[Nut-upsuser] battery.charge and other fixes needed for X-Power Tigra 1kVA
Tmima Pliroforikis Perifereiakis Enotitas Pierias
pliroforiki at pieria.pkm.gov.gr
Thu May 10 07:11:55 UTC 2012
Hello all,
been 5 years since I posted on this list, glad to be back :)
I have a number of X-power Tigra 1kVA online UPS units. From some
knowledgeable folks working for the local distributor, I learnt that
from inside this looked like a Best 610 ups unit.
Before, I had this UPS hooked via serial to my Windows 2003 server. For
monitoring, some winpilot/upspilot software was also provided. This
software produced also a csv format log (upsdata.csv) that contained the
following lines:
05/10/2012,07:36:56,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,035,029
05/10/2012,07:37:56,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,036,029
05/10/2012,07:38:56,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,036,029
05/10/2012,07:39:56,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,036,029
05/10/2012,07:40:56,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,035,029
05/10/2012,07:41:57,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,036,030
05/10/2012,07:42:57,COM1,ON-LINE,1,224,999,999,231,999,999,041.1,50.0,036,030
05/10/2012,07:43:57,COM1,ON-LINE,1,225,999,999,229,999,999,041.1,50.0,036,030
05/10/2012,07:44:57,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,036,030
05/10/2012,07:45:57,COM1,ON-LINE,1,225,999,999,231,999,999,041.1,50.0,035,030
So I disabled this bundled software and installed the windows version
NUT-Installer-2.6.3-3.msi, without the libusb option (since I had a
serial UPS)
In ups.conf I used the following
[ups1]
driver = bestups
port = com1
id = 610,1000,230,230,10.0,36.0
nombattvolt=41.1
battvoltmult = 18
With regard to the id option, the 2nd, 3rd and 4th options seemed ok.
Not sure about the fifth (10.0). And definitely not sure about the last
(36.0). I used 36.0 because the Best 610-1000 lists 36V as the DC bus
voltage. Not sure if that is correct or not. According to specs (
http://www.lexis.gr/upload/File/ProductBrochures/XPower/Tigrablack.pdf )
this Xpower ups has three (3) 12V batteries.
I used nombattvolt 41.1 since that seemed to be similar also to the Best
610-1000. As for battvoltmult, I must say I also experimented here.
The bestups driver seems to run ok:
C:\PROGRA~1\NUT\bin>bestups.exe -DDDDDDD -a ups1
Network UPS Tools - Best UPS driver 1.06 (2.6.3-3534:3545M)
0.000000 send_to_all: SETINFO driver.parameter.port "com1"
0.000000 send_to_all: SETINFO driver.parameter.id
"610,1000,230,230,10.0,36.0"
0.000000 send_to_all: SETINFO driver.parameter.nombattvolt "41.1"
0.015625 send_to_all: SETINFO driver.parameter.battvoltmult "18"
0.015625 debug level is '7'
0.015625 w32_serial_open (com1)
0.015625 setting initial state on com1
0.015625 000007AC = w32_serial_open (com1)
0.015625 Warning: no locking method is available: No error [The
operation completed successfully. ]
0.015625 vmin_ 0, vtime_ 0
0.109376 action 0
0.109376 vtime 0, vmin 1
0.125002 ReadTotalTimeoutConstant -2, ReadIntervalTimeout -1,
ReadTotalTi
meoutMultiplier -1
0.125002 send_to_all: SETINFO device.type "ups"
0.125002 send_to_all: SETINFO driver.version "2.6.3-3534:3545M"
0.125002 send_to_all: SETINFO driver.version.internal "1.06"
0.125002 send_to_all: SETINFO driver.name "bestups"
0.328129 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
0.328129 w32_serial_read : Reading 8 characters
0.328129 w32_serial_read : total characters read = 8
0.328129 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
0.343754 w32_serial_read : characters are available on input buffer
0.343754 w32_serial_read : Reading 1 characters
0.359380 w32_serial_read : total characters read = 1
0.359380 w32_serial_read : Reading 7 characters
0.359380 w32_serial_read : total characters read = 8
0.359380 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
0.359380 w32_serial_read : characters are available on input buffer
0.359380 w32_serial_read : Reading 1 characters
0.390630 w32_serial_read : total characters read = 1
0.390630 w32_serial_read : Reading 7 characters
0.390630 w32_serial_read : total characters read = 8
0.390630 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
0.390630 w32_serial_read : characters are available on input buffer
0.390630 w32_serial_read : Reading 1 characters
0.421880 w32_serial_read : total characters read = 1
0.421880 w32_serial_read : Reading 7 characters
0.421880 w32_serial_read : total characters read = 8
0.421880 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
0.421880 w32_serial_read : characters are available on input buffer
0.421880 w32_serial_read : Reading 1 characters
0.453131 w32_serial_read : total characters read = 1
0.453131 w32_serial_read : Reading 7 characters
0.453131 w32_serial_read : total characters read = 8
0.453131 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
0.453131 w32_serial_read : characters are available on input buffer
0.468756 w32_serial_read : Reading 1 characters
0.500006 w32_serial_read : total characters read = 1
0.500006 w32_serial_read : Reading 6 characters
0.500006 w32_serial_read : total characters read = 7
0.500006 NOTE: using user-supplied ID response
0.500006 send_to_all: SETINFO input.voltage.nominal "230"
0.500006 send_to_all: SETINFO output.voltage.nominal "230"
0.515632 send_to_all: SETINFO ups.mfr "Best Power"
0.515632 send_to_all: SETINFO ups.model "610 1000"
0.515632 send_to_all: SETINFO battery.voltage.nominal "216"
Detected Best Power 610 1000 on com1
0.609383 send_to_all: ADDCMD test.battery.start
0.625008 send_to_all: ADDCMD test.battery.stop
1.015638 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
1.031263 w32_serial_read : Reading 51 characters
1.031263 w32_serial_read : total characters read = 51
1.031263 Communications with UPS lost: Poll failed: short read
(got 3 bytes)
1.031263 dstate_init: sock \\.\pipe\bestups-ups1 open on fd 1956
1.031263 send_to_all: SETINFO driver.parameter.pollinterval "2"
1.031263 send_to_all: SETINFO device.mfr "Best Power"
1.031263 send_to_all: SETINFO device.model "610 1000"
1.437518 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
1.437518 w32_serial_read : Reading 47 characters
1.437518 w32_serial_read : total characters read = 47
1.437518 Communications with UPS re-established
1.453144 send_to_all: SETINFO battery.voltage "41.0"
1.453144 send_to_all: SETINFO input.voltage "226.5"
1.453144 send_to_all: SETINFO output.voltage "230.7"
1.453144 send_to_all: SETINFO ups.load "035"
1.453144 send_to_all: SETINFO input.frequency "50.0"
1.453144 send_to_all: SETINFO ups.temperature "34.0"
1.453144 send_to_all: SETINFO battery.charge "-24.8"
1.453144 send_to_all: SETINFO ups.status "OL"
1.453144 send_to_all: DATAOK
3.437544 w32_serial_read : ulen 64, vmin_ 1, vtime_ 0, hEvent
000007A8
3.437544 w32_serial_read : Reading 47 characters
3.437544 w32_serial_read : total characters read = 47
My questions are:
1) Any ideas on why battery.charge is set to -24.8 (note also the
negative sign)
2) Anything else that should be corrected in ups.conf, in your opinion?
3) Regardless if the battery.charge is correct, will the system shutdown
when battery charge is low?
4) In my FreeBSD installations, ups.log is written as a log, anything
similar for Windows?
I understand that this is a large number of questions, please accept my
apologies in advance.
With kind regards,
Michail.-