[Nut-upsuser] APC Smart-UPS 1500; system shutdown is not initiated.

Christian chanlists at googlemail.com
Sat Dec 7 19:38:29 UTC 2013


Dear list,

I have an APC Smart-UPS 1500 hooked up via the USB port. Recently, when
we had a power outage, the only entry in the logs was:

Dec  3 14:43:43 afs1 upsmon[3035]: UPS apc at localhost on battery

and then the machine seems to have run until the battery was empty. It
only notices the "battery low" after I turn the system back on:

Dec  3 16:01:39 afs1 usbhid-ups[21973]: Startup successful
Dec  3 16:01:39 afs1 upsd[21975]: listening on 192.168.103.221 port 3493
Dec  3 16:01:39 afs1 upsd[21975]: listening on 127.0.0.1 port 3493
Dec  3 16:01:39 afs1 upsd[21975]: Connected to UPS [apc]: usbhid-ups-apc
Dec  3 16:01:39 afs1 upsd[21995]: Startup successful
Dec  3 16:01:39 afs1 upsmon[22054]: Startup successful
Dec  3 16:01:39 afs1 upsd[21995]: User monuser at 127.0.0.1 logged into UPS
[apc]
Dec  3 16:01:39 afs1 upsmon[22056]: UPS apc at localhost battery is low

Any ideas?

I include my config below... Thanks,

Christian

nut is debian wheezy's 2.6.4-2.3.

/etc/nut/ups.conf:
[apc]
        driver = usbhid-ups
        port = auto
        desc = "APC SmartUPS 1500"

Occasionally, i get these in daemon.log:
Dec  4 03:11:54 afs1 usbhid-ups[21973]: libusb_get_interrupt: could not
claim interface 0: Device or resource busy
Dec  6 11:50:55 afs1 usbhid-ups[21973]: libusb_get_interrupt: error
sending control message: Connection timed out

afs1:/var/log# upsc apc at localhost
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2008/05/22
battery.runtime: 3420
battery.runtime.low: 120
battery.temperature: 24.7
battery.type: PbAc
battery.voltage: 27.7
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1500
device.serial: AS0821131402
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.4
driver.version.data: APC HID 0.95
driver.version.internal: 0.37
input.sensitivity: high
input.transfer.high: 253
input.transfer.low: 208
input.voltage: 231.8
output.current: 1.05
output.frequency: 50.0
output.voltage: 231.8
output.voltage.nominal: 230.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 653.18.I
ups.firmware.aux: 7.3
ups.load: 22.7
ups.mfr: American Power Conversion
ups.mfr.date: 2008/05/22
ups.model: Smart-UPS 1500
ups.productid: 0002
ups.serial: AS0821131402
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d



More information about the Nut-upsuser mailing list