[Nut-upsuser] blazer driver: Possible bugs with battery packs
Michail Pappas
m.pappas at pieria.pkm.gov.gr
Tue Apr 2 09:33:48 UTC 2013
Hello all,
long time away from this list, glad to be around again!
I have this Powercom Vanguard VGN VGD-20K31. Some details of this model:
* 3-phase input, single phase output
* Model has 240V / 12V9AH x 20 x 2SET, plus another set of 20 batteries.
All in all, 3 sets
* Serial connection to Windows 2k3 server with UPSMon
Now I was strongly considering replacing the bundled no-good upsmoon
crap, with NUT, in order to enable shutdown of other systems powered the
same ups, using a NUT master-slave installation.
So, I installed NUT on a XP system (for test) and connected this UPS
serially. NUT version is the latest for Windows, Beta 2.6.5-4 for Windows.
ups.conf:
[ups1]
driver = blazer_ser
port = com1
offdelay = 240
I can see that the blazer_ser driver is at version 1.55.
So here is where the problems begin, due to the fact that the device
does not provide a battery.charge indication. Specifically, without
providing a runtime cal, I get the following data:
battery.charge: 60
battery.voltage: 270.00
battery.voltage.high: 293.69
battery.voltage.low: 234.95
battery.voltage.nominal: 271.1
device.mfr: UPS
device.model: Model 20K
device.type: ups
driver.name: blazer_ser
driver.parameter.pollinterval: 2
driver.parameter.port: com1
driver.version: 2.6.5-3780M
driver.version.internal: 1.55
input.current.nominal: 86.0
input.frequency: 49.9
input.frequency.nominal: 50
input.voltage: 226.0
input.voltage.fault: 0.0
input.voltage.nominal: 230
output.voltage: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 180
ups.firmware: Ver ST1.0
ups.load: 26
ups.mfr: UPS
ups.model: Model 20K
ups.status: OL
ups.temperature: 11.0
ups.type: online
Notice the battery.charge estimation, which is clearly incorrect!
According to the UPS specs, if no extra cabin is installed runtime is
"...About 6 min Full loal / 15min Half load". This is for 2 packs.
Taking into account the 3rd pack which is connected, I increased these
values by 50%. So I inserted a "runtime = 540,100,1350,50". However,
doing so produced problematic figures:
battery.charge: 0
battery.runtime: 1
[...]
driver.parameter.runtimecal: 540,100,1350,50
I have tried fiddling with all information, lowering runtime cal to the
stock values (for 2 strings instead of 3). Nothing...
Then I examined the source code of blazer_ser.c. There might be a
problem there, although not sure.
By that time I had 2 issues:
1) When runtimecal is not specified, I have a battery.charge value of 60
instead of 80
2) With runtimecal specified, battery.charge drops to zero.
I have not investigated (2), but I did do some digging regarding one above.
When running with -DDDDD, I get the following:
Network UPS Tools - Megatec/Q1 protocol serial driver 1.55 (2.6.5-3780M)
0.000000 debug level is '5'
0.000000 w32_serial_open (com1)
0.000000 setting initial state on com1
0.000000 000007D0 = w32_serial_open (com1)
0.000000 Warning: no locking method is available: No error [?
ΈίώΪΎΫ±ή-ά
ΎΈΎΆΈύ±¦ϋύΆί Ήί ίΏώΪΫ?-ά. ]
0.000000 vmin_ 0, vtime_ 0
0.109369 action 0
0.109369 vtime 0, vmin 1
0.109369 ReadTotalTimeoutConstant -2, ReadIntervalTimeout -1,
ReadTotalTi
meoutMultiplier -1
0.109369 vmin_ 1, vtime_ 0
0.109369 action 0
0.109369 vtime 0, vmin -1
0.109369 ReadTotalTimeoutConstant -2, ReadIntervalTimeout -1,
ReadTotalTi
meoutMultiplier -1
0.218737 send_to_all: SETINFO device.type "ups"
0.218737 send_to_all: SETINFO driver.version "2.6.5-3780M"
0.218737 send_to_all: SETINFO driver.version.internal "1.55"
0.218737 send_to_all: SETINFO driver.name "blazer_ser"
0.218737 Trying megatec protocol...
0.328106 send: 'Q1'
0.328106 w32_serial_read : ulen 512, vmin_ -1, vtime_ 0, hEvent
000007CC
0.374978 w32_serial_read : characters are available on input buffer
0.374978 w32_serial_read : Reading 1 characters
[...]
0.546844 w32_serial_read : Reading 1 characters
1.546786 w32_serial_read : total characters read = 47
1.546786 read: '(229.5 000.0 230.0 023 49.9 2.25 07.0 00000000'
1.546786 send_to_all: SETINFO input.voltage "229.5"
1.546786 send_to_all: SETINFO input.voltage.fault "0.0"
1.546786 send_to_all: SETINFO output.voltage "230.0"
1.546786 send_to_all: SETINFO ups.load "23"
1.546786 send_to_all: SETINFO input.frequency "49.9"
1.546786 send_to_all: SETINFO battery.voltage "2.25"
1.546786 send_to_all: SETINFO ups.temperature "7.0"
1.546786 send_to_all: SETINFO ups.beeper.status "disabled"
1.546786 send_to_all: SETINFO ups.type "online"
1.546786 send_to_all: SETINFO ups.status "OL"
1.562410 Status read in 1 tries
1.562410 Supported UPS detected with megatec protocol
1.671779 send: 'F'
1.671779 w32_serial_read : ulen 512, vmin_ -1, vtime_ 0, hEvent
000007CC
1.703027 w32_serial_read : characters are available on input buffer
[...]
2.781090 w32_serial_read : total characters read = 22
2.781090 read: '#230.0 086 271.1 50.0'
2.781090 send_to_all: SETINFO input.voltage.nominal "230"
2.781090 send_to_all: SETINFO input.current.nominal "86.0"
2.781090 send_to_all: SETINFO battery.voltage.nominal "271.1"
2.781090 send_to_all: SETINFO input.frequency.nominal "50"
2.781090 Ratings read in 1 tries
2.890459 send: 'I'
2.890459 w32_serial_read : ulen 512, vmin_ -1, vtime_ 0, hEvent
000007CC
2.921707 w32_serial_read : characters are available on input buffer
[...]
3.077948 w32_serial_read : Reading 1 characters
4.077890 w32_serial_read : total characters read = 39
4.077890 read: '#UPS Model 20K Ver ST1.0'
4.077890 send_to_all: SETINFO ups.mfr "UPS"
4.077890 send_to_all: SETINFO ups.model "Model 20K"
4.077890 send_to_all: SETINFO ups.firmware "Ver ST1.0"
4.077890 Vendor information read in 1 tries
4.077890 No values provided for battery high/low voltages in
ups.conf
4.077890 send_to_all: SETINFO battery.voltage.low "234.95"
4.077890 send_to_all: SETINFO battery.voltage.high "293.69"
4.077890 Using 'guestimation' (low: 234.953333, high: 293.691667)!
4.077890 battery runtime exponent : 1.322
4.077890 battery runtime nominal : 540.0
4.077890 send_to_all: SETINFO battery.charge "0"
4.093514 battery runtime estimate : 0.0
4.093514 No charge time specified, using built in default [43200
seconds]
4.093514 No idle load specified, using built in default [10.0 %]
4.093514 send_to_all: SETINFO ups.delay.start "180"
4.093514 send_to_all: SETINFO ups.delay.shutdown "240"
4.093514 send_to_all: ADDCMD beeper.toggle
4.093514 send_to_all: ADDCMD load.off
4.093514 send_to_all: ADDCMD load.on
4.093514 send_to_all: ADDCMD shutdown.return
4.093514 send_to_all: ADDCMD shutdown.stayoff
4.093514 send_to_all: ADDCMD shutdown.stop
4.093514 send_to_all: ADDCMD test.battery.start
4.093514 send_to_all: ADDCMD test.battery.start.deep
4.109138 send_to_all: ADDCMD test.battery.start.quick
4.109138 send_to_all: ADDCMD test.battery.stop
4.218507 send: 'Q1'
4.218507 w32_serial_read : ulen 512, vmin_ -1, vtime_ 0, hEvent
000007CC
4.265379 w32_serial_read : characters are available on input buffer
[...]
5.437187 w32_serial_read : total characters read = 47
5.437187 read: '(229.5 000.0 231.0 024 49.9 2.25 07.0 00000000'
5.437187 send_to_all: SETINFO output.voltage "231.0"
5.437187 send_to_all: SETINFO ups.load "24"
5.437187 send_to_all: SETINFO battery.voltage "270.00"
5.437187 send_to_all: SETINFO battery.runtime "0"
5.437187 send_to_all: DATAOK
5.437187 dstate_init: sock \\.\pipe\blazer_ser-ups1 open on fd 1992
5.437187 send_to_all: SETINFO driver.parameter.pollinterval "2"
5.437187 send_to_all: SETINFO device.mfr "UPS"
5.437187 send_to_all: SETINFO device.model "Model 20K"
[...]
Now, please bear with me, my C skills are long gone and forgotten, plus
my understanding of UPS operation is next to non-existent. In any case
though from above, I see that NUT receives the following info:
1.546786 send_to_all: SETINFO battery.voltage "2.25"
[...]
5.437187 send_to_all: SETINFO battery.voltage "270.00"
I think I found 2 problems, one of them an issue and another a bug.
The issue first. According to the values above, NUT tries to autodetect
the number of battery packs. LThe battery packs detection code in
blazer.c is as follows:
static double blazer_packs(const char *ptr, char **endptr)
135{
136 const double packs[] = {
137 120, 100, 80, 60, 48, 36, 30, 24, 18, 12, 8, 6, 4, 3, 2, 1, 0.5, -1
138 };
139
140 const char *val;
141 int i;
142
143 val = dstate_getinfo("battery.voltage.nominal");
144
145 batt.volt.nom = strtod(val ? val : ptr, endptr);
146
147 for (i = 0; packs[i] > 0; i++) {
148
149 if (packs[i] * batt.volt.act > 1.2 * batt.volt.nom) {
150 continue;
151 }
152
153 if (packs[i] * batt.volt.act < 0.8 * batt.volt.nom) {
154 upslogx(LOG_INFO, "Can't autodetect number of battery packs
[%.0f/%.2f]", batt.volt.nom, batt.volt.act);
155 break;
156 }
157
158 batt.packs = packs[i];
159 break;
160 }
161
162 return batt.volt.nom;
163}
Like I said, the VGN has battery strings of 20 batteries each. I would
then expect for battery.packs to be equal to 120 (20 batteries * 6
plates per battery). This does not happen. batt.volt.nom is 271.4 and
the cell has a voltage of 2.25 (see above) so the detection algorithm
does not succeed when trying "120" as the packs[i] value...
I am not sure whether this is an issue or not. Or, if it is one, if the
detection algorithm can be improved.
I did however try to override the number of battery packs, by setting
"override.battery.packs = 120" in ups.conf. Nothing happened. Which
brings me to the (possible) bug issue: override.battery.packs is not
used anywhere at all in the blazer driver(s)!
Please contact me if you need more information, I definitely want to
have this going!
BR,
Michael.-