[Nut-upsuser] NUT for Windows + Eaton/PW 5110
    Frédéric Bohé 
    fredericbohe at eaton.com
       
    Mon May 28 09:43:45 UTC 2012
    
    
  
On Sat, 2012-05-26 at 12:27 -0700, Kris Jordan wrote:
> Kris Jordan wrote, On 5/14/2012 11:14 AM:
> > Frédéric Bohé wrote, On 5/14/2012 2:31 AM:
> >> Hello Kris,
> >>
> >> On Sat, 2012-05-12 at 16:00 -0700, Kris Jordan wrote:
> >>> Nut for Windows 2.6.3-3 + Eaton/PW 5110 (103004256-5591).
> >>>
> >>> I had to manually install libusb driver and I'm using bcmxcp_usb.
> >>
> >> Why did you install libusb manually ? Did the installer fail ?
> >
> > It says no known UPS device found, try installing manually.
> >
> > I forgot to mention a few specifics:
> > Windows 7 x64 SP1 (up2date)
> > 500VA (120V/US version of the UPS)
> > F/W: 1.5, USB: 0.5.
> >
> >> Can you send your configuration files please (nut.conf, upsd.conf,
> >> ups.conf. upsmon.conf and upssched.conf if you use upssched ).
> >
> > I made minimal changes to begin with, no changes to upssched.conf or 
> > upsd.conf.
> >
> >> FYI this is the output of upsc for my 5110. I'm afraid it won't satisfy
> >> your needs. Anyway, please send your configuration file since you may
> >> have discovered a bug. :
> >>
> > <SNIP>
> >> ups.beeper.status: enabled
> >> ups.load: 0.0
> > > ups.status: OL
> >
> > I was able to disable the beeper using lansafe (with 
> > permanently-disabled checked), but as soon as I turned the unit off, 
> > it lost the setting. So I'd have to use lansafe to maintain that setting.
> >
> > No load?
> >
> > No where did I see an "online" status in IPP or lansafe, just 
> > "charging" which to me sounds like a problem, unless they consider it 
> > float charging. I'd be interested what my 5110 says in NUT.
> 
> I created a log for the driver. 15seconds in I started upsd, 25 seconds 
> in I started upsmon where it crashes upsd.
> 
> If I start 'upsc eaton' a couple seconds *before* upsd, it will get the 
> values before it crashes upsd.
You mean before upsmon, not upsd ? Or is there another instance of upsd
running ?
> 
> I threw a bunch of D's on upsd,
Good ! Can you send the whole log of upsd -DDDDD (5 Ds) and upsmon
-DDDDD (5 Ds too) please.
Regards,
Fred
> mainloop: no data available
> mainloop: wait for 4 filedescriptors
> Out of memory
> ambient.temperature.high: 1
> battery.charge.low: 11
> battery.voltage: 13.7
> device.mfr: Eaton
> device.model: POWERWARE UPS \\ 500i
> device.serial: *çu☺
> device.type: ups
> driver.name: bcmxcp_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.shutdown_delay: 60
> driver.version: 2.6.3-3534:3545M
> driver.version.internal: 0.26
> input.frequency: 59.8
> input.frequency.high: 65
> input.frequency.low: 55
> input.frequency.nominal: 60
> input.transfer.boost.high: 108
> input.transfer.high: 150
> input.transfer.low: 93
> input.transfer.trim.low: 130
> input.voltage: 116
> input.voltage.nominal: 120
> output.current: 0.8
> output.current.nominal: 2.5
> output.frequency: 59.8
> output.phases: 1
> output.voltage: 116
> output.voltage.nominal: 120
> ups.beeper.status: enabled
> ups.firmware: Cont:00.50 Inve:01.50
> ups.load: 32.0
> ups.mfr: Eaton
> ups.model: POWERWARE UPS \ 500i
> ups.power.nominal: 500
> ups.serial: *çu☺
> ups.status: OL
> ups.test.result: Done and passed
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at lists.alioth.debian.org
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
-- 
Eaton Opensource Team - http://opensource.eaton.com
--------------------------------------------------------------------------
    
    
More information about the Nut-upsuser
mailing list