[Nut-upsuser] upsrw doesn't set variable
Kjell Claesson
kjell.claesson at epost.tidanet.se
Sat Jun 29 16:16:30 UTC 2013
lördagen den 29 juni 2013 11.28.14 skrev Mike.:
8<------------------snip---------------------
Hi Mike,
>
> Thanks for the quick reply.
>
> I checked the log file (which, admittedly, I should have done before I
> posted about the problem :) ).
>
> Here's the command and the corresponding log message:
>
> # upsrw -u au -p ap -s outlet.1.delay.shutdown=12 PW5125 at localhost
> OK
>
> bcmxcp[90004]: Set [outlet.1.delay.shutdown 12] failed due to invalid
> parameter
>
Yep the ups is telling that the command has an invalid parameter.
Have to check if there is any difference between the 5125 and others.
>
> Curious that the command gives an "OK" response, even though it logs a
> failure.
>
>
The OK kome from upsrw, as the driver is accepting the command.
>
> I'll try the -D flags when I have some time, maybe this evening. btw,
> how many is "a few" -D flags?
>
>
> fwiw, I don't have a USB port on the UPS, just serial.
>
> Thanks.
//Kjell