[Nut-upsuser] battery.charge and other fixes needed for X-Power Tigra 1kVA
Frédéric Bohé
fredericbohe at eaton.com
Mon May 14 12:16:22 UTC 2012
On Mon, 2012-05-14 at 13:20 +0300, Tmima Pliroforikis Perifereiakis
Enotitas Pierias wrote:
> Hello Frederic,
>
> Frédéric Bohé wrote:
> > [snip]
> >> And some more questions:
> >>
> >> 1) Upon reception of a shutdown command, my server takes approx. 60" for
> >> shutdown. Can I set on this Windows server the ups itself to power down
> >> after say 90"? According to the upsc output above, the ups has set
> >> ups.delay.shutdown to 30". By adding offdelay = 120 (from the docs it
> >> seems that offdelay values> 60" are rounded to multiples of 60") in
> >> ups.conf or by other means will NUT as part of the shutdown procedure
> >> call automatically:
> >> upscmd<upsname> shutdown.return 1
> >> for it to work? Or should I insert this command somewhere to make sure
> >> that the offdelay value will be respected?
> >
> >> From the blazer man page I see :
> >
> > offdelay = value
> > Time to wait before shutting down the UPS (seconds). This
> > value
> > is truncated to units of 6 seconds (less than 60 seconds) or
> > 60
> > seconds (more than 60 seconds). Defaults to 30 seconds.
> >
> >
> > So you can try to add this to your ups.conf and see if it works.
>
> If the a battery low is received, the system which is connected to the
> UPS initiates a shutdown successfully. However, the UPS does not power
> off as configured with offdelay and it does not power up as configured
> with ondelay. So it seems that a "upscmd <upsname> shutdown.return 1"
> should definitely be used.
Well, the blazer_ser driver should issue this command.
Can you call the following command after stopping NUT (there should be
no other driver running). Beware that this will likely shutdown your UPS
so make sure your PC is not electrically connected to it.
blazer_ser -a <ups_name> -DDDDD -k
Then you can send the output to the list.
Regards,
Fred
>
> Taking into account your response about having SHUTDOWNCMD point to a
> .bat file, I was considering modifying SHUTDOWNCMD to point to
> myown.bat, suitibly modified to include a call to shutdown.return, as
> follows:
> SHUTDOWNCMD "C:\\myown.bat"
>
> ...where myown.bat would contain the following:
> myown.bat:
> ========================================
> REM First start shutdown timers for UPS
> <pathToUpscmc>\upscmd <upsname> shutdown.return 1
>
> REM Needed sending a command to power
> REM down my ESXi server elsewhere (different UPS)
> SSH cmd here blah blah
>
> REM Finally initiate local system shutdown
> C:\WINDOWS\system32\shutdown.exe -s -t 0
> ========================================
>
> What do you think? Any caveats I should possibly watch out?
> BR,
>
>
> Michail.-
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at lists.alioth.debian.org
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
--
Eaton Opensource Team - http://opensource.eaton.com
--------------------------------------------------------------------------