[Nut-upsuser] Shutdown when both (all) UPS on battery / low battery
Rafal Oleszek
r.oleszek at wasko.pl
Tue Jan 21 14:24:14 UTC 2014
I tried all options:
1,2
and in MINSUPPLIES: 1,2,3,4
still didn't work.
UPS_251 and UPS_252 feeds all environment and it's not feed directly one
server, but many of them.
> On Jan 21, 2014, at 8:05 AM, Rafał Oleszek wrote:
>
>> MONITOR UPS_251 at localhost 2 monmaster password master
>> MONITOR UPS_252 at localhost 2 monmaster password master
>
> I think the "2"s here should be "1".
>
> "powervalue is an integer representing the number of power supplies that
> the UPS feeds *on this system*."
>
> So if UPS_251 is connected to one power supply on the system running
> upsmon, and UPS_252 is connected to another, then each powervalue is 1.
>
>> MINSUPPLIES 2
>
> Or you could change this to 4, but that masks what is actually going on.
>
> --
> Charles Lepple