideo, 480M
         |__ Port 4: Dev 9, If 1, Class='bInterfaceClass 0x0e not yet handled', Driver=uvcvideo, 480M
         |__ Port 4: Dev 9, If 2, Class=audio, Driver=snd-usb-audio, 480M
         |__ Port 4: Dev 9, If 3, Class=audio, Driver=snd-usb-audio, 480M
     |__ Port 8: Dev 5, If 0, Class=hub, Driver=hub/4p, 480M
         |__ Port 1: Dev 10, If 0, Class=HID, Driver=usbhid, 1.5M
         |__ Port 1: Dev 10, If 1, Class=HID, Driver=usbhid, 1.5M
         |__ Port 3: Dev 12, If 0, Class=HID, Driver=usbhid, 1.5M
         |__ Port 3: Dev 12, If 1, Class=HID, Driver=usbhid, 1.5M
         |__ Port 4: Dev 13, If 0, Class=vend., Driver=plusb, 480M
tom1:~# lsusb -vvv -d 0665:5161
Bus 001 Device 007: ID 0665:5161 Cypress Semiconductor USB to Serial
Device Descriptor:
   bLength                18
   bDescriptorType         1
   bcdUSB               1.10
   bDeviceClass            0 (Defined at Interface level)
   bDeviceSubClass         0
   bDeviceProtocol         0
   bMaxPacketSize0         8
   idVendor           0x0665 Cypress Semiconductor
   idProduct          0x5161 USB to Serial
   bcdDevice            0.02
   iManufacturer           1 INNO TECH
   iProduct                2 USB to Serial
   iSerial                 3 20100813
   bNumConfigurations      1
   Configuration Descriptor:
     bLength                 9
     bDescriptorType         2
     wTotalLength           34
     bNumInterfaces          1
     bConfigurationValue     1
     iConfiguration          3 20100813
     bmAttributes         0x80
       (Bus Powered)
     MaxPower              100mA
     Interface Descriptor:
       bLength                 9
       bDescriptorType         4
       bInterfaceNumber        0
       bAlternateSetting       0
       bNumEndpoints           1
       bInterfaceClass         3 Human Interface Device
       bInterfaceSubClass      0 No Subclass
       bInterfaceProtocol      0 None
       iInterface              4 Sample HID
         HID Device Descriptor:
           bLength                 9
           bDescriptorType        33
           bcdHID               1.00
           bCountryCode            0 Not supported
           bNumDescriptors         1
           bDescriptorType        34 Report
           wDescriptorLength      27
          Report Descriptors:
            ** UNAVAILABLE **
       Endpoint Descriptor:
         bLength                 7
         bDescriptorType         5
         bEndpointAddress     0x81  EP 1 IN
         bmAttributes            3
           Transfer Type            Interrupt
           Synch Type               None
           Usage Type               Data
         wMaxPacketSize     0x0008  1x 8 bytes
         bInterval              32
Device Status:     0x0000
   (Bus Powered)
tom1:~#