[Nut-upsuser] HP R12000/3 UPS reports status as OL DISCHRG OB
Charles Lepple
clepple at gmail.com
Wed Jul 17 02:25:01 UTC 2013
Here's the first update of ups.status:
0.102449 getting data: ups.status (.1.3.6.1.4.1.232.165.3.4.5.0)
0.102546 su_ups_get: ups.status .1.3.6.1.4.1.232.165.3.4.5.0
0.102646 nut_snmp_get(.1.3.6.1.4.1.232.165.3.4.5.0)
0.104539 SNMP UPS driver : entering su_status_set()
0.104641 su_find_infoval: found OL (value: 3)
0.104730 => value: 3
0.104823 getting data: ups.status (.1.3.6.1.4.1.232.165.3.2.5.0)
0.104919 su_ups_get: ups.status .1.3.6.1.4.1.232.165.3.2.5.0
0.105028 nut_snmp_get(.1.3.6.1.4.1.232.165.3.2.5.0)
0.107134 SNMP UPS driver : entering su_status_set()
0.107231 su_find_infoval: found DISCHRG (value: 2)
0.107319 => value: 2
0.107412 getting data: ups.status (.1.3.6.1.4.1.232.165.3.7.3.0)
0.107507 su_ups_get: ups.status .1.3.6.1.4.1.232.165.3.7.3.0
0.107616 nut_snmp_get(.1.3.6.1.4.1.232.165.3.7.3.0)
0.109529 SNMP UPS driver : entering su_status_set()
0.109630 su_find_infoval: found OB (value: 1)
0.109720 => value: 1
The first one (...3.4.5.0) is labeled in the driver as CPQPOWER_OID_POWER_STATUS. I checked around for this, and didn't find a good definition, but that seems to match the OL state.
The second one seems specific to the battery:
static info_lkp_t cpqpower_battery_abm_status[] = {
{ 1, "CHRG" },
{ 2, "DISCHRG" },
/* { 3, "Floating" }, */
/* { 4, "Resting" }, */
/* { 5, "Unknown" }, */
{ 0, "NULL" }
} ;
I could see the battery monitoring circuit discharging the battery occasionally for maintenance, but is there a separate front-panel indicator for this mode?
The third one is CPQPOWER_OID_ALARM_OB. This definitely doesn't make sense, since things with "alarm" in the name are usually pretty direct.
The big question in my mind is, where did the NUT definitions come from?
Did your UPS come with a CD that might contain a SNMP MIB definition file? Or is there an area on the HP support site? (All I saw was a firmware update .EXE)