On Jan 21, 2014, at 8:05 AM, Rafał Oleszek wrote:
> MONITOR UPS_251 at localhost 2 monmaster password master
> MONITOR UPS_252 at localhost 2 monmaster password master
I think the "2"s here should be "1".
"powervalue is an integer representing the number of power supplies that the UPS feeds *on this system*."
So if UPS_251 is connected to one power supply on the system running upsmon, and UPS_252 is connected to another, then each powervalue is 1.
> MINSUPPLIES 2
Or you could change this to 4, but that masks what is actually going on.
--