On May 15, 2012, at 11:34 AM, twhitney at clearbearing.com wrote:
> ups.status: OL
This is the only line that upsmon looks at. The UPS makes the call as to when the battery is low, and hopefully it has an internal runtime estimate. Often, though, that estimate is often not exposed over the protocol on less expensive models.
As Kris mentioned, you can instead trigger a shutdown after a certain number of minutes on battery, but that has its own issues.
--
Charles Lepple