[Nut-upsuser] upsrw doesn't set variable
Mike.
the.lists at mgm51.com
Sat Jun 29 19:22:44 UTC 2013
On 6/29/2013 at 6:16 PM Kjell Claesson wrote:
|lördagen den 29 juni 2013 11.28.14 skrev Mike.:
|8<------------------snip---------------------
|Hi Mike,
|>
|> Thanks for the quick reply.
|>
|> I checked the log file (which, admittedly, I should have done before
I
|> posted about the problem :) ).
|>
|> Here's the command and the corresponding log message:
|>
|> # upsrw -u au -p ap -s outlet.1.delay.shutdown=12
PW5125 at localhost
|> OK
|>
|> bcmxcp[90004]: Set [outlet.1.delay.shutdown 12] failed due to
invalid
|> parameter
|>
|Yep the ups is telling that the command has an invalid parameter.
|Have to check if there is any difference between the 5125 and others.
|>
|> Curious that the command gives an "OK" response, even though it logs
a
|> failure.
|>
|>
|The OK kome from upsrw, as the driver is accepting the command.
|>
|> I'll try the -D flags when I have some time, maybe this evening.
btw,
|> how many is "a few" -D flags?
|>
|>
|> fwiw, I don't have a USB port on the UPS, just serial.
=============
Here is the console output of bcmxcp with -DDD specified:
[snip]
13.721204 Auto delay on: 2
13.721243 send_command: (4 bytes) => ab 01 35 1f
13.821127 send_command: (4 bytes) => ab 01 33 21
13.920982 send_command: (4 bytes) => ab 01 3b 19
14.033202 Battery Status: (21 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
14.033249 00 00 00 00 01 03
14.033275 Battery Status = No test initiated (0)
14.261271 entering setvar(outlet.1.delay.shutdown, 12)
14.261318 send_command: (7 bytes) => ab 04 cf 69 e8 d5 5c
16.261647 send_command: (8 bytes) => ab 05 97 01 01 0c 00 ab
16.318194 Set [outlet.1.delay.shutdown 12] failed due to invalid
parameter
16.318245 send_command: (4 bytes) => ab 01 34 20
16.574540 send_command: (4 bytes) => ab 01 41 13
16.658312 init_outlet(14), res=14
16.658346 Number of outlets: 2
16.658358 Number of bytes: 6
16.658369 Outlet number: 1
16.658388 Outlet state: 1
16.658406 Auto delay off: -1
16.658432 Auto delay on: 1
16.658461 Outlet number: 2
16.658477 Outlet state: 1
16.658496 Auto delay off: -1
16.658525 Auto delay on: 2
[snip]
Let me know if there is anything else I should do.
Thanks.