[Nut-upsuser] Problem connecting to eaton ups. No matching HID UPS found. Driver failed to start(exit status=1)

Håvard Rabbe hrabbe at me.com
Wed Jul 18 22:35:26 UTC 2012


Hi!

Info
OS: TinyCore Linux 4.5.6
NUT version: 2.6.4
NUT innstallation method: source tarball
Device name: Eaton Ellipse ups eco 1600 usb din (EL1600USBDIN)

/usr/local/ups/etc/ups.conf file:

[eaton]
        driver = usbhid-ups
        port = auto


When I run:

root at Dalen:/usr/local/ups/bin/upsdrvctl start eaton
I get this error message:

Network UPS Tools - UPS driver controller 2.6.4
Network UPS Tools - Generic HID driver 0.37 (2.6.4)
USB communication driver 0.31
No matching HID UPS found
Driver failed to start (exit status=1)


I then run usbhid-ups

root at Dalen:/usr/local/ups/etc# /usr/local/ups/bin/usbhid-ups -u root -DD -a eaton
Network UPS Tools - Generic HID driver 0.37 (2.6.4)
USB communication driver 0.31
   0.000000	debug level is '2'
   0.001244	upsdrv_initups...
   0.076965	Checking device (1D6B/0002) (001/001)
   0.077890	- VendorID: 1d6b
   0.078385	- ProductID: 0002
   0.078756	- Manufacturer: Linux 3.0.3-tinycore ehci_hcd
   0.079166	- Product: EHCI Host Controller
   0.079544	- Serial Number: 0000:00:10.4
   0.079946	- Bus: 001
   0.080346	Trying to match device
   0.080791	Device does not match - skipping
   0.081272	Checking device (18A5/0302) (001/002)
   0.082755	- VendorID: 18a5
   0.083199	- ProductID: 0302
   0.083640	- Manufacturer: Verbatim
   0.084033	- Product: STORE N GO      
   0.084415	- Serial Number: 0000000000000580
   0.084785	- Bus: 001
   0.085185	Trying to match device
   0.085505	Device does not match - skipping
   0.085689	Checking device (1D6B/0001) (002/001)
   0.086084	- VendorID: 1d6b
   0.086437	- ProductID: 0001
   0.086486	- Manufacturer: Linux 3.0.3-tinycore uhci_hcd
   0.086629	- Product: UHCI Host Controller
   0.086772	- Serial Number: 0000:00:10.0
   0.086824	- Bus: 002
   0.086998	Trying to match device
   0.087055	Device does not match - skipping
   0.087165	Checking device (1D6B/0001) (003/001)
   0.087542	- VendorID: 1d6b
   0.087908	- ProductID: 0001
   0.088049	- Manufacturer: Linux 3.0.3-tinycore uhci_hcd
   0.088192	- Product: UHCI Host Controller
   0.088238	- Serial Number: 0000:00:10.1
   0.088386	- Bus: 003
   0.088431	Trying to match device
   0.088585	Device does not match - skipping
   0.088692	Checking device (0463/FFFF) (003/005)
   0.543897	- VendorID: 0463
   0.544300	- ProductID: ffff
   0.544419	- Manufacturer: EATON
   0.544627	- Product: Ellipse ECO
   0.544675	- Serial Number: 000000000
   0.544719	- Bus: 003
   0.544783	Trying to match device
   0.544927	Device matches
   0.617937	HID descriptor length 909
   3.849957	Report Descriptor size = 909
   3.851661	Using subdriver: MGE HID 1.31
   3.896977	Path: UPS.BatterySystem.Battery.AudibleAlarmControl, Type: Feature, ReportID: 0x20, Offset: 0, Size: 8, Value: 2
   3.951969	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
   3.952513	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Input, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
   3.952939	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
   3.953381	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Input, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
   4.002973	Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 16, Value: 1600
   4.003390	Path: UPS.Flow.[4].ConfigFrequency, Type: Feature, ReportID: 0x0d, Offset: 16, Size: 8, Value: 50
   4.048948	Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 230
   4.128988	Path: UPS.Flow.[4].FlowID, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 4
   4.204962	Path: UPS.HistorySystem.Event.[1].Code, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0
   4.258950	Path: UPS.HistorySystem.Event.[1].EventID, Type: Feature, ReportID: 0x17, Offset: 0, Size: 8, Value: 1
   4.259415	Path: UPS.HistorySystem.Event.[2].Code, Type: Feature, ReportID: 0x18, Offset: 16, Size: 16, Value: 0
   4.259601	Path: UPS.HistorySystem.Event.[2].EventID, Type: Feature, ReportID: 0x17, Offset: 8, Size: 8, Value: 2
   4.259799	Path: UPS.HistorySystem.Event.[3].Code, Type: Feature, ReportID: 0x18, Offset: 32, Size: 16, Value: 0
   4.259987	Path: UPS.HistorySystem.Event.[3].EventID, Type: Feature, ReportID: 0x17, Offset: 16, Size: 8, Value: 3
   4.260183	Path: UPS.HistorySystem.Event.[4].Code, Type: Feature, ReportID: 0x18, Offset: 48, Size: 16, Value: 0
   4.260352	Path: UPS.HistorySystem.Event.[4].EventID, Type: Feature, ReportID: 0x17, Offset: 24, Size: 8, Value: 4
   4.260566	Path: UPS.HistorySystem.Event.[5].Code, Type: Feature, ReportID: 0x18, Offset: 64, Size: 16, Value: 0
   4.260840	Path: UPS.HistorySystem.Event.[5].EventID, Type: Feature, ReportID: 0x17, Offset: 32, Size: 8, Value: 5
   4.305961	Path: UPS.OutletSystem.Outlet.[1].ConfigApparentPower, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 25
   4.306185	Path: UPS.OutletSystem.Outlet.[1].FlowID, Type: Feature, ReportID: 0x0b, Offset: 8, Size: 8, Value: 4
   4.306283	Path: UPS.OutletSystem.Outlet.[1].OutletID, Type: Feature, ReportID: 0x0b, Offset: 16, Size: 8, Value: 1
   4.360964	Path: UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 0
   4.408949	Path: UPS.OutletSystem.Outlet.[2].ECOControl, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 1
   4.409151	Path: UPS.OutletSystem.Outlet.[2].FlowID, Type: Feature, ReportID: 0x0b, Offset: 24, Size: 8, Value: 1
   4.409359	Path: UPS.OutletSystem.Outlet.[2].OutletID, Type: Feature, ReportID: 0x0b, Offset: 32, Size: 8, Value: 2
   4.460957	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Present, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 1
   4.461151	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Present, Type: Input, ReportID: 0x02, Offset: 0, Size: 8, Value: 1
   4.505955	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature, ReportID: 0x19, Offset: 0, Size: 8, Value: 0
   4.506060	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 1
   4.506266	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Input, ReportID: 0x02, Offset: 8, Size: 8, Value: 1
   4.506464	Path: UPS.OutletSystem.Outlet.[3].ECOControl, Type: Feature, ReportID: 0x0f, Offset: 8, Size: 8, Value: 0
   4.506666	Path: UPS.OutletSystem.Outlet.[3].FlowID, Type: Feature, ReportID: 0x0b, Offset: 40, Size: 8, Value: 1
   4.506868	Path: UPS.OutletSystem.Outlet.[3].OutletID, Type: Feature, ReportID: 0x0b, Offset: 48, Size: 8, Value: 3
   4.507103	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Present, Type: Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 1
   4.507281	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Present, Type: Input, ReportID: 0x02, Offset: 16, Size: 8, Value: 1
   4.551959	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 0
   4.552166	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x02, Offset: 24, Size: 8, Value: 1
   4.552376	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Input, ReportID: 0x02, Offset: 24, Size: 8, Value: 1
   4.552664	Path: UPS.OutletSystem.OutletSystemID, Type: Feature, ReportID: 0x0b, Offset: 56, Size: 8, Value: 1
   4.552847	Path: UPS.PowerConverter.Inverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x03, Offset: 16, Size: 8, Value: 0
   4.553038	Path: UPS.PowerConverter.Inverter.PresentStatus.InternalFailure, Type: Input, ReportID: 0x03, Offset: 16, Size: 8, Value: 0
   4.599949	Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x13, Offset: 0, Size: 16, Value: 264
   4.644947	Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 184
   4.645147	Path: UPS.PowerConverter.Output.OutputID, Type: Feature, ReportID: 0x0b, Offset: 64, Size: 8, Value: 1
   4.645315	Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Feature, ReportID: 0x03, Offset: 24, Size: 8, Value: 0
   4.645525	Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Input, ReportID: 0x03, Offset: 24, Size: 8, Value: 0
   4.689946	Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 230
   4.690142	Path: UPS.PowerConverter.PowerConverterID, Type: Feature, ReportID: 0x0b, Offset: 72, Size: 8, Value: 1
   4.690380	Path: UPS.PowerConverter.Rectifier.PresentStatus.DCBusUnbalanced, Type: Feature, ReportID: 0x03, Offset: 32, Size: 8, Value: 0
   4.690555	Path: UPS.PowerConverter.Rectifier.PresentStatus.DCBusUnbalanced, Type: Input, ReportID: 0x03, Offset: 32, Size: 8, Value: 0
   4.734944	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   4.735037	Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x0c, Offset: 8, Size: 8, Value: 1
   4.735220	Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x0c, Offset: 16, Size: 8, Value: 2
   4.779957	Path: UPS.PowerSummary.Country, Type: Feature, ReportID: 0x15, Offset: 0, Size: 8, Value: 0
   4.831960	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: -1
   4.883949	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: -1
   4.884049	Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x0c, Offset: 24, Size: 8, Value: 100
   4.884246	Path: UPS.PowerSummary.FlowID, Type: Feature, ReportID: 0x0b, Offset: 80, Size: 8, Value: 4
   4.884438	Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x0c, Offset: 32, Size: 8, Value: 100
   4.939947	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 5
   4.940147	Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x10, Offset: 8, Size: 8, Value: 1
   4.940240	Path: UPS.PowerSummary.iModel, Type: Feature, ReportID: 0x10, Offset: 16, Size: 8, Value: 3
   4.940440	Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x10, Offset: 24, Size: 8, Value: 2
   4.940627	Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x10, Offset: 32, Size: 8, Value: 4
   4.940728	Path: UPS.PowerSummary.iVersion, Type: Feature, ReportID: 0x10, Offset: 40, Size: 8, Value: 6
   4.985946	Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 0
   4.986141	Path: UPS.PowerSummary.PowerSummaryID, Type: Feature, ReportID: 0x0b, Offset: 88, Size: 8, Value: 1
   5.035951	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 1, Value: 1
   5.036159	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x01, Offset: 0, Size: 1, Value: 1
   5.036236	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 1, Size: 1, Value: 0
   5.036438	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x01, Offset: 1, Size: 1, Value: 0
   5.036537	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 2, Size: 1, Value: 1
   5.036814	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x01, Offset: 2, Size: 1, Value: 1
   5.037026	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x01, Offset: 3, Size: 1, Value: 0
   5.037290	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x01, Offset: 3, Size: 1, Value: 0
   5.037479	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 4, Size: 1, Value: 0
   5.037663	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x01, Offset: 4, Size: 1, Value: 0
   5.037856	Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x01, Offset: 5, Size: 1, Value: 1
   5.038055	Path: UPS.PowerSummary.PresentStatus.Good, Type: Input, ReportID: 0x01, Offset: 5, Size: 1, Value: 1
   5.038322	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x01, Offset: 6, Size: 1, Value: 0
   5.038424	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x01, Offset: 6, Size: 1, Value: 0
   5.038610	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x01, Offset: 7, Size: 1, Value: 0
   5.038880	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x01, Offset: 7, Size: 1, Value: 0
   5.039149	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
   5.039251	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
   5.039435	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 0
   5.039698	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x01, Offset: 16, Size: 8, Value: 0
   5.094983	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
   5.095243	Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
   5.139953	Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 20
   5.184944	Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 20
   5.185043	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x06, Offset: 8, Size: 32, Value: 3000
   5.185236	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x06, Offset: 8, Size: 32, Value: 3000
   5.307900	get_model_name(Ellipse ECO, 1600)

   5.308205	comparing with: ellipse 300
   5.308328	comparing with: ellipse 500
   5.308524	comparing with: ellipse 650
   5.308573	comparing with: ellipse 800
   5.308617	comparing with: ellipse 1200
   5.308766	comparing with: ellipse premium 500
   5.308814	comparing with: ellipse premium 650
   5.308955	comparing with: ellipse premium 800
   5.309009	comparing with: ellipse premium 1200
   5.309053	comparing with: Ellipse 600
   5.309120	comparing with: Ellipse 750
   5.309252	comparing with: Ellipse 1000
   5.309398	comparing with: Ellipse 1500
   5.309458	comparing with: (null)
   5.309607	comparing with: (null)
   5.309674	comparing with: (null)
   5.309801	comparing with: (null)
   5.309881	comparing with: Protection Center 420
   5.310011	comparing with: Protection Center 500
   5.310082	comparing with: Protection Center 675
   5.310209	comparing with: (null)
   5.310381	comparing with: (null)
   5.310428	comparing with: (null)
   5.310472	comparing with: (null)
   5.310618	comparing with: (null)
   5.310665	comparing with: (null)
   5.310811	comparing with: (null)
   5.311075	Report descriptor retrieved (Reportlen = 909)
   5.311313	Found HID device
   5.311385	Detected a UPS: EATON/Ellipse ECO 1600
   5.311658	Path: UPS.PowerSummary.Country, Type: Feature, ReportID: 0x15, Offset: 0, Size: 8, Value: 0
   5.312113	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
   5.312427	Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 20
   5.312922	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x06, Offset: 8, Size: 32, Value: 3000
   5.313737	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 5
   5.437383	Path: UPS.PowerSummary.iVersion, Type: Feature, ReportID: 0x10, Offset: 40, Size: 8, Value: 6
   5.542993	Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 0
   5.543804	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: -1
   5.544318	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: -1
   5.544963	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   5.593939	Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 16, Value: 1600
   5.595256	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 1, Value: 1
   5.595973	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 4, Size: 1, Value: 0
   5.596473	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 2, Size: 1, Value: 1
   5.597000	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 1, Size: 1, Value: 0
   5.597727	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
   5.598216	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x01, Offset: 7, Size: 1, Value: 0
   5.599165	Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x01, Offset: 5, Size: 1, Value: 1
   5.654954	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
   5.655759	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
   5.656349	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x01, Offset: 6, Size: 1, Value: 0
   5.656931	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 0
   5.657735	Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Feature, ReportID: 0x03, Offset: 24, Size: 8, Value: 0
   5.659675	Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 184
   5.660353	Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x13, Offset: 0, Size: 16, Value: 264
   5.662563	Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 230
   5.707937	Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 230
   5.709051	Path: UPS.Flow.[4].ConfigFrequency, Type: Feature, ReportID: 0x0d, Offset: 16, Size: 8, Value: 50
   5.789942	Path: UPS.OutletSystem.Outlet.[1].OutletID, Type: Feature, ReportID: 0x0b, Offset: 16, Size: 8, Value: 1
   5.790683	Path: UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 0
   5.791213	Path: UPS.OutletSystem.Outlet.[1].ConfigApparentPower, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 25
   5.792133	Path: UPS.OutletSystem.Outlet.[2].OutletID, Type: Feature, ReportID: 0x0b, Offset: 32, Size: 8, Value: 2
   5.792768	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature, ReportID: 0x19, Offset: 0, Size: 8, Value: 0
   5.793306	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 1
   5.794512	Path: UPS.OutletSystem.Outlet.[3].OutletID, Type: Feature, ReportID: 0x0b, Offset: 48, Size: 8, Value: 3
   5.795141	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 0
   5.795784	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x02, Offset: 24, Size: 8, Value: 1
   5.797041	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: -1
   5.797502	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: -1
   5.797994	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: -1
   5.798510	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   5.798975	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   5.799437	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   5.799898	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   5.800383	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 2
   5.801242	upsdrv_initinfo...
   5.801644	upsdrv_updateinfo...
   6.053933	libusb_get_interrupt: Connection timed out
   6.054374	Got 0 HID objects...
   6.054808	Quick update...
   6.055247	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: -1
   6.055677	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: -1
   6.056102	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 1, Value: 1
   6.056520	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 4, Size: 1, Value: 0
   6.056968	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 2, Size: 1, Value: 1
   6.057387	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 1, Size: 1, Value: 0
   6.057993	dstate_init: sock /var/state/ups/usbhid-ups-eaton open on fd 7
   6.058461	upsdrv_updateinfo...
   6.310943	libusb_get_interrupt: Connection timed out
   6.311443	Got 0 HID objects...
   6.311827	Quick update...
   6.363944	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: -1
   6.415936	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: -1
   6.465929	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 1, Value: 1
   6.466287	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 4, Size: 1, Value: 0
   6.466457	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 2, Size: 1, Value: 1
   6.466626	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 1, Size: 1, Value: 0
   8.060118	upsdrv_updateinfo...
   8.311936	libusb_get_interrupt: Connection timed out
   8.312133	Got 0 HID objects...


It seems like the ups is detected, but not receiving any hid objects.


I have no idea of how to debug this problem

Does anyone have any ideas about whats wrong?