[Nut-upsuser] UPS restart delay
Daniel O'Connor
doconnor at gsoft.com.au
Thu Aug 2 23:03:54 UTC 2012
On 27/07/2012, at 17:36, Daniel O'Connor wrote:
>
> On 21/07/2012, at 22:55, Charles Lepple wrote:
>>> Does anyone know if this is possible? A setting like this would provide some hysteresis for successive power failures which would be handy to have :)
>>
>> I don't know about that specific hardware, but the variables which would control this are battery.charge.restart ("Minimum battery level for UPS restart after power-off") and ups.delay.start ("Interval to wait before restarting the load (seconds)"). Check the output of "upsrw <ups>" to see if that variable is supported with your combination of UPS and driver.
>>
>> Which version of NUT are you using? There might be a newmge-shut driver included as well.
>
> I tried mge-shut in 2.6 with no change, but newmge-shut with 2.6 showed this parameter, thanks!
Unfortunately it doesn't appear to have any effect, ie..
Aug 02 11:34:04 ups1 at localhost upslog[1524] load: 18 temp: NA voltage: 0.0 recharge: 65 frequency: 0.0 status: OB DISCHRG
Aug 02 11:39:04 ups1 at localhost upslog[1524] load: 18 temp: NA voltage: 0.0 recharge: 50 frequency: 0.0 status: OB DISCHRG
Aug 02 11:39:14 ups1 at localhost upslog[1524] load: 18 temp: NA voltage: 0.0 recharge: 50 frequency: 0.0 status: FSD OB DISCHRG LB
Aug 02 11:53:01 ups1 at localhost upslog[1524] load: 17 temp: NA voltage: 225.0 recharge: 8 frequency: 49.0 status: OL CHRG
Aug 02 11:58:01 ups1 at localhost upslog[1524] load: 18 temp: NA voltage: 225.0 recharge: 11 frequency: 50.0 status: OL CHRG
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Value: 50
[battery.charge.restart]
Minimum battery level for restart after power off (percent)
Type: STRING
Value: 60
[ups.start.auto]
UPS starts when mains is (re)applied
Type: STRING
Value: yes
[ups.start.battery]
Allow to start UPS from battery
Type: STRING
Value: no
[ups.start.reboot]
UPS reboots when power returns during shutdown delay
Type: STRING
Value: no
I have the following ups.conf entry..
[ups1]
driver = newmge-shut
port = /dev/cuau1
ondelay = 190
offdelay = 120
The delay is because I am using FreeBSD and it does not remount the disks read only - the shutdown script calls 'upsdrvctl sutdown' when everything is still mounted read/write.
I added some debugging to my shutdown script and upsdrvctl is exiting with a 0 code so I think it's doing the right thing.
Unfortunately this UPS is remote so testing it is difficult :(
Any suggestions welcome :)
--
Daniel O'Connor software and network engineer
for Genesis Software - http://www.gsoft.com.au
"The nice thing about standards is that there
are so many of them to choose from."
-- Andrew Tanenbaum
GPG Fingerprint - 5596 B766 97C0 0E94 4347 295E E593 DC20 7B3F CE8C
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/pkcs7-signature
Size: 4358 bytes
Desc: not available
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20120803/a7536aa9/attachment.bin>
More information about the Nut-upsuser
mailing list