[Nut-upsuser] Delayed UPS start up after shutdown?

Roger Price roger at rogerprice.org
Fri Dec 6 15:36:51 UTC 2013


> Le 2013-12-06 15:14, Angel Tsankov a écrit :
> ...if main power comes back within 10 seconds after the UPS has been 
> shut down, the UPS will power up the PC but the latter will not start.

On Fri, 6 Dec 2013, Rene Garcia wrote:
> .... You can change the parameter ups.delay.start into your UPS to set 
> the "Interval to wait before (re)starting the load (seconds)"
> use upsset to change the value.

Hi, You could also place a declaration such as

   ondelay = 60

in file ups.conf.

Regards, Roger