[Nut-upsuser] APC UPS: replacement battery always triggers shutdown

JS jshaio at yahoo.com
Sun Jan 13 22:42:23 UTC 2013


Arnaud,


I was finally able to get back to this issue and would recommend adding these items to the FAQ #37 about recalibrating the UPS:


1a. It's important that the UPS be at 100% charge before starting the procedure; starting at lower will not work at all, not just produce inaccurate numbers.

      [I started the procedure when the UPS was at 91% charge. After that it would never report being more than 20% charge, even after leaving it plugged in

       for hours; running the procedure in FAQ #37 never left it reporting more than 20 seconds of charge left, which I verified was incorrect.]


1b. If for some reason the UPS never reaches 100% charge, this can be remedied (in the ACP ES-750 case), by leaving it unplugged for 1 week.

      [Doing this allowed me to recover from the case in 1a above. After that the procedure below, as in : http://excessups.com/blog/manual-runtime-calibration-apc-ups/

       worked fine.]


I would add that it is worth mentioning in the FAQs that often a replacement UPS costs only slightly more than the replacement battery for the old one,

as I found out after trying this procedure.


thanks,

--jack



________________________________
 ________

From: Arnaud Quette <aquette.dev at gmail.com>
To: JS <jshaio at yahoo.com>; Kastus Shchuka <ks-nut at tprfct.net>; Michal Soltys <soltys at ziu.info> 
Cc: nut-upsuser at lists.alioth.debian.org 
Sent: Monday, November 26, 2012 2:42 PM
Subject: Re: [Nut-upsuserAPC UPS: replacement battery always triggers shutdown] APC UPS: replacement battery always triggers shutdown


Michal, Kastus, Jack,

I have a similar request sitting in the Features requests for years:
https://alioth.debian.org/tracker/index.php?func=detail&aid=304645&group_id=30602&atid=411545
http://lists.alioth.debian.org/pipermail/nut-upsdev/2006-June/000938.html

would you please unite your efforts and bring a patch for NUT FAQ (or the driver(s))?

thanks a lot!
Arnaud
-- 
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr


2012/11/11 Kastus Shchuka <ks-nut at tprfct.net>

On Sun, Nov 11, 2012 at 07:21:35AM -0800, JS wrote:
>> I followed this procedure (charging the battery fully, letting it drain off a token load while UPS is grounded on a surge protector) but it did not help.
>>
>> Perhaps I missed something running this procedure; if anyone has suggestions for solving this they'd be greatly appreciated.
>
>I've been in the same situation after replacing the battery in SC620I model.
>
>Then I found http://old.nabble.com/SmartUPS-and-new-battery-td20678966.html
>and followed the procedure:
>
>1. Shutdown the apcupsd daemon.
>2. Run apctest
>3. Choose option 6 to enter terminal mode
>4. Enter Y (UPS should respond SM)
>5. Enter 1 (one, not el; wait 4 seconds)
>6. Enter 1 (one, not el; UPS should respond PROG)
>7. Enter 0 (zero, not oh; UPS should respond with current constant)
>8. Enter + (plus) or - (minus) to increment/decrement the value
>9. Enter R to reprogram constant value (UPS should respond Bye)
>10. Enter Y (UPS should respond SM)
>11. Enter 0 (zero, not oh; UPS should respond with the new constant)
>12. Enter Esc to exit terminal mode
>13. Choose option 7 to exit apctest.
>
>The value to store in the register 0 differs by the model. There is a table
>posted in the middle of the thread. I hope your model is listed there.
>If you cannot find your model, you may want to try experimenting with different
>values.
>
>In my case, after updating register 0, my UPS is back to 42 min runtime.
>
>Hope this helps.
>
>Kastus
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20121126/fda22d51/attachment-0001.html>

------------------------------

Message: 2
Date: Mon, 26 Nov 2012 19:09:54 -0800 (PST)
From: JS <jshaio at yahoo.com>
To: Arnaud Quette <aquette.dev at gmail.com>, Kastus Shchuka
    <ks-nut at tprfct.net>,     Michal Soltys <soltys at ziu.info>
Cc: "nut-upsuser at lists.alioth.debian.org"
    <nut-upsuser at lists.alioth.debian.org>
Subject: Re: [Nut-upsuser] APC UPS: replacement battery always
    triggers    shutdown
Message-ID:
    <1353985794.23786.YahooMailNeo at web161201.mail.bf1.yahoo.com>
Content-Type: text/plain; charset="utf-8"



I forgot to mention that I was not able to test
the procedure in #1 below successfully because my?
UPS never shows more than 65% battery charge anymore. This may be the result of a
failed calibration run.

Jack



________________________________
From: JS <jshaio at yahoo.com>
To: Arnaud Quette <aquette.dev at gmail.com>; Kastus Shchuka <ks-nut at tprfct.net>; Michal Soltys <soltys at ziu.info> 
Cc: "nut-upsuser at lists.alioth.debian.org" <nut-upsuser at lists.alioth.debian.org> 
Sent: Monday, November 26, 2012 9:38 PM
Subject: Re: [Nut-upsuser] APC UPS: replacement battery always triggers shutdown


?Arnaud,


I haven't been able to test Kastus' suggestion because my UPS (APC Back-UPS ES 750) doesn't appear on the list

and I didn't want to take take the risk of disabling it by mistake.


However, I did make a bit of progress on this:


1. There is a more detailed procedure than the one in NUT FAQ #37 in: http://excessups.com/blog/manual-runtime-calibration-apc-ups/?

? ? ?which is summarized as:


? ? Follow these steps to do a proper manual calibration on your APC UPS:

? ? 1. Battery must be at 100% capacity when the Runtime Calibration is initiated/started. (charge the UPS for 24hours prior)
? ? 2. The UPS must have 30-34% load on it during the calibration (Constant load, try: lamps, computers, monitors. Measure load % by PowerChute)
? ? 3. Disconnect the serial/USB comm cable from the UPS (you don?t want PowerChute to shut down equipment)
? ? 4. The battery must be discharged completely  (unplug UPS from wall outlet, let the UPS to shut off completely due to a discharged battery).
?
? 5. Remove the attached load (ie ? lights, computers)
? ? 6. Let the UPS charge for 8 hours while OFF (plug back into utility power, press OFF button when UPS turns ON)
? ? 7. Turn on UPS (run time should now be accurate)

?

2. the man page for the? usbhid-ups has an alternative, based on the battery charge instead of the estimated runtime:

?      ? ?"New" units have battery.runtime.low, but depending on battery quality, firmware version, calibration and UPS load - this variable can be underestimated quite
?      ? ?a bit - especially right after going into OB state. This in turn can cause LB to be asserted, which under normal conditions will cause NUT to initiate the
?      ? ?shutdown. You might want to disable this condition entirely, when relying on ignorelb option (this was actually the main
motivation behind introduction of
?      ? ?such feature).

?      ? ?Simple example:

?          ? ?[apc]
?              ? ?ignorelb
?              ? ?override.battery.charge.low = 15
?              ? ?override.battery.runtime.low = -1



I've been using this config and it works fine, allowing my system to keep running during the occasional 30-60 second AC power losses we see:
?   ? ? ? ?[apc]
?           ? ? ? ? driver = usbhid-ups
?           ? ? ? ? ?port = auto
?           ? ? ? ? desc = "APC Back-UPS ES 750"
?           ? ? ? ? ignorelb
?           ? ? ? ? override.battery.charge.low = 20
?           ?
? ? ? override.battery.runtime.low = -1


My system is running debian (testing distribution) and unfortunately the apcupsd package with apcsmart conflicts with nut-client. I tried installing it
but could not get it configured properly for the Back-UPS ES 750 (which has only a USB cable with a db-9 connector for access).

thanks,
--jack


________________________________
From: Arnaud Quette <aquette.dev at gmail.com>
To: JS <jshaio at yahoo.com>; Kastus Shchuka <ks-nut at tprfct.net>; Michal Soltys <soltys at ziu.info> 
Cc: nut-upsuser at lists.alioth.debian.org 
Sent: Monday, November 26, 2012 2:42 PM
Subject: Re: [Nut-upsuser] APC UPS: replacement battery always triggers shutdown


Michal, Kastus, Jack,

I have a similar request sitting in the Features requests for years:
https://alioth.debian.org/tracker/index.php?func=detail&aid=304645&group_id=30602&atid=411545
http://lists.alioth.debian.org/pipermail/nut-upsdev/2006-June/000938.html

would you please unite your efforts and bring a patch for NUT FAQ (or the driver(s))?

thanks a lot!
Arnaud
-- 
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org/
Free Software Developer - http://arnaud.quette.fr/


2012/11/11 Kastus Shchuka <ks-nut at tprfct.net>

On Sun, Nov 11, 2012 at 07:21:35AM -0800, JS wrote:
>> I followed this procedure (charging the battery fully, letting it drain off a token load while UPS is grounded on a surge protector) but it did not help.
>>
>> Perhaps I missed something running this procedure; if anyone has suggestions for solving this they'd be greatly appreciated.
>
>I've been in the same situation after replacing the battery in SC620I model.
>
>Then I found http://old.nabble.com/SmartUPS-and-new-battery-td20678966.html
>and followed the procedure:
>
>1. Shutdown the apcupsd daemon.
>2. Run apctest
>3. Choose option 6 to enter terminal mode
>4. Enter Y (UPS should respond SM)
>5. Enter 1 (one, not el; wait 4 seconds)
>6. Enter 1 (one, not el; UPS should respond PROG)
>7. Enter 0 (zero, not oh; UPS should respond with current constant)
>8. Enter + (plus) or - (minus) to increment/decrement the value
>9. Enter R to reprogram constant value (UPS should respond Bye)
>10. Enter Y (UPS should respond SM)
>11. Enter 0 (zero, not oh; UPS should respond with the new constant)
>12. Enter Esc to exit terminal mode
>13. Choose option 7 to exit apctest.
>
>The value to store in the register 0 differs by the model. There is a table
>posted in the middle of the thread. I hope your model is listed there.
>If you cannot find your model, you may want to try experimenting with different
>values.
>
>In my case, after updating register 0, my UPS is back to 42 min runtime.
>
>Hope this helps.
>
>Kastus
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20121126/63faaa2d/attachment.html>

------------------------------

_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

End of Nut-upsuser Digest, Vol 89, Issue 23
*******************************************