[Nut-upsuser] SNMP UPS: NETYS RT 1/1 UPS

Ing. Ján ONDREJ jan.ondrej at upjs.sk
Sat Oct 13 07:24:50 UTC 2012


Hello,

  I have an NETYS RT 1/1 UPS, which is not fully supported. Starting snmp
driver displays:

[root at kvm1 ~]# snmp-ups -a local
Network UPS Tools - Generic SNMP UPS driver 0.66 (2.6.4)
Duplicate driver instance detected! Terminating other driver!
No matching MIB found for sysOID '.1.3.6.1.4.1.2254.2.4'!
Please report it to NUT developers, with an 'upsc' output for your device.
Going back to the classic MIB detection method.
Detected NETYS RT 1/1 UPS on host 192.168.14.10 (mib: ietf 1.4)
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.2.3.0
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.2.6.0
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.3.3.1.4.1
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.3.3.1.5.1
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.4.4.1.4.1
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.5.3.1.3.1
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.5.3.1.4.1
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.5.3.1.5.1
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.6.3.8
[local] unhandled ASN 0x6 received from 1.3.6.1.2.1.33.1.7.1.0
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.9.6.0
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.9.7.0
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.9.9.0
[local] unhandled ASN 0x5 received from 1.3.6.1.2.1.33.1.9.10.0

Here is output of upsc command:

[root at kvm1 ~]# /etc/init.d/ups start
Spustenie ovládača radiča UPS:                             [  OK   ]
Spustenie upsd:                                            [  OK   ]
Spustenie sledovania UPS (server):                         [  OK   ]
[root at kvm1 ~]# upsc local
battery.charge: 0.00
battery.temperature: 33.00
battery.voltage: 55.00
device.mfr: Delta
device.model: NETYS RT 1/1 UPS
device.type: ups
driver.name: snmp-ups
driver.parameter.pollinterval: 2
driver.parameter.port: 192.168.14.10
driver.version: 2.6.4
driver.version.internal: 0.66 (mib: ietf 1.4)
input.bypass.frequency: 49.90
input.bypass.phases: 1.00
input.frequency: 49.90
input.frequency.nominal: 5.00
input.phases: 1.00
input.voltage: 2320.00
input.voltage.nominal: 230.00
output.current: 2.30
output.frequency: 49.90
output.frequency.nominal: 5.00
output.phases: 1.00
output.power.nominal: 2200.00
output.voltage: 2290.00
output.voltage.nominal: 230.00
ups.beeper.status: enabled
ups.firmware: 1.1
ups.firmware.aux: 2.0h
ups.load: 300.00
ups.mfr: Delta
ups.model: NETYS RT 1/1 UPS
ups.status: OL
ups.test.result: done and passed
ups.timer.reboot: 0
ups.timer.shutdown: 0
ups.timer.start: 0

What else is required for support of this UPS in NUT.

					SAL



More information about the Nut-upsuser mailing list